View Full Version : 3-2-10 rule revisited
Benjamin Thompson
04-29-2011, 03:22 PM
Does the 3 feet above the roof line only apply to wood burning fireplaces, not to gas appliances? I can't find anything in the IRC regarding this.
Bob Harper
04-29-2011, 05:53 PM
chimneys
Benjamin Thompson
04-29-2011, 05:57 PM
Thanks Bob. Does a prefabricated gas fireplace with type B vent count as a chimney? Is it OK to have type B vents 4-6 inches above the roof line?
Bob Harper
04-29-2011, 07:03 PM
Nope and nope.
B-vent is a *vent*--not a *chimney*.
Refer to the gas codes but they start at 12" above a flat roof then go up based upon roof pitch.
Benjamin Thompson
04-29-2011, 07:43 PM
Thanks again Bob! Here is a picture of the vent I thought was too low. It's about 3 feet from the parapet and well below it but not within 3 feet of the corner. I am not sure I understand why a gas appliance would not back draft when a fireplace would? Any insight?
22018
Bob Harper
04-30-2011, 04:56 AM
You have a vertical obstruction within 8ft horizontally so the flue gas outlet must extend at least 2 feet above the top of that parapet. The 3 ft rule is to allow sparks from wood burning to cool before they land on a possibly combustible roof deck. The 2/10 is to hopefully extend the vent above any pressure zones created by wind effect over a ridge.
The height of a vent above a roofline would have an effect on backdrafting only if it was wind related in which case it may need to extend a lot more than just the code minimum. Codes do not guarantee performance and can be exceeded.
Jerry Peck
04-30-2011, 06:42 PM
... code minimum. Codes do not guarantee performance and can be exceeded.
Expanding on what Bob said - codes are the minimum standard, with the emphasis on "MINIMUM" standard. Any 'good' builder/contractor will exceed code as code is the crappiest they are legally allowed to build.
Powered by vBulletin® Version 4.2.0 Copyright © 2025 vBulletin Solutions, Inc. All rights reserved.