Garage furnace with an induced draft vent. It is allowed to slope downward? Could not find any installation instructions. Place was built in 07
Nick Ostrowski
09-23-2010, 08:29 AM
I don't see those types of units around here.
Is that a condensate stain on the plate beneath the flue pipe?
John Arnold
09-23-2010, 08:34 AM
No way.
The Simpson Dura-Vent instructions I have say that any "horizontal" sections must slope upwards away from the appliance at least 1/4" per foot. I don't think it would say that if you were allowed to vent vertical sections down as shown.
Gunnar Alquist
09-23-2010, 08:46 AM
Induced draft is still considered natural draft and must be installed as such. As John said, needs correct slope.
Rod Butler
09-24-2010, 07:03 AM
Agreed as flat out wrong.:eek:
David Bell
09-24-2010, 07:09 AM
Also, clearance from venting to gas pipe not good, no sediment trap on gas line, clearance of unit to ceiling could be suspect.
Scott Craig
10-15-2010, 11:38 AM
Garage furnace with an induced draft vent. It is allowed to slope downward? Could not find any installation instructions. Place was built in 07
Must admit, I have never seen a set up like that! But really looks wrong. Don't think it should ever slope down!