View Full Version : Arc Fault Breaker Temp



Michael Bronner
04-16-2014, 05:58 PM
Gentlemen and Ladies,

Question. At what temperature would you consider an arc fault breaker to be 'too hot' indicating a potential concern? Measured several today that were all around 115*. Other, non arc faults, were all room temperature, 76-77*. I typically find them to them several degrees above non arc faults but not this much warmer.

Thanks

Raymond Wand
04-17-2014, 03:25 AM
The temperature rating should be on the breaker, to my knowledge that should be about 40 celcius/104 fahrenheit.

Dave Hahn
04-21-2014, 06:10 AM
Per the attached from Eaton (a manufacturer of over-current devises, including arc faults), between 80 - 120 F is normal, with higher temps (187 F given as example) still meeting UL listing for the devise.