Is there any code/restriction preventing the allowance of two blanks at the top of a panel for future Surge Protector, or must you "fill from top" and continue down?

Jim Luttrall
02-13-2013, 12:13 PM
No specification as to placement of breakers within the panel other than to comply with the manufacturers instructions.

Jim Port
02-13-2013, 03:47 PM
The only possible issue is the bus stab rating.

Billy Stephens
02-13-2013, 05:43 PM
The only possible issue is the bus stab rating.

Or open knock outs.

Rich Goeken
02-13-2013, 08:59 PM
Thanks, I thought so..... I never came across any restrictions anywhere, but in talking to a sparky a while back he indicated that they had to start from the top per code. It didn't sound right to me, but I didn't have time to follow up on the comment.