Looked in a ITE panel today and found a double tap @ the main lug, but other end went to a ITE Safety Switch box. Would this be acceptable

Jim Port
11-23-2010, 07:40 PM
No, that lug is good for only one conductor.

Jerry Peck
11-23-2010, 07:53 PM
Don't forget all those neutrals and grounds in the same terminals with each - that is not allowed either.

Roger Frazee
11-23-2010, 09:58 PM
To add

Appears there is no identified neutral ( not a big deal but just pointing it out)

You probably mentioned it in your report but they could use a few lessons on properly fastening those nm cables in the photo of the safety switch.

LEO304E CARR
11-24-2010, 12:04 AM
To add

Appears there is no identified neutral ( not a big deal but just pointing it out)

You probably mentioned it in your report but they could use a few lessons on properly fastening those nm cables in the photo of the safety switch.


All conductors shuld have a seperate connection:)

John Arnold
11-24-2010, 03:48 AM
All conductors shuld have a seperate connection:)

Often it's ok to have more than one equipment grounding conductor at the same terminal.