Okay...i'm having brain dump today. It's been several years since I've had to inspect a metal roof...just a quick double check with you....screw fasteners are not allowed on top of the standing seam or on top of the rake edge flashing, correct?

Jim Robinson
02-06-2014, 05:09 PM
Not sure about "not allowed", but they shouldn't be needed on the standing seam parts. For the rake edge, I'm not getting a visual image of how else it would be fastened to the roof. If they used the typical "pro panel" screws with the rubber washer, I wouldn't be too concerned about it. I don't see it would be any different than the more typical metal panel roof.

Jerry Peck
02-06-2014, 06:33 PM
Are you sure it is a standing seam roof?

With screws into the top of the 'standing seams' is sounds more like you may be describing a ribbed roof panel or V-crimp roof panel.

As Jim said, the rake edge closure/flashing is typically secured with screws, some along the top only (they hook over cleats or clips along the side), some along the top and side, and I think I've even seen some fastened along the side (those hooked over cleats or clips along the top).

Ted Menelly
02-06-2014, 06:52 PM
Any pictures

Marcel Cyr
02-10-2014, 04:17 PM
https://sp1.yimg.com/ib/th?id=H.4557614413710885&pid=15.1



This is one form of standing seam with concealed fasteners.

The OP might have meant this as Jerry suggested.

https://sp2.yimg.com/ib/th?id=H.5007666815831870&pid=15.1

:)