View Full Version : Is this a proer p-trap for a HVAC condesation line. I see it a lot.



ren ramsey
07-01-2013, 01:25 PM
http://i333.photobucket.com/albums/m378/ramdino/IMG_8605.jpg (http://s333.photobucket.com/user/ramdino/media/IMG_8605.jpg.html) I see this p-trap a lot. It does not look like it is doing much sloping down hill like that. Obviously he needs a cleanout installed as well. What about the trap? Does it need to go like a " U" like a trap for a sink or would this be fine as long as it ws not on a slope.?

Rick Cantrell
07-01-2013, 01:50 PM
Looks good

Jim Luttrall
07-01-2013, 02:09 PM
This is pretty shallow and has no vent, a "running" trap. Look at the a/c manufacturers requirements to know for sure. Most will specify a certain depth trap to overcome the pressure differential.

Jerry Peck
07-01-2013, 04:49 PM
This is pretty shallow and has no vent, a "running" trap. Look at the a/c manufacturers requirements to know for sure. Most will specify a certain depth trap to overcome the pressure differential.

As Jim said, that's a 'running trap', those are not allowed.

Typically, the minimum trap seal (depth) required is 2", I've seen required depths of 3", 4", 5",