View Full Version : "Sub Panel" Connections



Ken Amelin
10-16-2013, 06:12 AM
This panel is connected to the main service panel and a few things don't look right to me.

1. Can you share ground and neutral bus if a metal nipple is used for close connection? (white tape on neutral wire)

2. Is it OK to have the neutral connections for the two single pole breakers in the sub panel located remotely in the main service panel?

Will Hansen
10-16-2013, 10:06 AM
This panel is connected to the main service panel and a few things don't look right to me.

1. Can you share ground and neutral bus if a metal nipple is used for close connection? (white tape on neutral wire)

2. Is it OK to have the neutral connections for the two single pole breakers in the sub panel located remotely in the main service panel?

The neutrals and EGC's cannot share the same bar in a sub panel. The ground strap needs to be removed and a separate ground bar (not bus) should be installed.

- - - Updated - - -


This panel is connected to the main service panel and a few things don't look right to me.

1. Can you share ground and neutral bus if a metal nipple is used for close connection? (white tape on neutral wire)

2. Is it OK to have the neutral connections for the two single pole breakers in the sub panel located remotely in the main service panel?

The neutrals and EGC's cannot share the same bar in a sub panel. The ground strap needs to be removed and a separate ground bar (not bus) should be installed.

Joe Borkowski
10-16-2013, 10:08 AM
This panel is connected to the main service panel and a few things don't look right to me.

1. Can you share ground and neutral bus if a metal nipple is used for close connection? (white tape on neutral wire)

2. Is it OK to have the neutral connections for the two single pole breakers in the sub panel located remotely in the main service panel?

I see a bonding screw and clip. I believe it should be removed from the sub panel. Not sure about the conduit connection. I think as long as the box is not bonded that it'd OK. Anyone else got an opinion?

Jim Port
10-16-2013, 10:32 AM
The ground bar is missing. Once installed the grounding conductors need to be moved to the ground bus.

All conductors of the circuit need to originate in the same panel.

Mbrooke
10-16-2013, 06:16 PM
Not right, remove neutral buss to case bond, add ground bar, move grounds to new ground bar. Also 2 circuits are going into the main panel rather than having all conductors originate from the the sub.

Ken Amelin
10-17-2013, 03:41 AM
The ground bar is missing. Once installed the grounding conductors need to be moved to the ground bus.

All conductors of the circuit need to originate in the same panel.

Jim,

I get the issue regarding the neutral and ground bars. That's what I thought but just wanted to confirm here.

But what do you mean when you say "All conductors need to "originate" in the same panel. In the photo it looks like all the conductors for the two single pole breakers "originate" in the same panel except that the hot conductors then "protrude" into the adjacent panel.

Can you reference a code section for this comment?
Thanks!

Mike Kleisch
10-17-2013, 07:37 AM
Jim,

But what do you mean when you say "All conductors need to "originate" in the same panel. In the photo it looks like all the conductors for the two single pole breakers "originate" in the same panel except that the hot conductors then "protrude" into the adjacent panel.

Can you reference a code section for this comment?
Thanks!

Thought that was only for MWBC under 210.4(D) Grouping (2008 NEC), I'm interested to know as well.