Any real hazard associated with this?

Jerry Peck
06-09-2014, 07:45 AM
Define "real" and "hazard". :)

Only when something goes not good ("wrong").

Jim Port
06-09-2014, 10:21 AM
The code requires the conductor to terminate in an individual hole. Lug adapters are available for larger,conductors.

Corn Walker
06-10-2014, 08:55 PM
The code requires the conductor to terminate in an individual hole. Lug adapters are available for larger,conductors.

Yeah, but that’s an extra $2.50 and requires the yahoo that did this know what they’re doing. I suppose it’s better than what you normally see: half the strands clipped off and the remainder haphazardly shoved in there.

Bruce Ramsey
06-11-2014, 01:23 PM
Either leg could potentially carry the entire load of the full size wire. Since the leg is roughly half the size of the wire, it is undersized and could overheat leading to fire.

Is there a potential for arcs to jump between the two legs near where they split?

Jim Port
06-11-2014, 01:31 PM
The hazard would be if one were loose forcing the current onto the now undersized conductor. You could get some arcing at the loose connection to the bus.

gary carroll
06-23-2014, 10:22 AM
Yeah, but that’s an extra $2.50 and requires the yahoo that did this know what they’re doing. I suppose it’s better than what you normally see: half the strands clipped off and the remainder haphazardly shoved in there.

I think they did that too, on the top lug.

David Bertrams
06-23-2014, 07:33 PM
That is a listing violation. The equipment label will state what size wire can be in the hole and that ain't it. Strands are broken and damaged.

Marc M
06-24-2014, 12:02 AM
The hazard would be if one were loose forcing the current onto the now undersized conductor. You could get some arcing at the loose connection to the bus.