View Full Version : Is this Aluminum wire?
Robert Foster
03-09-2012, 06:44 AM
Is the upper conductor in this pic aluminum ? The house was built in 1954.
Thank you.
Jim Port
03-09-2012, 06:57 AM
Based on the fabric covered insulation I would say it is tinned copper.
John Arnold
03-09-2012, 07:01 AM
If you have pics from a different angle you may be able to see copper on the cut end.
Looks like tin coated copper to me, too.
Robert Foster
03-09-2012, 09:42 AM
Thank you for the quick replies....unfortunately, the end of the conductor was inserted so far into the fuse holder that I couldn't see the end and take that picture...
Jack Feldmann
03-09-2012, 03:49 PM
I'm going with tinned copper. You can sometimes get a better look at the neutrals.
Robert Meier
03-09-2012, 03:50 PM
It's not aluminum. :)
John Arnold
03-09-2012, 03:53 PM
...You can sometimes get a better look at the neutrals.
Excellent point.
Stephen G
03-09-2012, 04:03 PM
They appear to be the same size, aluminum would be a larger wire for same service...
but why tin only one wire...did some older wires come pre-tinned
Jerry Peck
03-09-2012, 04:53 PM
They appear to be the same size, aluminum would be a larger wire for same service...
but why tin only one wire...did some older wires come pre-tinned
Copper reacts with the compounds in the rubber, so the entire length of the conductors in the rubber insulation are tinned.
The conductor which is not tinned is likely a newer conductor with thermoplastic insulation, no tinning required.
When you see tinned copper (and thus rubber insulation) it is time to re-wire because the rubber dries out and becomes brittle and cracks, effectively cracking micro-cracks along the wire, and each of those cracks is a leakage point for the voltage and current on that wire to try to find any other path back to the source.