10-26-2011, 05:12 PM
House built in 1981. Stairway under stairs to the 2nd level does not have sheetrock installed for fire protection. Is it required? Closet door separating hallway from area under the stairway.

Thanks,

Jim

Gunnar Alquist
10-26-2011, 05:25 PM
Hi Jim,

Yes, it is required for most stairways. I don't have the code handy, otherwise I would quote it for you.

JIM MURPHY
10-26-2011, 05:32 PM
Thanks,

When you say most, can you clarify that please


Jim

James Duffin
10-26-2011, 05:38 PM
NC Code



R311.2.2 Under stair protection. Enclosed accessible space
under stairs shall have walls, under stair surface and any soffits
protected on the enclosed side with 1/2-inch (13 mm) gypsum
board.

Jerry Peck
10-26-2011, 05:47 PM
If the stair is open below (the underside of the stair is visible), then no protection is needed.

If the stair is enclosed below, whether it be a non-accessible concealed space or an accessible concealed space (i.e., a closet with a door), then the underside of the stair needs to have protection.

The reason is that if there is a fire under the stairway, either the occupants need to be able to see the fire (i.e., the area under the stair is not enclosed), or the occupants need to have the stair protected (i.e., they cannot see the fire down there and need time to be able to escape down the stairs before the stairs catch on fire). If the occupants can see the fire under the stairs, they will take some other way out and not go down the stairs.

JIM MURPHY
10-26-2011, 05:55 PM
Thank you all!

Jim

JIM MURPHY
10-26-2011, 05:56 PM
Does this apply to a 1981 house?

Billy Stephens
10-26-2011, 06:02 PM
.
Does this apply to a 1981 house?
.
Jim,

It's a Fire Hazard !

Code or No.

Correct Fire Hazard.

Safety Never Goes Out of Style. ;)
.

Jerry Peck
10-26-2011, 06:19 PM
Does this apply to a 1981 house?

It should have, not that it matters because ... :)


.
Jim,

It's a Fire Hazard !

Code or No.

Correct Fire Hazard.

Safety Never Goes Out of Style. ;)
.

A fire is not going to look up and decide if it was allowed to burn or not when the structure was built, it is just going to burn (fires are dumb, stubborn things, they simply do not care about the written word and its rules). :)

James Duffin
10-27-2011, 04:18 PM
Does this apply to a 1981 house?

Since this involves safety I would not be concerned about the code in 1981. I would include it in the report and let someone else decide it is important or not.