I looked at a new construction rowhome in Philly today. In addition to the front entry door, there is a door in the kitchen that leads to the rear exterior patio. The issue is that the walls surrounding the rear patio (left, right, straight ahead, and above the door) are about 25 feet high each so the patio is essentially at the bottom of a 25 foot high box. While the rear door does allow egress, the height of the walls prevents anybody from leaving the property which appears to be a real safety issue in the event of a fire. There is a rear 1st floor bedroom which has one window that exits to the same patio. There is also an attic pulldown ladder that allows access to the roof of the house. But there is no fire escape ladder to allow safe escape from the roof surfaces. Therefore, the only means of egress that allow complete and safe exiting of the property are the front entry door and the two front living room windows.

Are there any code references that might address this configuration?

James Duffin
07-12-2011, 08:09 PM
NC Code Reference - It look's like a court is ok in NC.

SECTION R310
EMERGENCY ESCAPE AND RESCUE OPENINGS

R310.1 Emergency escape and rescue required. Basements
with habitable space and every sleeping room shall have at least
one operable emergency escape and rescue opening. Such opening shall open directly into a public street, public alley, yard or I
court.

Jerry Peck
07-12-2011, 08:11 PM
Are there any code references that might address this configuration?

Yes. (bold and underlining are mine, also, I did not post the entire section, just the applicable part and some extra)
- R310.1 Emergency escape and rescue required. Basements

and every sleeping room shall have at least one operable emergency
and rescue opening. Such opening shall open directly
into a public street, public alley, yard or court. Where basements
contain one or more sleeping rooms, emergency egress
and rescue openings shall be required in each sleeping room,
but shall not be required in adjoining areas of the basement.
Where emergency escape and rescue openings are provided
they shall have a sill height of ...

And the definition:
- EMERGENCY ESCAPE AND RESCUE OPENING. An

operable exterior window, door or similar device that provides
for a means of escape and access for rescue in the event of an
emergency.

I.e., as you are alluding to - once out the window they need to be able to escape to someplace.

Also, keep in mind this part "and rescue" - rescue personnel need to have access to that area in order to be able to rescue the person(s) in the room.

Fred Weck
07-14-2011, 08:57 AM
In principle I agree with you Jerry, but this is another one of those places where the code and common sense diverge. It is opening into a court so it meets the minimum requirements of the code.

Nick Ostrowski
07-14-2011, 09:16 AM
In principle I agree with you Jerry, but this is another one of those places where the code and common sense diverge. It is opening into a court so it meets the minimum requirements of the code.

Then that code need to be rewritten. EMS personnel would need to have rappelling equipment on-hand to pull anybody out of there.

John Kogel
07-14-2011, 10:17 AM
Then that code need to be rewritten. EMS personnel would need to have rappelling equipment on-hand to pull anybody out of there.It can't be that hard to build a staircase with a one-way gate. If the builder doesn't do it voluntarily, then the tenants should demand it.

Jerry Peck
07-14-2011, 03:34 PM
In principle I agree with you Jerry, but this is another one of those places where the code and common sense diverge. It is opening into a court so it meets the minimum requirements of the code.

Fred,

Actually, the code and common sense do not diverge, the codes wording is simply not fully clear, while its intent is.

The code's intent is to have that escape and rescue path lead to a place where there is an escape from the building and to a place from which one can be rescued, and (as an alternative) have a path from a place accessible to rescue personnel which leads to the EERO through which rescue personnel can enter the structure and rescue people.

The code's wording starts out clear "public street, public alley," and then becomes a little less clear even though the intent has not changed "yard or court".

Think about it this way: If the code said this 'public street, public alley, public yard or public court' ... would the bedroom window be allowed to open to a "private" yard area? Nope. Can you imagine having to have your bedroom window open directly to a PUBLIC 'street, alley, yard, or court'? Holy smokes!

So the code starts out with specifically stating that it needs to open to a public area, then allows for it to open to a private area *as long as the private area is accessible to a public area where rescue can take place or where rescue personnel can enter from*.

If the code poorly worded? Yep. Could the code be worded better? Absolutely! Maybe something like this: 'public street, public alley, yard or court which is accessible from a public street or public way'. Of course, then you would get someone who would complain that they would not be able to 'fence in their yard', but they could, because, as one Fire Marshal in South Florida told me once when I asked about an subdivision where the EERO all opened to rear fenced yards with no access out of them, there were other fenced yards on the other sides of all the fences - "I've never seen a fence we could not run down with one of our firetrucks." He then added: "If there is a fire and people are in one of those rear yards, we will just put the truck in gear and stand on the gas pedal ... and stop when we have run over any and all fences which might have been in our way."

Nick's example is different in that, as I read his post, there are other building on the sides of that yard ... the difference is that buildings are harder to run over than fences ... but that does not mean the fire department might not try if the time comes ... :)

H.G. Watson, Sr.
07-14-2011, 09:01 PM
Yes. (bold and underlining are mine, also, I did not post the entire section, just the applicable part and some extra)


No, you snipped the most important applicable part for Nick's situation (the solitary EERO for the bedroom that opens to this 25' high-walled dead-end; and this erroneously lead to the confusion, and the statement by Nick that the code "needed to be rewritten" based upon your "snip", which it doesn't. The last sentance of R310.1 prior to the exception is THE most applicable part!!

You cut too early in your cut & paste:



- R310.1 Emergency escape and rescue required. Basements

and every sleeping room shall have at least one operable emergency
and rescue opening. Such opening shall open directly
into a public street, public alley, yard or court. Where basements
contain one or more sleeping rooms, emergency egress
and rescue openings shall be required in each sleeping room,
but shall not be required in adjoining areas of the basement.
Where emergency escape and rescue openings are provided
they shall have a sill height of ...




...There is a rear 1st floor bedroom which has one window that exits to the same patio. There is also an attic pulldown ladder that allows access to the roof of the house. But there is no fire escape ladder to allow safe escape from the roof surfaces...

Unclear if that "attic" is considered habital. Sounds like there may be a roof top deck, occupiable.

This is IRC R310.1 following (both 2009 and 2006). The Most applicable part(s) is(are) highlighted in bold, red, and underlined for emphasis (and the last sentance that you cut out is a larger font!):



SECTION R310 EMERGENCY ESCAPE AND RESCUE OPENINGS

R310.1 Emergency escape and rescue required. Basements, habitable attics and every sleeping room shall have at least one operable emergency escape and rescue opening. Where basements contain one or more sleeping rooms, emergency egress and rescue openings shall be required in each sleeping room. Where emergency escape and rescue openings are provided they shall have a sill height of not more than 44 inches (1118 mm) above the floor. Where a door opening having a threshold below the adjacent ground elevation serves as an emergency escape and rescue opening and is provided with a bulkhead enclosure, the bulkhead enclosure shall comply with Section R310.3. The net clear opening dimensions required by this section shall be obtained by the normal operation of the emergency escape and rescue opening from the inside. Emergency escape and rescue openings with a finished sill height below the adjacent ground elevation shall be provided with a window well in accordance with Section R310.2. Emergency escape and rescue openings shall open directly into a public way, or to a yard or court that opens to a public way.

Exception: Basements used only to house mechanical equipment and not exceeding total floor area of 200 square feet (18.58 m2).





SECTION R310 EMERGENCY ESCAPE AND RESCUE OPENINGS

R310.1 Emergency escape and rescue required. Basements and every sleeping room shall have at least one operable emergency escape and rescue opening. Such opening shall open directly into a public street, public alley, yard or court. Where basements contain one or more sleeping rooms, emergency egress and rescue openings shall be required in each sleeping room, but shall not be required in adjoining areas of the basement. Where emergency escape and rescue openings are provided they shall have a sill height of not more than 44 inches (1118 mm) above the floor. Where a door opening having a threshold below the adjacent ground elevation serves as an emergency escape and rescue opening and is provided with a bulkhead enclosure, the bulkhead enclosure shall comply with Section R310.3. The net clear opening dimensions required by this section shall be obtained by the normal operation of the emergency escape and rescue opening from the inside. Emergency escape and rescue openings with a finished sill height below the adjacent ground elevation shall be provided with a window well in accordance with Section R310.2. Emergency escape and rescue openings shall open directly into a public way, or to a yard or court that opens to a public way.

Exception: Basements used only to house mechanical equipment and not exceeding total floor area of 200 square feet (18.58 m2).


Definitions read the same also for "Public Way" in both editions, thusly:




SECTION R202 DEFINITIONS

PUBLIC WAY. Any street, alley or other parcel of land open to the outside air leading to a public street, which has been deeded, dedicated or otherwise permanently appropriated to the public for public use and that has a clear width and height of not less than 10 feet (3048 mm).

The kitchen door is a secondary exit not the primary means of egress.

That last sentance of 310.1,

"Emergency escape and rescue openings shall
open directly into a public way,
or
to a yard or court that opens to a public way"

should clear things up for Nick O. and Fred.;)

Obviously, climbing a fence, let alone scaling a 25' wall, doesn't "cut it". The yard or court must OPEN to a public way, if serving an EERO.

See further definitions in the IBC, and IFC, which are incorporated into the IRC by reference in Chapter 2.

Rick Cantrell
07-15-2011, 02:55 AM
A few words makes a big difference.
Good catch Mr Watson

Fred Klein
07-15-2011, 06:08 AM
I looked at a new construction rowhome in Philly today. In addition to the front entry door, there is a door in the kitchen that leads to the rear exterior patio. The issue is that the walls surrounding the rear patio (left, right, straight ahead, and above the door) are about 25 feet high each so the patio is essentially at the bottom of a 25 foot high box. While the rear door does allow egress, the height of the walls prevents anybody from leaving the property which appears to be a real safety issue in the event of a fire. There is a rear 1st floor bedroom which has one window that exits to the same patio. There is also an attic pulldown ladder that allows access to the roof of the house. But there is no fire escape ladder to allow safe escape from the roof surfaces. Therefore, the only means of egress that allow complete and safe exiting of the property are the front entry door and the two front living room windows.

Are there any code references that might address this configuration?

I too inspect in Philadelpia and they do not care about code or just use their interpitation. I have inspected homes that were taken down to the basement foundation walls and rebuilt without emergency egress from finished basements. The city accepts this, which from everything I know is wrong. Also the city inspection process in the city is poor to non existent.

Fred Klein
07-15-2011, 06:11 AM
Then that code need to be rewritten. EMS personnel would need to have rappelling equipment on-hand to pull anybody out of there.

But assuming as in Philadelpha that full time fire fighters respond they can gain access. Yes it is poor planing

Nick Ostrowski
07-15-2011, 06:31 AM
Yeah, Philadelphia has little to no enforcement. Makes for some interesting inspections.

Michael Gantt
07-15-2011, 02:24 PM
DO they have sprinklers?

Jerry Peck
07-15-2011, 02:50 PM
A few words makes a big difference.
Good catch Mr Watson