Inspected a 1968 home with a type of main panel box I have never before seen. The breaker design was foreign to me. Anyone have any past experience with this design? Like, how to reset a breaker? How reliable is it at this age, ect. Thanks in advance.[ATTACH]25405

Robert Meier
04-20-2012, 03:01 PM
Looks like a Bulldog Pushmatic panel with a fused main. The center of the CB is pushed into cycle it on and off.

http://i.ebayimg.com/t/PUSHMATIC-ITE-Siemens-Gould-Bulldog-2-Pole-BREAKER-20-Amp-P220-old-31220-/00/s/NDgwWDY0MA==/$%28KGrHqFHJEIE88cr2Pb+BPTryyznDQ%7E%7E60_3.JPG

Garry Blankenship
04-20-2012, 04:49 PM
What Robert said. That upper assembly is the main disconnect. You cannot switch or tirn it on/off. The handle on that upper assembly is there to pull it completely, ( physically ), out; fuses & all. If you do that, the panel is dead / disconnected.

Rollie Meyers
04-20-2012, 06:42 PM
If it's 1968 vintage then it would be a ITE Pushmatic panel, if one were to pull out the 200A pullout, it prob. is stamped "ITE Circuit Breaker Company, Walker Div".:)

Pushmatic was the only residential bolt-on type breaker panel, other then old & obsolete nothing wrong w/ them, not like a Zinsco of the same era where it was crap when it was still in the box on the distributors shelf.

Erby Crofutt
04-21-2012, 08:12 AM
It's a pushmatic but a clear picture of the label certainly would have helped identify it as ITE or Bulldog.

Michael Bronner
04-22-2012, 05:31 AM
Thank you all for the information. It is an ITE, Walker out of Atlanta, I do recall seeing that on the labeling.

Speedy Petey
04-22-2012, 05:37 AM
Pushmatics were considered some of the best residential breakers going, in their day.

About the only issues I see these days is failure to reset. Sometimes breakers when turned off or tripped can be very difficult to press back in.