View Full Version : Main service disconnect 200 amp, panel 125 amp?



Trent Tarter
11-09-2014, 07:35 PM
The homes main electrical service is 200 amps, it's located on a power pole near home and spits off to serve both home and outbuildings. My concern is that the panel in home is rated at 125 amps and has no disconnect other than the main 200 amp. This is the first time is have seen this type of setup, want to make sure I am correct in calling for the homes panel to have a 125 amp disconnect installed.

Jim Port
11-10-2014, 09:15 AM
Were there multiple breakers in the meter main?

Trent Tarter
11-10-2014, 09:26 AM
Were there multiple breakers in the meter main?
No just the 200 amp main at the exterior service entrance.

Jim Port
11-10-2014, 11:00 AM
It sounds like there are several issues. The service is at the pole but the remote panel does not have a means of disconnect along with improper overcurrent protection.

Trent Tarter
11-10-2014, 11:12 AM
It sounds like there are several issues. The service is at the pole but the remote panel does not have a means of disconnect along with improper overcurrent protection.
Yes that appears to be the case, also ground wires in remote panel should be on separate bus bar bonded to panel.

Jerry Peck
11-10-2014, 03:17 PM
Yes that appears to be the case, also ground wires in remote panel should be on separate bus bar bonded to panel.

Along with grounding electrode systems at each building as well as at the pole.

Were the feeders run to the separate buildings from the pole mounted service equipment 3-wire (no separate neutral and ground) or 4-wire (separate neutral and ground)?

Do you know when that work was done?

Trent Tarter
11-10-2014, 03:50 PM
Along with grounding electrode systems at each building as well as at the pole.

Were the feeders run to the separate buildings from the pole mounted service equipment 3-wire (no separate neutral and ground) or 4-wire (separate neutral and ground)?

Do you know when that work was done?
House panel is grounded to water supply pipes only, main service has ground rod. Feeders serving outbuildings were 3-wire. Majority of the outbuilding electrical needs updated and replaced, lots of old fused panels with many improper wiring issues, over sized fuses, no ground rods, etc.

Tom Rees
11-11-2014, 07:23 PM
The homes main electrical service is 200 amps, it's located on a power pole near home and spits off to serve both home and outbuildings. My concern is that the panel in home is rated at 125 amps and has no disconnect other than the main 200 amp. This is the first time is have seen this type of setup, want to make sure I am correct in calling for the homes panel to have a 125 amp disconnect installed.
Trent, When you say it "spits off to serve both home and outbuildings" was the 200 Amp breaker double tapped to feed two sub panels.

Trent Tarter
11-11-2014, 08:13 PM
Trent, When you say it "spits off to serve both home and outbuildings" was the 200 Amp breaker double tapped to feed two sub panels.
No the main 200 amp lugs were not double tapped. This place was a small farm with many outbuildings. It really just needs to be updated to a 320-400 amp service. Outbuilding wiring was a rats nest of old fuse panels and wiring.

Rollie Meyers
11-11-2014, 11:00 PM
That pole mounted panel is a Unicorn, they made a "Pick-A-Amp" breaker based on Zinsco, all you had to do was change the rating plug if you needed 100a or 200A, see photos below. http://i197.photobucket.com/albums/aa308/RFM959/Picture719.jpg (http://s197.photobucket.com/user/RFM959/media/Picture719.jpg.html) Rating plug. http://i197.photobucket.com/albums/aa308/RFM959/Picture716.jpg (http://s197.photobucket.com/user/RFM959/media/Picture716.jpg.html) Unicorn Breaker next to Milbank 3 pole, who bought Unicorn. My question is does the main have that feature?

Dave Ruth
11-14-2014, 05:48 PM
It really just needs to be updated to a 320-400 amp service.

Why? Do they have enough load to justify?