Am I dreaming or not? I think I remember seeing a requirement for under stair storage closet to have a light. Yes or no?

And here is another, do dining room receptacle outlets need AFCI protection or are they technically exempt?

Jim Port
06-06-2013, 06:35 PM
The NEC does not require understairs lighting.

Here is the 2011 regarding AFCIs. Note it says outlets so lighting is covered.


210.12 Arc-Fault Circuit-Interrupter Protection.(A) Dwelling Units. All 120-volt, single phase, 15- and20-ampere branch circuits supplying outlets installed indwelling unit family rooms, dining rooms, living rooms,parlors, libraries, dens, bedrooms, sunrooms, recreationrooms, closets, hallways, or similar rooms or areas shallbe protected by a listed arc-fault circuit interrupter,combination-type, installed to provide protection of thebranch circuit.

Harry Janssen
06-06-2013, 06:45 PM
No.not required.

Jim Luttrall
06-06-2013, 06:53 PM
Thank you gentlemen!

Jim Luttrall
06-06-2013, 07:35 PM
Closets do not require lighting outlets unless they fall under storage spaces.
When is a closet NOT used for storage?

Roland Miller
06-07-2013, 05:21 AM
Clothes, Closet. A non-habitable room or space intended primarily for storage of garments and apparel. (2011 NEC)

If it does not have a permanently installed clothes rod a lighting outlet is required. I also believe it must be sheetrocked (someone please verify this or not?).

So --Yes will cover this space, since no architect in his right mind would design it for a clothes closet.

The term "outlet" covers lighting outlets and receptacle outlets. So Yes it is required to be AFCI protected in a dining room of a dwelling.

Jim Luttrall
06-07-2013, 07:15 AM
Thank you!

John Kogel
06-07-2013, 08:19 AM
Closets do not require lighting outlets unless they fall under storage spaces.And what would make the closet fall, unless the whole house fell with it? :biggrin:

Ray Thornburg
06-07-2013, 11:44 AM
I say not required because it says these rooms....Storage or Equipment Spaces. For attics, underfloor
spaces, utility rooms, and basements, at least one lighting
outlet containing a switch or controlled by a wall switch
shall be installed where these spaces are used for storage or
contain equipment requiring servicing.

Alan Highland
06-07-2013, 11:55 AM
The NEC does not require understairs lighting.

Here is the 2011 regarding AFCIs. Note it says outlets so lighting is covered.


210.12 Arc-Fault Circuit-Interrupter Protection.(A) Dwelling Units.

All 120-volt, single phase, 15- and20-ampere branch circuits supplying outlets installed indwelling unit family rooms, dining rooms, living rooms,parlors, libraries, dens, bedrooms, sunrooms, recreationrooms, closets, hallways, or similar rooms or areas shallbe protected by a listed arc-fault circuit interrupter,combination-type, installed to provide protection of the
branch circuit.



Geez, other than kitchens, garages and bathrooms that's the whole home. I have never seen AFCI's on anything but bedrooms here in KS.

Roland Miller
06-07-2013, 12:20 PM
I say not required because it says these rooms....Storage or Equipment Spaces. For attics, underfloor
spaces, utility rooms, and basements, at least one lighting
outlet containing a switch or controlled by a wall switch
shall be installed where these spaces are used for storage or
contain equipment requiring servicing.


You say "no" and quote the NEC where it says "yes". What office do you hold?

Floor--the surface of a structure on which one travels. merriam-webster.com

Ray Thornburg
06-07-2013, 12:43 PM
You say "no" and quote the NEC where it says "yes". What office do you hold?

Floor--the surface of a structure on which one travels. merriam-webster.com

Really.........

Roland Miller
06-07-2013, 03:07 PM
And--verified
"IBC 1009.5.3 requires that enclosed usable space under stairs be protected with 1-hour fire-resistance-rated construction. The only exception to this is for stairs in R-2 or R-3 occupancies.
Note that these requirements do not require the underside of a stairway to have a fire-rated enclosure merely because there is usable space under the stairs. These requirements apply only when the usable space itself is enclosed".

R 311.2.2 requires enclosed accessible spaces under stairs to be protected by 1/2 gypsum.

Jim Luttrall
06-07-2013, 03:49 PM
Geez, other than kitchens, garages and bathrooms that's the whole home. I have never seen AFCI's on anything but bedrooms here in KS.

Code change, only those on the newest code cycle have it. Even some of the more progressive municipalities here still are not on the newest editions. I've only seen it in a handful of properties so far.

- - - Updated - - -

jack davenport
06-07-2013, 04:22 PM
Geez, other than kitchens, garages and bathrooms that's the whole home. I have never seen AFCI's on anything but bedrooms here in KS.
Code change, only those on the newest code cycle have it. Even some of the more progressive municipalities here still are not on the newest editions. I've only seen it in a handful of properties so far.
NOT a recent code change

From the 2008 NEC 210.12(B) All 120 volt single phase, 15 & 20 ampere branch circuits supplying outlets installed in dwelling unit family rooms, dining rooms, living rooms, parlors, libraries, dens, bedrooms, sunrooms, recreation rooms, closets, hallways, or similar rooms or areas shall be protected by a listed arc-fault circuit interrupter, combination-type installed to provide protection of the branch circuit.

- - - Updated - - -


Geez, other than kitchens, garages and bathrooms that's the whole home. I have never seen AFCI's on anything but bedrooms here in KS.

Wait till the 2014 NEC comes out in few months- They added Kitchens and Laundry rooms to the AFCI list

Jerry Peck
06-08-2013, 06:29 AM
Closets do not require lighting outlets unless they fall under storage spaces.


When is a closet NOT used for storage?


Clothes, Closet. A non-habitable room or space intended primarily for storage of garments and apparel. (2011 NEC)

If it does not have a permanently installed clothes rod a lighting outlet is required. I also believe it must be sheetrocked (someone please verify this or not?).

An understair closet requires a lighting outlet as it is intended for use as storage and possibly even is where the water heater is located (I've seen many water heaters located in understair closets, especially in townhouses, and laundry equipment space too).

... even if a closet does have a permanently installed clothes rod and is then a "clothes closet" - how many here have seen clothes closets *not* also used for "storage"? Is a lighting outlet 'required' in a clothes closet' on the floor plan drawing - 'no' .. then house is built and the occupants move in and store stuff in that clothes closet - now 'yes'. ;)

Maybe this is a way to address the issue:
- clothes hanging rod *only* - no light required
- clothes hanging rod *and* a shelf (which is for "storage") - light required
- no clothes hanging rod - light is required

Roland Miller
06-08-2013, 11:10 AM
Since at it very basic definition a stairway is a floor (use your dictionary), the space underneath it is under floor space. If you sheetrock it and enclose it then the NEC requires a lighting outlet because it becomes an underfloor storage space.

Similiarly, an attic without equipment or trusses load rated for storage does not require a lighting outlet. Once you add equipment or use trusses designed to carry 20 pounds per square foot you are required by the NEC to add a lighting outlet(s)..

jack davenport
06-08-2013, 12:35 PM
[QUO TE=Roland Miller;227648 ]Since at it very basic definition a stairway is a floor (use your dictionary), the space underneath it is under floor space. If you sheetrock it and enclose it then the NEC requires a lighting outlet because it becomes an underfloor storage space.

Similiarly, an attic without equipment or trusses load rated for storage does not require a lighting outlet. Once you add equipment or use trusses designed to carry 200 pounds per square foot you are required by the NEC to add a lighting outlet(s)..[/QUOTE]

Please inform us as to which dictionary you are using to base this opinion on. A stairway is a serious of steps that often leads from one floor level to another. Please show me the definition and the dictionary to prove otherwise

Roland Miller
06-08-2013, 01:05 PM
Read post #12.

Jim Port
06-09-2013, 03:23 AM
I agree with Robert, a closet is not one of the items mentioned in the list of things that require a lighting outlet. I am going to disagree with Jerrys definitions as some closets will not even allow the proper clearances to even install a fluorescent light.

A staircase is a transition between floors. Simply because it is walked upon does not make it a floor. Would anyone try to sell a 2 story house with a basement as a 5 floor because of the stairs between floors?

Roland Miller
06-09-2013, 05:49 AM
I always liked the definition of common sense--"the ability to see that something needs done and then do it".

Some of you guys would completely enclose a area under a stairway, put a door on it and not install a lighting outlet because it is not specifically listed in a standard. And then use it for storage and not call it storage space. :clap2:

Jerry Peck
06-09-2013, 05:55 AM
Jim,

You are mixing "floor" with "storey" (or "story").

A "floor" as used is what you walk on, versus a 3 "story" house which may have 5 "floors":
- basement "floor"
- 1st "floor"
- 2nd "floor"
- 3rd "floor"
- attic "floor"

A, yes, a stair is a "floor" as used in the code, but is not a "story" as you are trying to use it.

Al Roden
06-09-2013, 08:53 AM
This storage closet, under the stairs, has a light, but it's a safety hazard - boxes could get stacked right up to the exposed bulb, somebody could turn the light on by accident since the switch is on the outside of the closet, and the house could burn.

However, if I'm reading it right, relocating it per code would seem to require it to be replaced for a fully enclosed fixture and relocating it to the ceiling or the the wall above the door.

Still, wouldn't that be a safety hazard since boxes could be stacked just inside the door or right up to the ceiling? And an enclosure wouldn't prevent boxes from heating up would they? It may take longer to combust since they wouldn't be touching the light bulb, but they'd still heat up, dry out, and eventually combust.

Wouldn't a fluorescent fixture that produces less heat and that is switched on the inside of the closet be a better alternative?

Jerry Peck
06-09-2013, 09:29 AM
Al,

Code does not address all of the stupid things people can do.

Mike Kleisch
06-09-2013, 10:23 AM
This storage closet, under the stairs, has a light, but it's a safety hazard - boxes could get stacked right up to the exposed bulb, somebody could turn the light on by accident since the switch is on the outside of the closet, and the house could burn.

However, if I'm reading it right, relocating it per code would seem to require it to be replaced for a fully enclosed fixture and relocating it to the ceiling or the the wall above the door.

Still, wouldn't that be a safety hazard since boxes could be stacked just inside the door or right up to the ceiling? And an enclosure wouldn't prevent boxes from heating up would they? It may take longer to combust since they wouldn't be touching the light bulb, but they'd still heat up, dry out, and eventually combust.

Wouldn't a fluorescent fixture that produces less heat and that is switched on the inside of the closet be a better alternative?


You can try to make it safer, but you cannot police what people will do 24/7. I agree, above the door is probably best, as people are unlikely to stack items in front of the door. However, have you ever opened a door to only have things fall out at you??? :p

Kind of reminds me of a time when I had a warehouse job in High School. We could stack boxes 24' high, and the Metal Halides were 25' high, never thought about it then, and apparently neither did the manager... other than don't hit the lights, good thing for those wire cages... :shocked:

jack davenport
06-09-2013, 01:47 PM
In reality a stair is made up of steps. Steps are built with treads and risers. Steps, stairs, or stairways are not floors they are steps, stairs, or stairways. But like most misconceptio0ns around here some folks insist on reading more into things to fit their own opinions.

Jerry Peck
06-09-2013, 03:35 PM
In reality a stair is made up of steps. Steps are built with treads and risers. Steps, stairs, or stairways are not floors they are steps, stairs, or stairways. But like most misconceptio0ns around here some folks insist on reading more into things to fit their own opinions.

"Treads" is the name used to refer to the part of the stair you walk on ... i.e., the "floor" surface of the stair.

If you were to take the "floor" where the stair is to go, lay the stair out on the floor, each "tread" you drew on the floor is the "floor" area that, when raised up by the risers, becomes the "tread" of the stair.

Roland Miller
06-09-2013, 04:26 PM
In reality a stair is made up of steps. Steps are built with treads and risers. Steps, stairs, or stairways are not floors they are steps, stairs, or stairways. But like most misconceptio0ns around here some folks insist on reading more into things to fit their own opinions.

At least I read. Your position is based on a misreading of the NEC and the insistance that definitions contained elsewhere do not apply. You are arguing with the NEC and Websters dictionary (not me)--"How is that working for you"?:confused:

Jerry Peck
06-09-2013, 05:42 PM
In reality a stair is made up of steps. Steps are built with treads and risers. Steps, stairs, or stairways are not floors they are steps, stairs, or stairways. But like most misconceptio0ns around here some folks insist on reading more into things to fit their own opinions.

Jack,

I have another visual example for you: a "ramp".

When there is a change in elevation of a floor, you can "cut" the "floor" section out and raise one end of the cut out floor, raise that floor section end and you just created a "ramp" ... the walking surface of the ramp is the "floor" of the ramp - that surface is the floor surface for that area (ramp).

That may be easier to visualize than the "tread" of the stair, although the only real difference is that the ramp floor is angled while the stair floor is separate sections which are kept level while one floor surface (tread) is raised higher than the next raised floor surface (next higher tread).

BARRY ADAIR
06-10-2013, 04:10 AM
there i fixed it! (http://www.sears.com/trademark-cordless-ceiling-wall-light-with-remote-control-light/p-03416425000P?sid=IDx01192011x000001&kpid=03416425000P&kispla=03416425000P)
no sparky required

Al Roden
06-10-2013, 07:04 AM
there i fixed it! (http://www.sears.com/trademark-cordless-ceiling-wall-light-with-remote-control-light/p-03416425000P?sid=IDx01192011x000001&kpid=03416425000P&kispla=03416425000P)
no sparky required

:o I had put that in my report as an option.

Roland Miller
06-11-2013, 09:15 AM
Since the discussion has tapered off, I will assume that everyone sees the importance of looking outside the box we are all in. I was in a state of shock when I first came to know there was 7 feet of shelved books that I needed to read to begin to understand the NEC. Merriam-Webster's dictionary is one of the few dictionaries that contain definitions the US court system will accept.:shocked:

And one of my favorite statements is: "If you want to start an argument ask 2 inspectors the exact same question, then stand back and watch the fun.":)

Dennis Webber
06-11-2013, 09:46 AM
Am I dreaming or not? I think I remember seeing a requirement for under stair storage closet to have a light. Yes or no?

The area under a stairwell (which can be thought of as a closet), does NOT require a light fixture. However, if this area contains any electrical or mechanical equipment which requires service, a wall-switch controlled light fixture would then be required per NEC-110-.26(D), 210.70(A)(3) and M1305.1.4.3 of the ICR (quoting 2009 vs.)


And here is another, do dining room receptacle outlets need AFCI protection or are they technically exempt?
The answer depends on whether your community is using the 2005 NEC, in which case it does NOT, or the 2008 & later NEC, in which case it DOES. See NEC-210.12.
(BTW, the 2014 NEC is going to require AFCI's in kitchens as well).

Roland Miller
06-11-2013, 01:34 PM
The area under a stairwell (which can be thought of as a closet), does NOT require a light fixture. However, if this area contains any electrical or mechanical equipment which requires service, a wall-switch controlled light fixture would then be required per NEC-110-.26(D), 210.70(A)(3) and M1305.1.4.3 of the ICR (quoting 2009 vs.)


And to steal someone else's line "Really?"

Have you been reading all the previous posts?

Jim Port
06-11-2013, 06:58 PM
And to steal someone else's line "Really?"

Have you been reading all the previous posts?


Maybe his area does not interpret it the way your area does. I know none of the ones I have worked in consider the NEC to require lighting in an understair area. I asked one I know if he would require a light and all I heard was a laugh.

Roland Miller
06-12-2013, 05:35 AM
Maybe his area does not interpret it the way your area does. I know none of the ones I have worked in consider the NEC to require lighting in an understair area. I asked one I know if he would require a light and all I heard was a laugh.


That's probably it, Jim. And not everyone will interpret it the way I would.;) Thanks for the input.

William Kading
06-17-2013, 05:57 PM
Re: AFCI for 2014 - Does that mean no more GFCI's in new construction?

- - - Updated - - -



Wait till the 2014 NEC comes out in few months- They added Kitchens and Laundry rooms to the AFCI list[/QUOTE]

Mike Kleisch
06-18-2013, 06:12 AM
Re: AFCI for 2014 - Does that mean no more GFCI's in new construction?

- - - Updated - - -



Wait till the 2014 NEC comes out in few months- They added Kitchens and Laundry rooms to the AFCI list[/QUOTE]

You will have both, I won't have to worry about it for a while as we have not even adopted the 2011 NEC yet, they say it will be soon.

Jim Port
06-18-2013, 01:30 PM
Re: AFCI for 2014 - Does that mean no more GFCI's in new construction?

- - - Updated - - -



Wait till the 2014 NEC comes out in few months- They added Kitchens and Laundry rooms to the AFCI list[/QUOTE]

AFCI and GFI are not the same and serve different purposes. GFI protection will still be required in kitchens, baths, outdoors etc. The technologies are compatible.