This is for a gas snow melt boiler. The tag was difficult to read but it appeared to be a simpson Dura Vent. Does this require 2 ft of clearance above the roof.

Mike Lamb
05-06-2012, 01:11 PM
Duravent does not recommend outside vents in cold climates unless installed in an enclosure. Once that is done I'd just follow their height termination chart.

http://home.comcast.net/~marylandhomeinspectors/BVentGuide.pdf

Check out Fig. 11, page 8.

wayne soper
05-06-2012, 07:27 PM
http://www.mtlfab.com/media/L2147.pdf

Stephen Tilleux
05-09-2012, 02:47 PM
"appeared to be a simpson Dura Vent" Simpson "B-Vent"? or Direct Vent? I can't tell from the picture.

Does the "boiler" manual call out clearences for it's venting?

Also it needs a wall strap above that 90, as the leg with the cap could rotate 180 and face the cap down (bad).

My2c

Bob Harper
05-09-2012, 06:25 PM
Cross-check the appliance and vent listed instructions and go with the most restrictive as always.

Yes, that vent needs support both below the elbow to provide support for that horizontal leg and as Stephen pointed out above it. However, if you only have one point of stability, so the vent could wave at you as you drive by and sag. You cannot rely on the listed wall penetration, which is not visible but hopefully they used.