View Full Version : Remote panel in crawlspace



Marc M
05-03-2011, 09:55 PM
So, if there is accessibility to the panel and lighting in front of the panel in a crawlspace (that you can stand in), are there any other reasons why a panel cannot be installed here?

Tom Thompson
05-03-2011, 10:36 PM
Easy access is required with clearances 30" each side, 36" in front (some very by location) also standing headroom isn't crawl space

Marc M
05-03-2011, 10:44 PM
Easy access is required with clearances 30" each side, 36" in front (some very by location) also standing headroom isn't crawl space

Cool, thanks. But, I did have to crawl through a typical screen cover ( like you see out in Northridge every day) under the house and then it opened up to a pretty large area.

Tom Thompson
05-03-2011, 10:51 PM
Cool, thanks. But, I did have to crawl through a typical screen cover ( like you see out in Northridge every day) under the house and then it opened up to a pretty large area.
That is not easy access

Marc M
05-03-2011, 10:58 PM
That is not easy access

I suppose you're correct technically...although I slipped in pretty easily at a buck fifty.:D

ken horak
05-04-2011, 08:11 AM
Easy access is required with clearances 30" each side, 36" in front (some very by location) also standing headroom isn't crawl space

30" of working space in width total. Not 30" each side of panel

Jimmy Roberts
05-04-2011, 08:45 AM
I expect there is a service disconnect on the outside of the structure, at the meter base?

Marc M
05-04-2011, 11:18 AM
I expect there is a service disconnect on the outside of the structure, at the meter base?

Yea, its just a remote panel