Does anyone see anything wrong with this 100 amp downstream service panel ? Aren't the neutral and grounds suppose to be separated in a aka sub-panel ? Thanks in advance

John Kogel
11-12-2014, 08:04 PM
Yes he should have installed a grounding bus on the back of the panel box for the grounding conductors.

He should have provided grounding to the panel box with a 4th conductor. It is all wrong.

Rollie Meyers
11-12-2014, 10:59 PM
In addition to being wrong because of not having a equipment grounding conductor, the Siemens breakers in that GE panel do not belong there.

Dwight Doane
11-13-2014, 05:23 AM
the Siemens breakers in that GE panel do not belong there.[/QUOTE]

We need to call you Hawk eye . what are you using that allowed you to enlarge the photo from the screen , or do have to save it then open it another application ?

Brian Tilton
11-13-2014, 02:49 PM
Does anyone see anything wrong with this 100 amp downstream service panel ? Aren't the neutral and grounds suppose to be separated in a aka sub-panel ? Thanks in advance

The service feed to the panel box is only two wire wire with a ground, it should be three wire with a ground.

Mike Borchardt
11-13-2014, 05:20 PM
the Siemens breakers in that GE panel do not belong there.

We need to call you Hawk eye . what are you using that allowed you to enlarge the photo from the screen , or do have to save it then open it another application ?[/QUOTE]

Right click on the picture. In the drop down menu select "save picture as". Save the picture in (Pictures) on your computer. Open the (Pictures) on you computer and you can then zoom in on it.

John Kogel
11-13-2014, 07:39 PM
We need to call you Hawk eye . what are you using that allowed you to enlarge the photo from the screen , or do have to save it then open it another application ?


Right click on the picture. In the drop down menu select "save picture as". Save the picture in (Pictures) on your computer. Open the (Pictures) on you computer and you can then zoom in on it.From Brian I got this - Open the pic on your desktop and use 'cntrl' and '+' to zoom.

Rollie Meyers
11-14-2014, 01:37 AM
I just opened the thumbnails, ITE / Siemens breakers are pretty easy to recognize.