Would it be acceptable to jump off the main lug to power a sub-panel that didn't have a main breaker. Main service panel was a GE 200 amp., the sub-panel didnt have a main breaker. TKS
wayne soper
02-15-2013, 07:11 PM
no, double tap not allowed.
main panel more than likely overloaded
repairs required
Darrel Hood
02-16-2013, 05:04 AM
Wayne, if the conductor was pig tailed, using proper techniques, to eliminate the double tap, would it be OK?
Jim Port
02-16-2013, 05:57 AM
Wayne, what are you basing your possibly overloaded comment on? Looks?
Jerry Peck
02-16-2013, 08:39 PM
'Yes', 'no', and 'not like that', along with 'the remote panel bus would need to be rated the same or higher than the rating of the main disconnect'.