03-12-2011, 03:57 PM
I came across this Square D panel yesterday. Everything seems to be in order however I am unsure as to the acceptable use of aluminum as grounding wires in a predominantly copper wired panel. Is this something that should be noted and referred to a licensed electrician for further evaluation?

Is it possible the alum ground is for an appliance? The sub panel is also shown in the next picture, and it contains all copper wiring.

Thank you for your time!

PK

Matt Fellman
03-12-2011, 04:17 PM
I've run across this a couple times over the years.... I seem to remember it's a 1960s era roughly. Logically, I can't see a problem as the ground system doesn't regularly carry current but my SOPs do require I call out any aluminum 110volt circuits so I at least brought it to their attention.

I think I may have posted about this before so you might try a search.

John Kogel
03-12-2011, 05:03 PM
Could you post larger pics? 640 X 480 pixels.
I can't see enough detail to draw any conclusions.
What is the age of the house?

Patrick Knight
03-13-2011, 12:19 PM
I thought the pics were larger. Thanks for any additional help!

PK

John Kogel
03-13-2011, 12:36 PM
As far as I can make out, there are some Al neutrals as well. Sometimes the camera flash will make Cu look pale, so it's hard to tell. But usually if there are solid Al grounds, the hots and neutrals are also Al.

Yes, I would call for an electrician to go over the connections. not just in the panel, but at the fixtures as well. Something to look for is reno'd rooms where they've bought new receptacles at a box store. They will often use cheap Cu-only fixtures, and mix Cu and Al with the wrong wire nuts, etc.

CHARLIE VAN FLEET
03-13-2011, 02:26 PM
bigger pictures please

Patrick Knight
03-13-2011, 02:51 PM
I made my pictures as big as they allow and then uploaded and it makes them even smaller. Do not know what gives. If you would like to see a bigger picture, I can email it to you. Thanks, PK

CHARLIE VAN FLEET
03-13-2011, 03:03 PM
patrick

still to small to really see--but most of the problems with alum branch wires is at the outlet and switches . they can get hot and alter the expansion and contraction of the wire. wires get loose and mr. sparky shows up. but even lately, some electricians are cop/alum cripping the wires in the panel.

cvf

John Lindley-Howard
03-14-2011, 04:44 AM
There are a couple fo other things that I noticed that should be mentioned. In the main panel there are a couple of distribution wires that have too much sheathing exposed in the panel. One is just visible in the top left (a couple of inches of sheathing), and the other comes all the way down on the right. There should be less than 1 inch of sheathing on the wires as they enter the panel.

It is tough to tell on the sub-panel, but it looks like as though the insulation is stripped back on the feed wires for several inches. The is not correct and presents a significant safety risk for anyone working in the panel.

David Bertrams
03-14-2011, 05:53 AM
What about color code?

Bill Kriegh
03-14-2011, 07:43 AM
There are a couple fo other things that I noticed that should be mentioned. In the main panel there are a couple of distribution wires that have too much sheathing exposed in the panel. One is just visible in the top left (a couple of inches of sheathing), and the other comes all the way down on the right. There should be less than 1 inch of sheathing on the wires as they enter the panel.

It is tough to tell on the sub-panel, but it looks like as though the insulation is stripped back on the feed wires for several inches. The is not correct and presents a significant safety risk for anyone working in the panel.

The NEC states that a minimum of 1/4 inch of sheath must extend beyond the cable clamp. It doesn't say anything about a maximum, although an install like this is usually a sign of an amature at work.

It looks like your stripped too long wires have paint on them.