View Full Version : Need some help with this installation



Marc M
10-04-2012, 10:25 PM
Need some help with this repair. Left vertical is a vent right is to a tub. I wasn't sure if there is a clearance between the San T and vertical drain? Educate me, thanks.

TR Platt
10-05-2012, 03:26 AM
No problem with the clearance, but you have issues if the vent is supposed to be for the tub.

Marc M
10-05-2012, 08:18 AM
my mistake, its not the tub...I'll re post when i remember what its for.

Markus Keller
10-05-2012, 08:20 AM
IRC 3005.1 & 706 - the sanitary Tee on the left side of the picture is not supposed to be installed on its' back.

Marc M
10-05-2012, 08:29 AM
thanks Markus.

Jerry Peck
10-05-2012, 09:04 AM
IRC 3005.1 & 706 - the sanitary Tee on the left side of the picture is not supposed to be installed on its' back.

Correct, that sanitary tee should either be a wye and an eighth bend as installed at the bottom, or it could be a combination wye and eighth bend as either would go from horizontal to vertical.

TR Platt
10-05-2012, 02:01 PM
If left vertical is a vent as stated by OP, sanitary tee is allowed on its back as depicted. If left vertical is receiving discharge from any fixture, the tee would be incorrect.