During an inspection today I noticed the overhead doors were missing the photo-eyes. I then proceeded to open and then close the door, while standing inside and extending my forearms with bent elbows at waist height to allow the door to come down on my forearms to meet resistance and hopefully return up again. EPIC FAILURE! At the point of resistance at which a door would return up, the upper panel where the opener ties in completely came apart, also damaging the upper panel.
Am I at fault? How would you handle this situation? Both the potential buyer and homeowner witnessed the ordeal. Come to find out the photo-eyes were mounted on the ceiling behind the opener.

Thanks a bunch,
Chad Webster

Nick Ostrowski
05-26-2015, 02:38 PM
Door failed under testing - repairs/replacement needed...

It doesn't sound like you did anything out of the ordinary in checking the operability of a standard safety feature for the door and opener. The fact that the motion beam sensors were mounted on the ceiling behind the opener is an indicator alone that the the installation was wrong.

Did the homeowner say if the door or opener were newer? Any pics you can post of the aftermath?

Dom D'Agostino
05-26-2015, 04:56 PM
Your testing methods aren't correct. That outstretched arm test has bested many inspectors and busted many doors.

You should have seen the photo eyes before operating the motor (they weren't missing). Although not a sure thing, that may have provided clues to "be on the look out" for more issues. The upper panel may have had visible clues of damage, improper installation, or a missing support brace.

Did you operate the door manually first?

Dom.

Jack Feldmann
05-26-2015, 05:41 PM
I'm with Dom. You didn't test the door properly.
Regardless how the sensors were mounted, you didn't test it correctly.
Pay for the repair and consider it a "stupid tax" (as Dave Ramsey likes to call it).

Mark Reinmiller
05-26-2015, 05:53 PM
I normally don't think an inspector is responsible if something fails during normal operation. But, knowing that the sensors were not in place would be enough for me to question the installation.

I have also learned from experience that if metal doors do not have proper reinforcing at the top panel they can fail. When sensors are not present and if the door is reinforced I put a little resistance against the door as it closes. If it does not reverse with relatively light pressure I suggest adjustment and then testing.

If a company installed the opener that way, the owner should go after them. It is not only against manufacturer's requirements to not install the sensors 4-6 inches above the floor, it also violates federal laws.

Scott Patterson
05-26-2015, 06:14 PM
I hate to agree with my brethren, but you screwed up. The method you used is not approved by any manufacturer or their garage door association for testing any door or opener. It sounds like an old door and opener and more than likely did not have the reversing feature. Many inspectors have fallen prey to this method of testing and have watched the door buckle and in some cases fall.

I only swing my foot in front of the eyes and I test the doors balance. I do not test the pressure reversing feature for the very reason you discovered. The proper way to test the reversing feature is with a 2x4 on the ground.

Garry Sorrells
05-26-2015, 06:31 PM
Chad,
Without seeing the installation of the opener and the door my thought is that you are not at fault. Your location for testing can have some effect on extent of damage on failure of operation functions. But the door properly installed and adjusted will reverse at any point of operation except within the last 1 inch of meeting floor.

Based on what you described my guess is the following.
1) Single panel metal door.
2) No reinforcement on the door at the opener/door connection.
3) Photo-eyes were mounted on the ceiling behind the opener suggest that the opener was new enough to be adjustable for it opening and closing functions.
4) With the eyes on the ceiling the entire installation is suspect. Though I know why they were put there.
5) Door failed to reverse on meeting an obstruction and resulting damage is directly a result of the installation method and adjustment, not the person testing its operation.

The seller/owner is responsible for repairs.

Jack Feldmann
05-26-2015, 08:06 PM
I just happen to have a brochure for garage door openers on my desk, and this is what is says...

Test the reversing feature every month

First, test the balance of the door. If the door is properly balanced, then proceed.

With the door fully open, place a 1-1/2" thick piece of wood (a 2x4 laid flat) on the floor in the center of the door.

Push the transmitter or wall button to close the door. The door must reverse when it strikes the wood.

If the door does not reverse, have it repaired or replaced. Have a qualified individual adjust, repair, or replace the opener or door.

John Kogel
05-26-2015, 08:17 PM
Early in my career if you can call it that I busted a garage window stopping it with my hand. Now I let them go down if they insist on carrying on. It is a subtle thing and I understand why some guys use a roll of paper towels instead of a 2 X 4.
I hate witnesses. Next time you will look before you leap and let it go before it breaks itself. :D

I bought a piece of glass and fixed the door, with help from the owner, who was good about it.

Nick Ostrowski
05-27-2015, 02:36 AM
Well, then I stand corrected and it seems I have been testing this feature incorrectly all along. if the proper way to test this feature is with a piece of wood, that seems like an even more likely way to induce damage to the door. I see garage doors that regularly will not stop with my arm pressure and I can only imagine how many doors might get damaged/bent if I put a solid piece of wood beneath them.

Is the idea behind using a 2x4 to limit the amount of damage to the door if it will not stop since it will be a short travel at that point in how close it is to being fully closed?

chad webster
05-27-2015, 02:38 AM
Ok gang,
Your insight has been helpful. The method of testing is how I was instructed to use in my certification classes. We were told specifically not to use a 2x4. I did not look for any reinforcement in the upper panel, therefor, I believe I have just learned a lesson the hard way. I would much rather repair the door than my reputation.
Thanks very much,
Your professionalism is much appreciated,
Chad

Garry Sorrells
05-27-2015, 02:55 AM
Chad,
Without knowing all of what you were taught, all doors should reverse at any point that they meet an obstruction with the exception of 1"inch from floor. Conversely they door should also stop if it meets resistance as it opens.

In your case I think it may be more about what you were taught to look for in the door installation. Things that clue you in that provide you with an expectation of some potential operational issue that may cause a failure.

There are several threads that have discussed testing methodology take a look.

Jim Hintz
05-27-2015, 07:38 AM
Personally, I wait till the door is a bit above knee-high, put my hand (backhanded) under the door and put a little resistance into it - if it hurts my back before the door reverses, I let go and write it up or adjust it myself while showing the new owner how and why it's done...... Just adjusted one yesterday as a matter of fact. Sometimes it's easier to fix something that to spend the time to write it up... JMO.

CHARLIE VAN FLEET
05-27-2015, 05:38 PM
CHAD
I always open door first and check to see if door hardware is secured-most wood framed doors you will find loose hardware. then I test eye for operation--next I let door come down waist high and use my hands to put resistance on for reversal.if it doesn't work I adjust it and show client how and where to do it. so i don't have to write it up--ljke finding loose cabinet hinges

cvf

Mark Reinmiller
05-27-2015, 06:09 PM
Chad,
Without seeing the installation of the opener and the door my thought is that you are not at fault. Your location for testing can have some effect on extent of damage on failure of operation functions. But the door properly installed and adjusted will reverse at any point of operation except within the last 1 inch of meeting floor.

Based on what you described my guess is the following.
1) Single panel metal door.
2) No reinforcement on the door at the opener/door connection.
3) Photo-eyes were mounted on the ceiling behind the opener suggest that the opener was new enough to be adjustable for it opening and closing functions.
4) With the eyes on the ceiling the entire installation is suspect. Though I know why they were put there.
5) Door failed to reverse on meeting an obstruction and resulting damage is directly a result of the installation method and adjustment, not the person testing its operation.

The seller/owner is responsible for repairs.

But, assuming #2 is correct, then testing the reversing feature is a bed idea.

Jerry Peck
05-27-2015, 06:11 PM
Two inspectors stating that they "fix things" instead of writing the items up - it is NEVER "easier" to "fix" something than it is to "write it up" ... unless one is a very poor writer ...

Besides that - YOU NOW HAVE THE LIABILITY for "adjusting"/"fixing" it!

If you have insurance - does your insurance company know that you "fix"/"adjust" things?

I bet they would be very interested in knowing just what you are doing besides "inspecting" because they are the ones who YOU think will write the big check, but ... they will find it much "easier" to tell you - 'Sorry, YOU "fixed"/"adjusted" it, now YOU bought it, and we (the insurance company) are out of the picture.' 'Oh, and that classic Mustang which the door fell on and crushed ... that is now yours and you get to buy another one for the owner.'

What if the garage door failed to properly reverse and a person was crushed - how are you going to explain it to the judge that 'all you did was a minor adjustment' ... yeah, and that minor adjustment just killed someone.

I can't believe some of the things I am reading here lately.

michael Rodney
05-27-2015, 07:39 PM
I hate to agree with my brethren, but you screwed up. The method you used is not approved by any manufacturer or their garage door association for testing any door or opener. It sounds like an old door and opener and more than likely did not have the reversing feature. Many inspectors have fallen prey to this method of testing and have watched the door buckle and in some cases fall.<br>
<br>
I only swing my foot in front of the eyes and I test the doors balance. I do not test the pressure reversing feature for the very reason you discovered. The proper way to test the reversing feature is with a 2x4 on the ground.<br>
<br>
<br>
I agree with Scott: I too only swing my foot a between the eyes. The door should stop and then reverse. The pressure test should be done with a piece of 2x4, but I do not do that test. I have a narrative in my reports saying which tests are done, which ones are not and why.

Garry Sorrells
05-28-2015, 03:08 AM
2) No reinforcement on the door at the opener/door connection.


But, assuming #2 is correct, then testing the reversing feature is a bed idea.

Precisely my point. You have to first inspect the entire door installation and the door itself before you touch anything. Don't care if you think that the owner has been using it for 20 years without any issues. Only after inspecting the installation and finding no flaws that would effect the operation would you then engage the electric opener and perform any other testing of operations.

More to the point for the no reinforcement issue, if the door should have it and it doesn't then I would not operate it with the opener. Only by hand. If the owner is present then have them demonstrate the operation and the monthly testing that they are performing.:wink:

Normally there are some telltale signs that non correctly reinforced doors have been stressed, but you have to look and be able to recognize those signs.

Jerry Peck
05-28-2015, 06:40 AM
Is the idea behind using a 2x4 to limit the amount of damage to the door if it will not stop since it will be a short travel at that point in how close it is to being fully closed?

No, but any damage will likely be less for that reason. With the door nearly vertical and nearly at the end of its travel - at 1-1/2" above the floor the door is almost ready for the operator to push the top tight to the wall as the bottom of the door closes against the floor - there shouldn't be much room for damage with a properly placed 2x4 and a door which has first been inspected to make sure the stiffener/brace is properly present and that there are not other signs of impending failure.

The door is not intended to try to crush the 2x4, the 2x4 is intended to provide a good, solid, repeatable, resistance at 1-1/2" high above the floor, and the door is intended to reverse on contact with the 2x4 ... not while one watches to see if the door can crush the 2x4 :) .

Of course, though, I always looked to see how high the track would bow upward when the opener was trying to crush the 2x4 ... yeppers, that one did not automatically reverse either nor could it crush the 2x4 either - something must be wrong with it ... :biggrin:

Lloyd Goldrick
05-28-2015, 01:38 PM
Greetings from Ohio,
During an inspection today I noticed the overhead doors were missing the photo-eyes. I then proceeded to open and then close the door, while standing inside and extending my forearms with bent elbows at waist height to allow the door to come down on my forearms to meet resistance and hopefully return up again. EPIC FAILURE! At the point of resistance at which a door would return up, the upper panel where the opener ties in completely came apart, also damaging the upper panel.
Am I at fault? How would you handle this situation? Both the potential buyer and homeowner witnessed the ordeal. Come to find out the photo-eyes were mounted on the ceiling behind the opener.

Thanks a bunch,
Chad Webster

Regardless of the method used to test the reversing operation, it is hard to see how you are liable, but then risk management in most jurisdictions is litigation averse so they may pay damages anyway. It is annoying however. I shudder to think what the result would have been if an elderly person was bent over & hobbling thru that door way while it was in operation. Likely the door would have been damaged just as it was in your test, but an elder would most likely also have been put on the ground with injuries. Lawyers tend to muddy the clearest water & like it or not your jurisdiction may end up settling by paying the cost of repairs.

Nick Ostrowski
05-28-2015, 01:40 PM
I would have to say my rub with this accepted testing method is it does not replicate a real world scenario. If the bottom of the door is only 1.25" away from the garage floor, anything in it's way at that point is not going to be of any great value. A real world scenario is a car parked halfway out of the garage and somebody accidentally sends the door down. Yes, the door does need to be properly installed to begin with but the accepted testing method does not accurately depict how the door and feature will perform under a real world situation.

Jerry Peck
05-28-2015, 06:23 PM
I would have to say my rub with this accepted testing method is it does not replicate a real world scenario.
.
.
Yes, the door does need to be properly installed to begin with but the accepted testing method does not accurately depict how the door and feature will perform under a real world situation.

The 2x4 test accurately represents the tests required for the manufacturers.

Do you want to use a standard recognized test or a test which has not real meaning?

If the door reverses on contact with the 2x4, that is the test for the standard recognized auto reverse feature, and ... it is likely shown depicted in the form of a drawing on a label on every garage door and has text stating how the test is done. I am not sure, but I think that label is required to be placed on the garage door which has an operator attached to it.

Do it the way that label says. We do not seem to have a problem referring to manufacturer's installation and operating instructions for other items ... why do we have it for garage door operators, especially when it is a larger item and has a great potential for killing or injuring someone?

Mark Reinmiller
05-28-2015, 06:30 PM
I would have to say my rub with this accepted testing method is it does not replicate a real world scenario. If the bottom of the door is only 1.25" away from the garage floor, anything in it's way at that point is not going to be of any great value. A real world scenario is a car parked halfway out of the garage and somebody accidentally sends the door down. Yes, the door does need to be properly installed to begin with but the accepted testing method does not accurately depict how the door and feature will perform under a real world situation.

I am not defending the accepted test procedure. I have not tried it, but suspect an improperly braced door could be damaged if tested that way. Of course, whoever came up with the test probably did not test door under real word conditions.

The point of the safety reverse feature is not to protect your car, but your kids. That is why the sensors are supposed to be 4 to 6 inches above the floor.

Nick Ostrowski
05-28-2015, 07:09 PM
OK, then what is the purpose of the mechanical reverse feature? The motion beam sensors (to me) are for kids. What is the mechanical reverse feature for? What is it supposed to save/prevent?

Jim Luttrall
05-28-2015, 09:32 PM
OK, then what is the purpose of the mechanical reverse feature? The motion beam sensors (to me) are for kids. What is the mechanical reverse feature for? What is it supposed to save/prevent?
Important redundancy. If I am not mistaken, the auto reverse / obstruction feature came first and the sensor beam was added to the mix at a later date. Belt and suspenders to prevent entrapment.

Rick Cantrell
05-29-2015, 03:54 AM
OK, then what is the purpose of the mechanical reverse feature? The motion beam sensors (to me) are for kids. What is the mechanical reverse feature for? What is it supposed to save/prevent?
The reverse on contact is an "Anti-entrapment" feature and offers additional safety that the photo beams does not provide.
Photo beams are 4"-6" above the floor. An arm or leg can be under the door yet not trip the photo beam.

Garry Sorrells
05-29-2015, 05:28 AM
......... Of course, whoever came up with the test probably did not test door under real word conditions.

The point of the safety reverse feature is not to protect your car, but your kids. That is why the sensors are supposed to be 4 to 6 inches above the floor.


OK, then what is the purpose of the mechanical reverse feature? The motion beam sensors (to me) are for kids. What is the mechanical reverse feature for? What is it supposed to save/prevent?

The criteria for the operator functions were developed by UL and the Consumer Product Safety Commission. The UL criteria was then incorporated into federal requirements.

The UL looked at several situations that may (actually have) occurred when they developed the reversal requirements (specifications). These were two real world situations that occurred.
a) Door closing and encountering someone on a ladder.
b) Door closing and encountering someone standing in opening.
For a and b above the person being struck by the door could then collapse where the door would continue down to crush them if it did not reverse. If the door only were to stop it could cause enough pressure and restriction to cause death. Or as in one case the person was trapped and unable to extricate themselves. In that case it was a long time before someone found the trapped person. So there was a 1" requirement created that they thought would cover everything and still allow the door to compress the bottom seal effectively.

After the reversal requirements were created they found that there were injuries to children from being crushed (compressed) by the door before it did reverse. {{{ Remember there is no requirement for amount of pressure (PSI) exerted by the door, just time of contact before reversal (2 seconds).}}} So the UL came up with the sensor beam that stops the door if there is something on the floor such as a child, old frail people or HIs interrupting the beam.

The use of a 2x4 (actual 1.5" by 3.5") block became excepted as a testing mechanism, since it was a commonly available item that came close to the actual UL testing criteria measurement. The block on the floor creates a testing condition that limits the potential liability of personal injury. The liability is what so many fret about to a paranoid extreme.

In the real world installers test the operator reverse function at around 3 or 4 feet from floor. It is a relatively passive creation of a presumed obstruction that may occur. It is not a Hulk Hogan wrestling match with the door.

Now let me say that the most of the door operators on the market have been redesigned and they have an entirely different system that causes the motor to reverse. In addition the operators have a different method to set the travel distances of the door operation, travel limits. Some manufactures refer to a self learning function of the operator. Takes some of the fun out of installation and maintenance.

As a side note: don't forget older doors still have manual adjustments that effect operator functions which will cause damage to the door is not correct.

Mark Reinmiller
05-29-2015, 04:46 PM
If memory serves me correct, the door is supposed to reverse when it encounters no more than 15 pounds of resistance.

Although it is not the correct test method, that is why I use my hands, because I can judge when the resistance seems to be too much and let go before the door breaks (this assumes the door is properly braced). If anything looks questionable, I don't test that feature.

I'm not saying my method is correct, it is just what I have done for the past 30 years.

Garry Sorrells
05-30-2015, 05:05 AM
If memory serves me correct, the door is supposed to reverse when it encounters no more than 15 pounds of resistance.

Although it is not the correct test method, that is why I use my hands, because I can judge when the resistance seems to be too much and let go before the door breaks (this assumes the door is properly braced). If anything looks questionable, I don't test that feature.

I'm not saying my method is correct, it is just what I have done for the past 30 years.

Mark,
The discussion I hope has been about an overhead sectional vertical tracked door, else it is apples and oranges type of discussion. Also specifically discussing the anti entrapment function of the operator itself and not a secondary sensor. Therefore; No, there is no PSI involved in the reversal requirement on an over head sectional vertical tracked door operator. It is a time on contact function to meet requirements.

I contacted the UL for a clarification to the question of PSI involved with the requirements that must be met with a door operator.
A portion of an email 4/21/12 from: UL, Jim Miller, P.E. Senior Project Engineer

Residential garage door operators are also required to be provided with inherent entrapment protection (in addition to the external entrapment protection), where the door is required to reverse within 2 s a minimum of 2 in. But there are currently no requirements for the amount of the force that is allowed, just needs to reverse.


Some of the actual nitty gritty for those interested:
http://www.gpo.gov/fdsys/pkg/CFR-2012-title16-vol2/pdf/CFR-2012-title16-vol2-part1211.pdf

§ 1211.7 Inherent entrapment protection requirements.
(a)(1) Other than for the first 1 foot (305mm) of door travel from the full upmost position both with and without any external entrapment protection device functional, the operator of a downward moving residential garage door shall initiate reversal of the door within 2 seconds of contact with the obstruction as specified in paragraph (b) of this section.



The 15LB is from:
Underwriters Laboratories ( UL )
UL 325 Sec. 36
36 Edge Sensors
36.1 Normal operation test
36.1.1 When installed on a representative residential door edge, an edge sensor shall actuate upon the application of a 15 lbf (66.7 N) or less force in the direction of the application. For an edge sensor intended to be used on a sectional door, the force is to be applied by the longitudinal edge of a 1-7/8 in (47.6 mm) diameter cylinder placed across the sensor so that the axis is perpendicular to plane of the door. For an edge sensor intended to be used on a one piece door, the force is to be applied so that the axis is at an angle 30 degrees from the direction perpendicular to the plane of the door.

Then it shows up in:
§ 1211.12 Requirements for edge sensors.
(a) Normal operation test. (1) When installed on a representative door edge, an edge sensor shall actuate upon the application of a 15 pounds (66.7 N) or less force in the direction of the application. For an edge sensor intended to be used on a sectional door, the force is to be applied by the longitudinal edge of a 17⁄8 inch (47.6 mm) diameter cylinder placed across the switch so that the axis is perpendicular to the plane of the door. For an edge sensor intended to be used on a one piece door, the force is to be applied so that the axis is at an angle 30 degrees from the direction perpendicular to the plane of the door. See figure 6.
(2) With respect to the test of paragraph (a)(1) of this section, the test is to be repeated at various representative points of the edge sensor across the width of the door.
(3) Exception: The edge sensor need not be sensitive to actuation two inches (50.4mm) or less from each end of the intended width of the door opening.


§ 1211.13 Inherent force activated secondary door sensors.
(a) Normal operation test. (1) A force activated door sensor of a door system installed according to the installation instructions shall actuate when the door applies a 15 pound (66.7 N) or less force in the down or closing direction and when the door applies a 25 pound (111.2 N) or less force in the up or opening direction. For a force activated door sensor intended to be used in an operator intended for use only on a sectional door, the force is to be applied by the door against the longitudinal edge of a 17⁄8 (47.6 mm) diameter cylinder placed across the door so that the axis is perpendicular to the plane of the door. See Figure 6 of this part. The weight of the door is to be equal to the maximum weight rating of the operator.

Lon Henderson
05-30-2015, 07:16 AM
This has been a topic of several other threads which also have gone "hot". There are links to code, federal guidelines, and manufacturer's instructions in those other threads. Some manufacturers use the "hand" test to set the obstruction sensor. But none of the manufacturers recommend grabbing the door around waist level.

While you didn't use a recommended opener test, you still found a defect. Obstructions can occur at any height. Tell the parties of this transaction that you found a defect, possibly prevented damage to that classic Mustang, or worse, injury to a kid who left his/her bicycle in the door path. The seller incorrectly installed or failed to correct the installation of the opener, and that is where the fault lies.

For the future, revise your testing methods.

Mark Reinmiller
05-30-2015, 05:17 PM
Mark,
The discussion I hope has been about an overhead sectional vertical tracked door, else it is apples and oranges type of discussion. Also specifically discussing the anti entrapment function of the operator itself and not a secondary sensor. Therefore; No, there is no PSI involved in the reversal requirement on an over head sectional vertical tracked door operator. It is a time on contact function to meet requirements.

I contacted the UL for a clarification to the question of PSI involved with the requirements that must be met with a door operator.
A portion of an email 4/21/12 from: UL, Jim Miller, P.E. Senior Project Engineer

Residential garage door operators are also required to be provided with inherent entrapment protection (in addition to the external entrapment protection), where the door is required to reverse within 2 s a minimum of 2 in. But there are currently no requirements for the amount of the force that is allowed, just needs to reverse.


Some of the actual nitty gritty for those interested:
http://www.gpo.gov/fdsys/pkg/CFR-2012-title16-vol2/pdf/CFR-2012-title16-vol2-part1211.pdf

§ 1211.7 Inherent entrapment protection requirements.
(a)(1) Other than for the first 1 foot (305mm) of door travel from the full upmost position both with and without any external entrapment protection device functional, the operator of a downward moving residential garage door shall initiate reversal of the door within 2 seconds of contact with the obstruction as specified in paragraph (b) of this section.



The 15LB is from:
Underwriters Laboratories ( UL )
UL 325 Sec. 36
36 Edge Sensors
36.1 Normal operation test
36.1.1 When installed on a representative residential door edge, an edge sensor shall actuate upon the application of a 15 lbf (66.7 N) or less force in the direction of the application. For an edge sensor intended to be used on a sectional door, the force is to be applied by the longitudinal edge of a 1-7/8 in (47.6 mm) diameter cylinder placed across the sensor so that the axis is perpendicular to plane of the door. For an edge sensor intended to be used on a one piece door, the force is to be applied so that the axis is at an angle 30 degrees from the direction perpendicular to the plane of the door.

Then it shows up in:
§ 1211.12 Requirements for edge sensors.
(a) Normal operation test. (1) When installed on a representative door edge, an edge sensor shall actuate upon the application of a 15 pounds (66.7 N) or less force in the direction of the application. For an edge sensor intended to be used on a sectional door, the force is to be applied by the longitudinal edge of a 17⁄8 inch (47.6 mm) diameter cylinder placed across the switch so that the axis is perpendicular to the plane of the door. For an edge sensor intended to be used on a one piece door, the force is to be applied so that the axis is at an angle 30 degrees from the direction perpendicular to the plane of the door. See figure 6.
(2) With respect to the test of paragraph (a)(1) of this section, the test is to be repeated at various representative points of the edge sensor across the width of the door.
(3) Exception: The edge sensor need not be sensitive to actuation two inches (50.4mm) or less from each end of the intended width of the door opening.


§ 1211.13 Inherent force activated secondary door sensors.
(a) Normal operation test. (1) A force activated door sensor of a door system installed according to the installation instructions shall actuate when the door applies a 15 pound (66.7 N) or less force in the down or closing direction and when the door applies a 25 pound (111.2 N) or less force in the up or opening direction. For a force activated door sensor intended to be used in an operator intended for use only on a sectional door, the force is to be applied by the door against the longitudinal edge of a 17⁄8 (47.6 mm) diameter cylinder placed across the door so that the axis is perpendicular to the plane of the door. See Figure 6 of this part. The weight of the door is to be equal to the maximum weight rating of the operator.







1211.13 diffuses secondary reversing sensors and 15 pounds of force. As far as I recall the photo eyes force sensors and 2 second reverse are required. I think the info in the email is incomplete.

Garry Sorrells
05-30-2015, 06:28 PM
1211.13 diffuses secondary reversing sensors and 15 pounds of force. As far as I recall the photo eyes force sensors and 2 second reverse are required. I think the info in the email is incomplete.

Door operator (motor) is primary § 1211.7 , with no other sensors on door edge, which is the 2 second contact criteria to reverse with no consideration of amount of force (pressure,PSI) applied at contact point by the operator.

A secondary sensor such a edge sensor, on bottom edge, is what the 15lb is referring to and works differently than the operator sensor. § 1211.13 Inherent force activated secondary door sensors.

The email was directed at the standard vertical sectional door operator and if there was any consideration by UL on the PSI excreted on contact to trigger reversal of the door. PSI was not a consideration on the UL reversal requirements that formed the basis for primary operator sensor.

The photo eyes are separate having no connection to door sensor requirement and are required with either § 1211.13 or § 1211.7

Mark Reinmiller
05-31-2015, 06:21 PM
The email was directed at the standard vertical sectional door operator and if there was any consideration by UL on the PSI excreted on contact to trigger reversal of the door. PSI was not a consideration on the UL reversal requirements that formed the basis for primary operator sensor.



I understand what the original email was about. My point, if I was not clear, is that even with the photo eye sensors, door openers still have a mechanical reversing feature and this should reverse the door at 15 pounds of force (not PSI).

Garry Sorrells
06-01-2015, 06:30 AM
I understand what the original email was about. My point, if I was not clear, is that even with the photo eye sensors, door openers still have a mechanical reversing feature and this should reverse the door at 15 pounds of force (not PSI).

Leaving the photo eye sensor out of discussion. Photo eye are add on accessories to the door installation and operator and operates independently.

Yes and no. Apples and oranges on what happens at the bottom edge of the door.

**Yes - The door operator(motor) with no other edge sensor installed on the door does have a reversing feature (internal mechanism/design) that is integrated into the operator motor that senses the non movement of the door. It is required to reverse the door when the motor fails to move the door for 2 seconds. There is no criteria of force used or exerted by the motor on the door by the motors arm connection to the door. There is no sensor on the door edge. It is all about the actual operator (motor) design and how it functions. The specific technical design that is used in the motor circuit board that determines that door is not moving is not specified by UL. Just that the operator (motor) recognize it is not moving the door and then in 2 seconds or less reverse the motor direction and thus reverse the door.

Lets approach it in a different way. If you were to block the top roller in the track of the 2nd door panel from the top. The roller being prevented from movement will cause the door to stop. The motor senses that the door is not moving and will reverse. Nothing is in contact with the bottom edge of the door. For this type of reversal the bottom edge is just another point that the door could be blocked from movement(travel).

**No - The typical garage door does not have an edge sensor (mechanism) built into it. The typical edge sensor is actually added to the door, optional feature. There are two contact strips enclosed in a full length rubber tube that is attached on the bottom edge of the door. When the two contact strips come in contact with each other the result is to trigger a switch that reverses the motor. This attached tube edge is to be activated if
"§ 1211.12 Requirements for edge sensors.
(a) Normal operation test. (1) When installedon a representative door edge, an edge sensor shall actuate upon the application of a 15 pounds (66.7 N) or less force in the direction of the application. For an edge sensor intended to be used on a sectional door, the force is to be applied by the longitudinal edge of a 17⁄8 inch (47.6 mm) diameter cylinder placed across the switch so that the axis is perpendicular to the plane of the door. ...." or
"§ 1211.13 Inherent force activated secondary door sensors"


The test is to cause the contact strips to meet with 15lbs of force exerted on them. This is ot occur at 1 7/8 inches from the floor as a minimum measurement. You could also push on the edge sensor at any point of the downward movement of the door and it will require 15 lbs to cause the contact strips to meet and than reverse the door. It is correct that this is not specified as 15 PSI and that PSI is not involved in any of the criteria as a measurement to cause reversal function of the door operator.


Why they chose a cylinder as apposed to a block of wood must have some rational, I can not say for sure. It may be due to typical edge sensor thickness and enclosure design. Making them use a 2" or less outside diameter tube to house the contact strips. Or, distance between the internal contact points if so designed. Before I hear it, contract strips are not the only type of design used on the edge sensors.


It would be interesting for someone to do math to determine the PSI that is exerted on the cylinder as the 15lbs of force is generated. You would have to take into account the deflection of the circuit enclosure over the cylinder. For my part I am to lazy to do that. Definitely would have to break out my physics and calculus books to develop the formula. BUT I would love someone else to do that. Though it would have to be adjusted for different edge sensor designs.

So in a recap.
--Door without an Edge Sensor ( see § 1211.7 ) added to it requires 2 seconds or less of movement at 1" from floor, but a 2x4 wood block that is 1 1/2" thick is also acceptable to do monthly test.

-- Door with an Edge Sensor (see § 1211.12 , § 1211.13 ) added to it requires a maximum 15lb of force to be exerted on a 1 7/8" cylinder located on floor.

Allen Ingling
06-01-2015, 04:31 PM
If memory serves me correct, the door is supposed to reverse when it encounters no more than 15 pounds of resistance.

Although it is not the correct test method, that is why I use my hands, because I can judge when the resistance seems to be too much and let go before the door breaks (this assumes the door is properly braced). If anything looks questionable, I don't test that feature.

I'm not saying my method is correct, it is just what I have done for the past 30 years.

I appreciate all the good technical remarks by my many learned colleagues but Mark hits the "mark" in my opinion. I have tested many, many doors, long before the "eyes" came out and I would never stick a solid object in the path of a moving door. That could cause a lot of expensive unnecessary damage. I always do just as Mark does, I wait until the door is about thigh high and grasp the bottom with one hand. If I can't stop it, its a write up with strong warning not to ignore the condition, but to get a competent technician to fix it. I have never broken a door and I am pretty sure I have not caused any unnecessary alarm. If I can't stop the door then the force of the door would be enough to kill someone's cat or dog or severely injure a child.

- - - Updated - - -


If memory serves me correct, the door is supposed to reverse when it encounters no more than 15 pounds of resistance.

Although it is not the correct test method, that is why I use my hands, because I can judge when the resistance seems to be too much and let go before the door breaks (this assumes the door is properly braced). If anything looks questionable, I don't test that feature.

I'm not saying my method is correct, it is just what I have done for the past 30 years.

I appreciate all the good technical remarks by my many learned colleagues but Mark hits the "mark" in my opinion. I have tested many, many doors, long before the "eyes" came out and I would never stick a solid object in the path of a moving door. That could cause a lot of expensive unnecessary damage. I always do just as Mark does, I wait until the door is about thigh high and grasp the bottom with one hand. If I can't stop it, its a write up with strong warning not to ignore the condition, but to get a competent technician to fix it. I have never broken a door and I am pretty sure I have not caused any unnecessary alarm. If I can't stop the door then the force of the door would be enough to kill someone's cat or dog or severely injure a child.

- - - Updated - - -


If memory serves me correct, the door is supposed to reverse when it encounters no more than 15 pounds of resistance.

Although it is not the correct test method, that is why I use my hands, because I can judge when the resistance seems to be too much and let go before the door breaks (this assumes the door is properly braced). If anything looks questionable, I don't test that feature.

I'm not saying my method is correct, it is just what I have done for the past 30 years.

I appreciate all the good technical remarks by my many learned colleagues but Mark hits the "mark" in my opinion. I have tested many, many doors, long before the "eyes" came out and I would never stick a solid object in the path of a moving door. That could cause a lot of expensive unnecessary damage. I always do just as Mark does, I wait until the door is about thigh high and grasp the bottom with one hand. If I can't stop it, its a write up with strong warning not to ignore the condition, but to get a competent technician to fix it. I have never broken a door and I am pretty sure I have not caused any unnecessary alarm. If I can't stop the door then the force of the door would be enough to kill someone's cat or dog or severely injure a child.

Mark Reinmiller
06-01-2015, 06:20 PM
Garry, Bottom line is that every door opener I have seen constructed since 1993 has photo eyes AND a reversing clutch that is adjustable for force. Forget the edge sensors. I have never seen any. If this is not clear, then look at any opener or instruction manual. The resistance clutch is present in addition to the photo eyes.

Jerry Peck
06-01-2015, 07:23 PM
The resistance clutch is present in addition to the photo eyes.

To put it in the correct order ... the photo eyes are in addition to the motor mechanically/electrically reversing from the door making contact.

The mechanical/electrical reversing came first, the photo eyes came second.

Garry Sorrells
06-02-2015, 03:15 AM
To put it in the correct order ... the photo eyes are in addition to the motor mechanically/electrically reversing from the door making contact.

The mechanical/electrical reversing came first, the photo eyes came second.


Isn't it great to be old enough to know what it was like before the wheel??? :clap2:
Kinda like before all cars came with AC in the standard package, AC non existent then an option then no thought that it is there.

Garry Sorrells
06-02-2015, 03:27 AM
Garry, Bottom line is that every door opener I have seen constructed since 1993 has photo eyes AND a reversing clutch that is adjustable for force. Forget the edge sensors. I have never seen any. If this is not clear, then look at any opener or instruction manual. The resistance clutch is present in addition to the photo eyes.

But, the UL and the Fed Regs do not use force as the criteria for reversal in doors without Edge Sensors. Though you may believe that you are adjusting the force exerted to reverse. The Regs deal only with time. I also was under the misconception that when I adjusted the operator I was working with force. I always set sensitivity to the highest point that I could and still have the door close. Which is why in another thread when Force or PSI was in discussion I contacted UL to see if they had any pressure criteria involved in testing protocol to meet requirements for installation. The answer was no, unless the door had an Edge Sensor. I have not tried to tracking down someone who actually was on the team that came up with their final protocal that has been implemented. Why they did not have force as a factor in the operator protocol for field testing would be interesting to know. Also I have not gone to the effort to see exactly how much force or PSI is being exerted when the maximum allowed (2 sec) contact takes place. A project to add to the list of thing to do one day.

Different doors have edge seals that vary in their stiffness and how much pressure it takes to compress them. Then there are the optional seals (bigger) that the standard shipped with the door that take even more pressure to compress. Yet it still is about time meeting the obstruction and not the amount of pressure to meet Regs requirements.

Sorry that you have not seen an edge sensor, they are out there which is why there is a criteria for them separate from the motor operator used.

Most of the edge sensors are on commercial installations.

As a side note.
Newer doors do not have the old adjustments. They are now a programing system to teach the operator to recognize travel limits. Also the sensitivity to meeting an obstruction is being taken over by the operator and taken away from the owner to maintain/test adjust.

Mark Reinmiller
06-02-2015, 07:29 AM
The attached file is from a Liftmaster instruction manual with a 2007 copyright date. This page discusses how to adjust the FORCE activated reversing mechanism.

Also, Force and PSI are two different things. PSI has nothing to do with this topic. 31846

Garry Sorrells
06-02-2015, 02:56 PM
Mark,
The installation instructions refer to the adjustment using the term "force mechanism adjustment" and yes the operator does apply a force to the door to move it up or down. Depending on the door, spring size and their adjustment, track and wheel lubrication the operator will be required to apply different amounts of force to move the door. The instructions also include testing the door half way down and up for reversal and stoppage. Which is always a fun discussion for the HIs and their personal testing methods. No argument that force is required to move the door up and down. If there was no force involved it would move by magic.

The instructions are telling the consumer/installer to adjustment the force to as light a possible (more sensitive) or in other words to use as little force as required to move the door. No where is there anything that says the amount of force (lbs) that is being applied just that they direct to have as little as required to operated the door satisfactorily.

The regs delineate between doors equipped with edge sensors and those not so equipped. Lift master is not addressing the edge sensor requirement because the operator they are supplying has no edge sensor.

There is also in the instructions the Federal required statement that the door must reverse on contact with a 2x4 block, though there is no description of what amount of force is required to trigger that reversal. Just that it reverse.

Mark Reinmiller
06-02-2015, 03:26 PM
Mark,
The installation instructions refer to the adjustment using the term "force mechanism adjustment" and yes the operator does apply a force to the door to move it up or down. Depending on the door, spring size and their adjustment, track and wheel lubrication the operator will be required to apply different amounts of force to move the door. The instructions also include testing the door half way down and up for reversal and stoppage. Which is always a fun discussion for the HIs and their personal testing methods. No argument that force is required to move the door up and down. If there was no force involved it would move by magic.

The instructions are telling the consumer/installer to adjustment the force to as light a possible (more sensitive) or in other words to use as little force as required to move the door. No where is there anything that says the amount of force (lbs) that is being applied just that they direct to have as little as required to operated the door satisfactorily.

The regs delineate between doors equipped with edge sensors and those not so equipped. Lift master is not addressing the edge sensor requirement because the operator they are supplying has no edge sensor.

There is also in the instructions the Federal required statement that the door must reverse on contact with a 2x4 block, though there is no description of what amount of force is required to trigger that reversal. Just that it reverse.

Ok, after this I give up. A motor produces a constant about of torque, which is converted to a force. Adjusting the closing force does not change the torque, it changes the amount of force needed to reverse the door.

Perhaps the 2x4 test is not intended to test reversing force, but to see if the door reverses within 2 seconds?

Garry Sorrells
06-03-2015, 12:45 PM
Ok, after this I give up. A motor produces a constant about of torque, which is converted to a force. Adjusting the closing force does not change the torque, it changes the amount of force needed to reverse the door.

Perhaps the 2x4 test is not intended to test reversing force, but to see if the door reverses within 2 seconds?

Sorry that you seem frustrated. But you are exactly right in your last statement on the 2x4 test.

The first part is correct also. There is force involved but the amount is subjective not quantitative. The manufacture refer to force in their installation instructions and how to increase and decrease the force required to open and close the door. The discussion of force stops when it comes to testing operation to meet Fed Requirements.

Some links that may be of interest:
DASMA
DASMA Door and Access Systems Manufacturers Association (http://www.dasma.com/SafetyGDMaint.asp)
Garage door openers manufactured after January 1, 1993, are required by federal law to have advanced safety features that comply with the latest UL (Underwriters Laboratories) 325 standards. Contact your manufacturer or installer for additional information.



Test the reversing feature every month.

2. With the door fully open, place a 1-1/2" thick piece of wood (a 2" X 4" laid flat) on the floor in the center of the door


Force Setting Test
Test the force setting of your garage door opener by holding the bottom of the door as it closes. If the door does not reverse readily, the force setting may be excessive and need adjusting.

GENIE
Model : Powermax manual
http://www.geniecompany.com/data/products/genie_owners-manual_eng.pdf


Contact Reverse Test (page 9)

NOTE: The Limit and Force settings MUST BE COMPLETED before performing the Contact Reverse Test.


Lay a 2” x 4” board _at under the center of the door opening.
When the door contacts the board, it should stop and reverse direction within 2 seconds to the fully OPEN position

Model : Directlift manual
http://www.geniecompany.com/data/products/retail/lowes_directlift-2060-3060-install.pdf
Page 7


The Open Force and Close Force Controls are to be set to the minimum force necessary to ensure the door smoothly opens and closes completely.

Page 8


Limit Switch and Force Adjustments must be completed before checking the contact reverse function (Figure MA-3).



B) Lay a 2” x 4” board flat in center of doorway.
C) Close door using Wall Console.


Overhead Door MODELS Destiny1200, Destiny1500, Odyssey1000, & Odyssey1200
http://www.overheaddoor.com/garage-door-openers/Documents/installation/odyssey-destiny-openers-installation-english.pdf
Page 4


Safe-T-Reverse® Contact Reversing System

Automatically stops and reverses a closing door within two seconds of contact with an object.


Automatic ForceGuard™ Control

Automatically sets the force required to fully open and close the door for maximum safety.
Page 9


Lay a 2x4” board flat under the center of the door opening
When the door contacts the board, it should stop and reverse direction within 2 seconds to the fully OPEN position.

Page 17


Adjustment Guide - Force settings


Belt/Chain Drive – standard Drive 650 & Legacy 850

http://www.overheaddoor.com/garage-door-openers/Documents/installation/standarddrive650-legacy850-manual.pdf
When the door contacts the board, it should stop and reverse direction within 2 seconds to the fully open position. Red LED lights on the powerhead will begin to flash with the reversal of the do or. Remove the 2" x 4" board after a successful contact reversal test. The next cycle will clear the flashing red LEDs

Vern Heiler
06-05-2015, 07:18 AM
I appreciate all the good technical remarks by my many learned colleagues but Mark hits the "mark" in my opinion. I have tested many, many doors, long before the "eyes" came out and I would never stick a solid object in the path of a moving door. That could cause a lot of expensive unnecessary damage. I always do just as Mark does, I wait until the door is about thigh high and grasp the bottom with one hand. If I can't stop it, its a write up with strong warning not to ignore the condition, but to get a competent technician to fix it. I have never broken a door and I am pretty sure I have not caused any unnecessary alarm. If I can't stop the door then the force of the door would be enough to kill someone's cat or dog or severely
Allen, a word of advice from school of hard knocks. Wait until the top panel is nearly vertical before testing resistance. The operator arm horizontal pressure turns vertical in a heart beat. If the top panel bends under the vertical pressure the rollers pop out of there tracks and nothing can stop the chaos. Letting go of the bottom of the door no longer removes the "resistance" and if the downward pressure adjustment is set too high (9 out of 10 times) the jammed door crumples up like and old beer can. This is also another reason to test the resistance rather than relying on the 2X4 test only, as not all obstructions occur 3.5" from the floor.

Garry Sorrells
06-05-2015, 08:32 AM
..... while standing inside and extending my forearms with bent elbows at waist height to allow the door to come down on my forearms to meet resistance and hopefully return up again. EPIC FAILURE! ......
Am I at fault? .......


Your testing methods aren't correct. That outstretched arm test has bested many inspectors and busted many doors.
..........


......The method you used is not approved by any manufacturer or their garage door association for testing any door or opener........


...... Some manufacturers use the "hand" test to set the obstruction sensor. But none of the manufacturers recommend grabbing the door around waist level...........For the future, revise your testing methods.


Returning to the OP and methods of testing a door operations.
Checking the force adjustment of the door is a valid test. It is not the first thing to do, though it is a valid test to perform prior to testing reversal at the floor using a 2x4 board.

For many years installers have been testing the force of the door as it closed. Testing the door force is a part of the normal operator installation and should be done prior to the floor obstruction reversal test, AKA the 2x4 test. The exception comes with the newest operators that the adjustment is more internalized in its actual adjustment. Though the should always reverse if it meets an obstruction above 1" from floor such as a car or a person standing the opening..

Here are sources for testing force reversal adjustment of the door operator by an Association and Manufactures.
DASMA http://www.dasma.com/safetygdmaint.asp
"Force Setting Test:
Test the force setting of your garage door opener by holding the bottom of the door as it closes. If the door does not reverse readily, the force setting may be excessive and need adjusting. See your owner’s manual for details on how to make the adjustment."

This test will demonstrate what may happen when the door meets an obstruction at the floor. It has been a typical installer's test as part of installing and adjusting the garage door operator for many years. Going back to the introduction of the reversal function on meeting resistance on operation of the door. It has a real purpose and like anything that you do common sense must be used.


Chamberlain
http://www.chamberlain.com/CatalogResourcesV3/en-us/shared/files/tucmanuals/114A3165.pdf
Page 21--- "1. Test the DOWN (close) force
• Grasp the door bottom when the door is about halfway through DOWN (close) travel. The door should reverse......"

Quatum : Wayne Dalton
http://www.gdosupport.com/interface/main/downloads/quantum_manual.pdf
Page 21 "CLOSING FORCE ADJUSTMENT to help determine that the closing door force is not excessive, grasp the door handle or bottom edge during downward travel. The opener should REVERSE to this force. NOTE: Do not stand under door during this test...."

Raynor
http://www.raynor.com/pdf/corporal_inst.pdf
1. Page 24 -- "Test the DOWN (close) force

Grasp the door bottom when the door is about halfway through DOWN (close) travel. The door should reverse. ..."
--------------------------------------------------------------------------------------------------
Picture from :: DASMA http://www.dasma.com/safetygdmaint.asp

Garry Sorrells
06-08-2015, 04:53 AM
Found some info for doors outside the USA dealing with FORCE exerted by door on closing for reversal and time to reverse, take a look at thread:

Garage Door Anti-Entrapment Force outside USA


http://www.inspectionnews.net/home_inspection/showthread.php?t=43345

Keith Rogers
06-08-2015, 06:52 PM
Great thread, thanks for the learned discussion. As most threads do, it made me go out looking for more information. I came across a safety campaign Liftmaster is promoting on their website, "Don't Chance it, Check it."

Observing that 1 in 15 garage doors may not be safe (I think that is a low number!) the safety campaign encourages homeowners to perform three tests;
1. Check the sides of the garage door for properly installed photo eyes (black sensors), mounted no higher than 6 inches off the floor. 2. Block the photo eye with an object over 6 inches tall, and press the Garage Door Opener's close button. The door should not close. 3. Lay an object that is at least 1.5 inches higher on the ground in the door's path, and press the close button. The door should reverse off this object.

The website includes a youTube video demonstrating the tests. Here's the link:

https://www.liftmaster.com/For-Homes/Garage-Safety

Thanks for sharing your experience and knowledge with the rest of us!

- - - Updated - - -

Great thread, thanks for the learned discussion. As most threads do, it made me go out looking for more information. I came across a safety campaign Liftmaster is promoting on their website, "Don't Chance it, Check it." <br>
<br>
Observing that 1 in 15 garage doors may not be safe (I think that is a low number!) the safety campaign encourages homeowners to perform three tests; <br>
<font color="#313131"><span style="font-family: Helvetica Neue 55">1. Check the sides of the garage door for properly installed photo eyes (black sensors), mounted no higher than 6 inches off the floor. 2. </span></font><font color="#313131"><span style="font-family: Helvetica Neue 55">Block the photo eye with an object over 6 inches tall, and press the Garage Door Opener's close button. The door should not close. 3. </span></font><font color="#313131"><span style="font-family: Helvetica Neue 55">Lay an object that is at least 1.5 inches higher on the ground in the door's path, and press the close button. The door should reverse off this object.</span></font><font color="#313131"><span style="font-family: Helvetica Neue 55"><br>
</span></font><br>
The website includes a youTube video demonstrating the tests. Here's the link:<br>
<br>
<a href="https://www.liftmaster.com/For-Homes/Garage-Safety" target="_blank" rel="nofollow">https://www.liftmaster.com/For-Homes/Garage-Safety</a><br>
<br>
Thanks for sharing your experience and knowledge with the rest of us!

- - - Updated - - -

Great thread, thanks for the learned discussion. As most threads do, it made me go out looking for more information. I came across a safety campaign Liftmaster is promoting on their website, "Don't Chance it, Check it." &lt;br&gt;<br>
&lt;br&gt;<br>
Observing that 1 in 15 garage doors may not be safe (I think that is a low number!) the safety campaign encourages homeowners to perform three tests; &lt;br&gt;<br>
&lt;font color="#313131"&gt;&lt;span style="font-family: Helvetica Neue 55"&gt;1. Check the sides of the garage door for properly installed photo eyes (black sensors), mounted no higher than 6 inches off the floor. 2. &lt;/span&gt;&lt;/font&gt;&lt;font color="#313131"&gt;&lt;span style="font-family: Helvetica Neue 55"&gt;Block the photo eye with an object over 6 inches tall, and press the Garage Door Opener's close button. The door should not close. 3. &lt;/span&gt;&lt;/font&gt;&lt;font color="#313131"&gt;&lt;span style="font-family: Helvetica Neue 55"&gt;Lay an object that is at least 1.5 inches higher on the ground in the door's path, and press the close button. The door should reverse off this object.&lt;/span&gt;&lt;/font&gt;&lt;font color="#313131"&gt;&lt;span style="font-family: Helvetica Neue 55"&gt;&lt;br&gt;<br>
&lt;/span&gt;&lt;/font&gt;&lt;br&gt;<br>
The website includes a youTube video demonstrating the tests. Here's the link:&lt;br&gt;<br>
&lt;br&gt;<br>
&lt;a href="https://www.liftmaster.com/For-Homes/Garage-Safety" target="_blank" rel="nofollow"&gt;https://www.liftmaster.com/For-Homes/Garage-Safety&lt;/a&gt;&lt;br&gt;<br>
&lt;br&gt;<br>
Thanks for sharing your experience and knowledge with the rest of us!

- - - Updated - - -

Great thread, thanks for the learned discussion. As most threads do, it made me go out looking for more information. I came across a safety campaign Liftmaster is promoting on their website, "Don't Chance it, Check it." &lt;br&gt;<br>
&lt;br&gt;<br>
Observing that 1 in 15 garage doors may not be safe (I think that is a low number!) the safety campaign encourages homeowners to perform three tests; &lt;br&gt;<br>
&lt;font color="#313131"&gt;&lt;span style="font-family: Helvetica Neue 55"&gt;1. Check the sides of the garage door for properly installed photo eyes (black sensors), mounted no higher than 6 inches off the floor. 2. &lt;/span&gt;&lt;/font&gt;&lt;font color="#313131"&gt;&lt;span style="font-family: Helvetica Neue 55"&gt;Block the photo eye with an object over 6 inches tall, and press the Garage Door Opener's close button. The door should not close. 3. &lt;/span&gt;&lt;/font&gt;&lt;font color="#313131"&gt;&lt;span style="font-family: Helvetica Neue 55"&gt;Lay an object that is at least 1.5 inches higher on the ground in the door's path, and press the close button. The door should reverse off this object.&lt;/span&gt;&lt;/font&gt;&lt;font color="#313131"&gt;&lt;span style="font-family: Helvetica Neue 55"&gt;&lt;br&gt;<br>
&lt;/span&gt;&lt;/font&gt;&lt;br&gt;<br>
The website includes a youTube video demonstrating the tests. Here's the link:&lt;br&gt;<br>
&lt;br&gt;<br>
&lt;a href="https://www.liftmaster.com/For-Homes/Garage-Safety" target="_blank" rel="nofollow"&gt;https://www.liftmaster.com/For-Homes/Garage-Safety&lt;/a&gt;&lt;br&gt;<br>
&lt;br&gt;<br>
Thanks for sharing your experience and knowledge with the rest of us!

- - - Updated - - -

Great thread, thanks for the learned discussion. As most threads do, it made me go out looking for more information. I came across a safety campaign Liftmaster is promoting on their website, "Don't Chance it, Check it." &lt;br&gt;<br>
&lt;br&gt;<br>
Observing that 1 in 15 garage doors may not be safe (I think that is a low number!) the safety campaign encourages homeowners to perform three tests; &lt;br&gt;<br>
&lt;font color="#313131"&gt;&lt;span style="font-family: Helvetica Neue 55"&gt;1. Check the sides of the garage door for properly installed photo eyes (black sensors), mounted no higher than 6 inches off the floor. 2. &lt;/span&gt;&lt;/font&gt;&lt;font color="#313131"&gt;&lt;span style="font-family: Helvetica Neue 55"&gt;Block the photo eye with an object over 6 inches tall, and press the Garage Door Opener's close button. The door should not close. 3. &lt;/span&gt;&lt;/font&gt;&lt;font color="#313131"&gt;&lt;span style="font-family: Helvetica Neue 55"&gt;Lay an object that is at least 1.5 inches higher on the ground in the door's path, and press the close button. The door should reverse off this object.&lt;/span&gt;&lt;/font&gt;&lt;font color="#313131"&gt;&lt;span style="font-family: Helvetica Neue 55"&gt;&lt;br&gt;<br>
&lt;/span&gt;&lt;/font&gt;&lt;br&gt;<br>
The website includes a youTube video demonstrating the tests. Here's the link:&lt;br&gt;<br>
&lt;br&gt;<br>
&lt;a href="https://www.liftmaster.com/For-Homes/Garage-Safety" target="_blank" rel="nofollow"&gt;https://www.liftmaster.com/For-Homes/Garage-Safety&lt;/a&gt;&lt;br&gt;<br>
&lt;br&gt;<br>
Thanks for sharing your experience and knowledge with the rest of us!

Nick Ostrowski
06-09-2015, 03:49 AM
Looks like the correct way to test the doors is based on manufacturer info and that there is no set across-the-board testing method.

Allen Ingling
06-09-2015, 07:29 AM
Found some info for doors outside the USA dealing with FORCE exerted by door on closing for reversal and time to reverse, take a look at thread:

Garage Door Anti-Entrapment Force outside USA


http://www.inspectionnews.net/home_inspection/showthread.php?t=43345

Good job Garry. Fortunately you introduced my favorite topic, force vs. pressure vs. torque vs. whatever. We beat this to death on cable railings and here it is again. The simple way to measure door reversal force is with the same scale I use on the railings. I've included a photo of how to do it if you want to. As with the railings, I like to see over 50 lbs. force on a door reversal. I have not seen any go to the force Garry quotes, usually they are under 75 lbs which I can easily stop with one hand. The picture shows the height at which I always test, about thigh high (on me), at this point the top panel is still horizontal and having tested hundreds of these I have not broken one yet (I'm only 78, I may test a few more yet).

- - - Updated - - -


Found some info for doors outside the USA dealing with FORCE exerted by door on closing for reversal and time to reverse, take a look at thread:

Garage Door Anti-Entrapment Force outside USA


http://www.inspectionnews.net/home_inspection/showthread.php?t=43345

Good job Garry. Fortunately you introduced my favorite topic, force vs. pressure vs. torque vs. whatever. We beat this to death on cable railings and here it is again. The simple way to measure door reversal force is with the same scale I use on the railings. I've included a photo of how to do it if you want to. As with the railings, I like to see over 50 lbs. force on a door reversal. I have not seen any go to the force Garry quotes, usually they are under 75 lbs which I can easily stop with one hand. The picture shows the height at which I always test, about thigh high (on me), at this point the top panel is still horizontal and having tested hundreds of these I have not broken one yet (I'm only 78, I may test a few more yet).

Stuart Brooks
11-19-2015, 01:06 PM
I may be retired but this thread has been beat to death for ages and just have to repeat the fact that garage door operator standards are prescribed by Federal Regulations. Manufacturers usually reword the Federal requirements to provide pertinent details and omit the extra verbiage. Although a closing "pressure" requirement would seem to be more applicable to some, the regulations are for non-entrapment not total safety. There are no pressure standards so measuring the force means what? How would you determine how much pressure is too much?

I cut a piece of wood (cherry) 1-1/2" square, about 12" long, and carried it in my tool bag. I also put lines around the block to indicate the mounting height of the secondary IR beam. The 6" position was in red, and a black line at each inch above the red line. That way I could easily illustrate in a picture if the beam was too high and by how much by standing the block on end at the eye. I referred to the center of the beam lenses.

From the OP description, I would think this was a handyman or homeowner installation. It seemed odd to me that the manufacturers' instructions I found did not include the reversal test in the installation section but in the maintenance section.

The following is the Federal document. Look it up. You don't need to look up each individual manufacturer.

[Code of Federal Regulations]
[Title 16, Volume 2]
[Revised as of January 1, 2002]
From the U.S. Government Printing Office via GPO Access
[CITE: 16CFR1211.15]

[Page 337-338]
TITLE 16--COMMERCIAL PRACTICES
CHAPTER II--CONSUMER PRODUCT SAFETY COMMISSION
PART 1211--SAFETY STANDARD FOR AUTOMATIC RESIDENTIAL GARAGE DOOR OPERATORS-

Jerry Peck
11-19-2015, 02:23 PM
I cut a piece of wood (cherry) 1-1/2" square, about 12" long, and carried it in my tool bag. I also put lines around the block to indicate the mounting height of the secondary IR beam. The 6" position was in red, and a black line at each inch above the red line. That way I could easily illustrate in a picture if the beam was too high and by how much by standing the block on end at the eye. I referred to the center of the beam lenses.

Did you also have a line at the 4" position? :)

Stuart Brooks
11-19-2015, 06:57 PM
Did you also have a line at the 4" position? :)

No. I never had a too low installation to illustrate

Jerry Peck
11-19-2015, 07:36 PM
No. I never had a too low installation to illustrate

I've seen them setting on the floor, which makes them too low. :(

Garry Sorrells
11-19-2015, 07:38 PM
:deadhorse: --:)

.......There are no pressure standards so measuring the force means what? How would you determine how much pressure is too much?

.......... It seemed odd to me that the manufacturers' instructions I found did not include the reversal test in the installation section but in the maintenance section.

The following is the Federal document. Look it up. You don't need to look up each individual manufacturer.

.....

No pressure standards for overhead door operators means just that in the US. Pressure to trigger reversal is not something that Underwriters Labs focused on and thus was not an issue in the Fed Regs. It is time on contact. Thus it could be any amount of pressure exerted so long as it reversed within 2 sec. I have not tracked down anyone that actually participated in U.Ls. testing development and subsequent protocols on operation criteria. Pretty sure it all derived from the fact that they wanted a non instrumented way to demonstrate the door operating within a specification. So it is a 1" block that turned into accepting a 2x4 for practicality/convenience in home owner testing.

Manufacture instructions mirror the Fed Regs and yet the manufacture's instructions have changed over the years. Today you find that testing reversal above the floor in many instructions and also DASMA instructions on testing.

Most often our discussion turns to what the particular product manufacture states in their instructions as to determine installation and testing criteria. Looking at various manufacture instructions can demonstrate what the accepted norm may be. Decades back testing the pressure needed to cause the door to reverse was a norm for installers, even though not specified in the Fed Regs or manufacture instructions. It was just what the installer would do to protect the door from being damaged during installation adjustments of the operator.


The regs say that he door must reverse on meeting an obstruction at any point of its operating cycle which is a backhanded way to say that you should test the door at various positions of operation to assure that the Regs are being met for reversal.

This thread is just part of the never ending story for the topic. Yet you fired it back up after 6 months of dormancy.:peep:

Lon Henderson
11-20-2015, 06:35 AM
I've seen them setting on the floor, which makes them too low. :(

Is there a federal guideline saying that is too low?

Jerry Peck
11-20-2015, 06:49 AM
Is there a federal guideline saying that is too low?

Almost all of the installation instructions I've seen require them to be installed between 4" and 6" above the floor.

I'd have to check the federal standards to see if they have that requirement too ... but if the installation instructions have it - it is a requirement.

Garry Sorrells
11-20-2015, 07:46 AM
Manufacture instructions for placement derive from:

e-CFR data is current as of November 18, 2015
eCFR (http://www.ecfr.gov/cgi-bin/text-idx?rgn=div5&node=16:2.0.1.2.50)

§1211.11 Requirements for photoelectric sensors.
§1211.11 Requirements for photoelectric sensors. (http://www.ecfr.gov/cgi-bin/text-idx?rgn=div5&node=16:2.0.1.2.50#se16.2.1211_111)

(2) The obstruction noted in paragraph (a)(1) of this section shall consist of a white vertical surface 6 inches (152 mm) high by 12 inches (305 mm) long. The obstruction is to be centered under the door perpendicular to the plane of the door when in the closed position. See figure 3.

Jerry Peck
11-20-2015, 07:49 AM
Is there a federal guideline saying that is too low?


Almost all of the installation instructions I've seen require them to be installed between 4" and 6" above the floor.

I'd have to check the federal standards to see if they have that requirement too ... but if the installation instructions have it - it is a requirement.

I went through CFR 16-1211 and did not find a requirement for 4" high ... or 6" high.

And there is an additional test with a 4" high object, not just a '2x4'.

Read through the sections here: eCFR (http://www.ecfr.gov/cgi-bin/text-idx?tpl=/ecfrbrowse/Title16/16cfr1211_main_02.tpl)

I will add, before someone points it out, that I do know where that 6" 'requirement ' came from and why it is thought of as a 'requirement'. Most things in CFR 16-1211 are spelled out to a 'T' with the 'i's' dotted and the 't's' crossed.

Lon Henderson
11-20-2015, 04:14 PM
I went through CFR 16-1211 and did not find a requirement for 4" high ... or 6" high.

I didn't see it either when I read that a year or so ago. I'm not going to go hunting through installation instructions, but I'm pretty sure that I've read the 6" maximum in several of them, but I don't remember a minimum.

Jerry Peck
11-20-2015, 05:18 PM
I'm not going to go hunting through installation instructions, ..

I did when I was doing AHJ inspections - so I would know how it was supposed to be installed.


but I'm pretty sure that I've read the 6" maximum in several of them, but I don't remember a minimum.

The second one I looked at online: http://www.overheaddoor.com/garage-door-openers/Documents/installation/safe-t-beam-installation-english.pdf - Step 2 - the mounting bracket for the photo cell ... maximum 6" high, min 5" high ... which would be the top of the photo cell, that would put the photo cell at about 4" min to 5-1/2" high max based on the apparent size of the bracket.

ROBERT YOUNG
11-22-2015, 05:26 AM
"Don't Chance it, Check it."

Observing that 1 in 15 garage doors may not be safe (I think that is a low number!) the safety campaign encourages homeowners to perform three tests;
1. Check the sides of the garage door for properly installed photo eyes (black sensors), mounted no higher than 6 inches off the floor. 2. Block the photo eye with an object over 6 inches tall, and press the Garage Door Opener's close button. The door should not close. 3. Lay an object that is at least 1.5 inches higher on the ground in the door's path, and press the close button. The door should reverse off this object.

The website includes a youTube video demonstrating the tests. Here's the link:

https://www.liftmaster.com/For-Homes/Garage-Safety

Thanks for sharing your experience and knowledge with the rest of us!


Thanks for sharing your experience and knowledge with the rest of us!

I concur. Happy to be here.

Garry Sorrells
11-23-2015, 06:31 AM
Been waiting for someone to present the explanation/rational behind why some manufactures instruct position of sensor above 4 inches from floor and no higher than 6 inches. But I will give it a try. I have attempted to provide the most relevant sections as they relate to each other for reference and as they are mentioned. So you can follow the exact wording.


There is a requirement that the door reverse if it meets an obstruction or movement is impeded, a change in the constant pressure, and prior to 1 inch from the floor such as a car hood or a person standing in the opening. .See: “§1211.6 (http://www.ecfr.gov/cgi-bin/text-idx?SID=b38dfa9c0589b4b856bf5357b742ed36&mc=true&node=se16.2.1211_16&rgn=div8) (b)(1)(ii) Reverse direction and open the door to the upmost position when constant pressure on a control is removed prior to operator reaching its lower limit, and”

We have discussed the method of using you hand to test the §1211.6 (http://www.ecfr.gov/cgi-bin/text-idx?SID=b38dfa9c0589b4b856bf5357b742ed36&mc=true&node=se16.2.1211_16&rgn=div8) (b)(1)(ii) requirement which some manufactures like Chamberlain now list in their installation instructions as well as DASMA (The page cannot be found (http://www.dasma.com/safetygdmaint.asp)). This test yields the same effective result to fulfill the requirement as described in §1211.7 (http://www.ecfr.gov/cgi-bin/text-idx?SID=b38dfa9c0589b4b856bf5357b742ed36&mc=true&node=se16.2.1211_17&rgn=div8) (a)(1). By following the specifications of §1211.7 (http://www.ecfr.gov/cgi-bin/text-idx?SID=b38dfa9c0589b4b856bf5357b742ed36&mc=true&node=se16.2.1211_17&rgn=div8) (b)(3) the same result is obtained by the tester without having to personally touch the door. It is achieved using a solid block. Personally I still like to use my hands for many reasons.

Now this is where the 4 inch to 6 inch height gets introduced for the photo sensors. The sensors have to be less than 6 inches so that a child or adult arm /leg trigger the sensor. The height of 4 inches assures that the door obstruction is higher than the 1” requirement. They could have made it 2 inches, but they didn’t. So the sensors to be installed and working and at the same fulfill the requirement of §1211.6 (http://www.ecfr.gov/cgi-bin/text-idx?SID=b38dfa9c0589b4b856bf5357b742ed36&mc=true&node=se16.2.1211_16&rgn=div8) (b)(1)(ii) and §1211.7 (http://www.ecfr.gov/cgi-bin/text-idx?SID=b38dfa9c0589b4b856bf5357b742ed36&mc=true&node=se16.2.1211_17&rgn=div8)( a)(1) the sensors have to be greater than 4 inches from floor else the block would trigger the door not to move.




{{{ I have highlighted- BOLD }}} Reference as mentioned sequentially: eCFR (http://www.ecfr.gov/cgi-bin/text-idx?tpl=/ecfrbrowse/Title16/16cfr1211_main_02.tpl)

§1211.6 (http://www.ecfr.gov/cgi-bin/text-idx?SID=b38dfa9c0589b4b856bf5357b742ed36&mc=true&node=se16.2.1211_16&rgn=div8) (b)(1)(ii) Reverse direction and open the door to the upmost position when constant pressure on a control is removed prior to operator reaching its lower limit, and

§1211.7 (http://www.ecfr.gov/cgi-bin/text-idx?SID=b38dfa9c0589b4b856bf5357b742ed36&mc=true&node=se16.2.1211_17&rgn=div8) ( a)(1) Other than for the first 1 foot (305mm) of door travel from the full upmost position both with and without any external entrapment protection device functional, the operator of a downward moving residential garage door shall initiate reversal of the door within 2 seconds of contact with the obstruction as specified in paragraph (b) of this section. After reversing the door, the operator shall return the door to, and stop at, the full upmost position. Compliance shall be determined in accordance with paragraphs (b) through (i) of this section.

§1211.10 (http://www.ecfr.gov/cgi-bin/text-idx?SID=b38dfa9c0589b4b856bf5357b742ed36&mc=true&node=se16.2.1211_110&rgn=div8)(a) (3) The door operator is not required to return the door to, and stop the door at, the full upmost position when a control is actuated to stop the door during the upward travel—but the door can not be moved downward until the operator reverses the door a minimum of 2 inches (50.8 mm).

§1211.7 (http://www.ecfr.gov/cgi-bin/text-idx?SID=b38dfa9c0589b4b856bf5357b742ed36&mc=true&node=se16.2.1211_17&rgn=div8)(b) (3) To test operators for compliance with requirements in paragraphs (a)(3), (f)(3), and (g)(3) of this section, §1211.10(a)(6)(iii), and §1211.13(c), a solid rectangular object measuring 4 inches (102 mm) high by 6 inches (152 mm) wide by a minimum of 6 inches (152 mm)long is to be placed on the floor of the test installation to provide a 4-inch (102 mm) high obstruction when operated from a partially open position.

§1211.7 (http://www.ecfr.gov/cgi-bin/text-idx?SID=b38dfa9c0589b4b856bf5357b742ed36&mc=true&node=se16.2.1211_17&rgn=div8) (f)(3) The door operator is not required to return the door to, and stop the door at, the full upmost position when a control is actuated to stop the door during the upward travel—but the door can not be moved downward until the operator reverses the door a minimum of 2 inches (50.8 mm).


§1211.7 (http://www.ecfr.gov/cgi-bin/text-idx?SID=b38dfa9c0589b4b856bf5357b742ed36&mc=true&node=se16.2.1211_17&rgn=div8) (g)(3) The door operator is not required to return the door to, and stop the door at, the full upmost position when a control is actuated to stop the door during the upward travel—but the door can not be moved downward until the operator reverses the door a minimum of 2 inches (50.8 mm). When the door is stopped manually during its descent, the 30 seconds shall be measured from the resumption of the close cycle.


§1211.10 (http://www.ecfr.gov/cgi-bin/text-idx?SID=b38dfa9c0589b4b856bf5357b742ed36&mc=true&node=se16.2.1211_110&rgn=div8) (a)(6)(iii) The door operator is not required to return the door to, and stop the door at, the full upmost position when a control is actuated to stop the door during the upward travel—but the door can not be moved downward until the operator has reversed the door a minimum of 2 inches (50.8 mm).

§1211.13 (http://www.ecfr.gov/cgi-bin/text-idx?SID=b38dfa9c0589b4b856bf5357b742ed36&mc=true&node=se16.2.1211_113&rgn=div8) (c) Obstruction test. For a door traveling in the downward direction, when an inherent secondary entrapment protection device senses an obstruction and initiates a reversal, a control activation shall not move the door downward until the operator reverses the door a minimum of 2 inches (50.8 mm). The test is to be performed as described in §1211.7(b)(3).



§1211.7 (http://www.ecfr.gov/cgi-bin/text-idx?SID=b38dfa9c0589b4b856bf5357b742ed36&mc=true&node=se16.2.1211_17&rgn=div8) (b)(3). To test operators for compliance with requirements in paragraphs (a)(3), (f)(3), and (g)(3) of this section, §1211.10(a)(6)(iii), and §1211.13(c), a solid rectangular object measuring 4 inches (102 mm) high by 6 inches (152 mm) wide by a minimum of 6 inches (152 mm)long is to be placed on the floor of the test installation to provide a 4-inch (102 mm) high obstruction when operated from a partially open position.

Jerry Peck
11-23-2015, 09:39 AM
Garry,

I see you found the 4 inches I referred to - but I don't see that you've found the 6 inches height I referred to.

Jerry Peck
11-23-2015, 03:13 PM
Here is where the 6 inches height comes from:
- eCFR (http://www.ecfr.gov/cgi-bin/text-idx?SID=272b3e239a925092a9d97317d782876a&mc=true&node=se16.2.1211_111&rgn=div8)

§1211.11 Requirements for photoelectric sensors.
- (a) Normal operation test. (1) When installed as described in §1211.10(a) (1)-(4), a photoelectric sensor shall sense an obstruction as described in paragraph (a)(2) of this section that is to be placed on the floor at three points over the width of the door opening, at distances of 1 foot (305 mm) from each end and the midpoint.
- - (2) The obstruction noted in paragraph (a)(1) of this section shall consist of a white vertical surface 6 inches (152 mm) high by 12 inches (305 mm) long. The obstruction is to be centered under the door perpendicular to the plane of the door when in the closed position. See figure 3.

See figure 3 in the above link.

If the photo cell is above 6 inches high, the photo cell will not detect the 6 inch test obstruction. That means the maximum height permitted for the photo cell is 6 inches above the floor.

Many contractors (at least in Florida) build in a 3/4" recess for the garage door to close to so that the garage door closes below the garage floor level to help prevent wind blown rain and water penetration into the garage.

IF ... if that recess extends 6 inches in from the center of the door, one could measure the 6 inch height as being from above that recess (I am not recommending such, but IF the recess is that wide, it would meet the CFR 16-1211.11 requirements).

Most recesses I have seen are maybe a minimum of 5-1/2 inches wide (1x6 width to clear a 2x4 or 2x6 frame wall) to 9-1/4 inches wide (1x10 width to clear an 8 inch wide block wall) with the door being near the inside edge of the recess - which means measuring from the garage floor.

And, yes, I think some manufacturer's include 4 inches, or even 5 inches, to be above that 4" high obstruction, but ... that is not listed for the photo cell test, so some don't include any minimum height, not even for the 1" closing space at the bottom of the travel.

At least that is my thinking of how the 4 inch minimum and 6 inch maximum heights made their way into the manufacturer's installation instructions. Garry was on the right track, just hadn't pulled all the way into the station yet. :)

Garry Sorrells
11-23-2015, 05:31 PM
Garry,

I see you found the 4 inches I referred to - but I don't see that you've found the 6 inches height I referred to.


Manufacture instructions for placement derive from:

e-CFR data is current as of November 18, 2015
eCFR (http://www.ecfr.gov/cgi-bin/text-idx?rgn=div5&node=16:2.0.1.2.50)

§1211.11 Requirements for photoelectric sensors.
§1211.11 Requirements for photoelectric sensors. (http://www.ecfr.gov/cgi-bin/text-idx?rgn=div5&node=16:2.0.1.2.50#se16.2.1211_111)

(2) The obstruction noted in paragraph (a)(1) of this section shall consist of a white vertical surface 6 inches (152 mm) high by 12 inches (305 mm) long. The obstruction is to be centered under the door perpendicular to the plane of the door when in the closed position. See figure 3.

From Post #57. is the 6" see Pict I included. which is Fig 3. (top figure)

You are trying to lump the 4" and 6" together. The 4" is for an obstruction that the door actually hits and the 6" is if there is something laying on the floor for the photo eye to see.

Jerry Peck
11-23-2015, 06:04 PM
You are trying to lump the 4" and 6" together. The 4" is for an obstruction that the door actually hits and the 6" is if there is something laying on the floor for the photo eye to see.

Not lumping them together, go back and read my post - I said they were different: (I just added the bold and underlining for your)

And, yes, I think some manufacturer's include 4 inches, or even 5 inches, to be above that 4" high obstruction, but ... that is not listed for the photo cell test, so some don't include any minimum height, not even for the 1" closing space at the bottom of the travel.

Garry Sorrells
11-24-2015, 07:39 AM
..................Many contractors (at least in Florida) build in a 3/4" recess for the garage door to close to so that the garage door closes below the garage floor level to help prevent wind blown rain and water penetration into the garage.

IF ... if that recess extends 6 inches in from the center of the door, one could measure the 6 inch height as being from above that recess (I am not recommending such, but IF the recess is that wide, it would meet the CFR 16-1211.11 requirements).

...................:)

Not to uncommon to see the floor higher than drive in Maryland, typically to block rain water from entering. But your 2nd part of quote above had me thinking to find an example of installation. As it turned out not to difficult.

Take a look at Chamberlain help video. Notice the recess offset of the floor in relation to the door and sensors.

Showing a recess in the floor at the point of closure at floor and sensor location. About 30 sec into video. Ignore the question that the video is answering. Check the floor. Here is a link

(http://www.chamberlain.com/garage-door-openers/chain-drives/model-pd752kev)Why won't my door fully open? (http://www.youtube.com/embed/u1komdMy5pc?rel=0&autoplay=1&wmode=opaque)
(http://www.chamberlain.com/garage-door-openers/chain-drives/model-pd752kev)

Garry Sorrells
11-24-2015, 07:59 AM
Referring back to the OP.

Then as to____:boink:_to some.__ But not to restart an argument. Just to provide a little info/reference/support for anyone that may want a manufacture's wording/instructions to support their inspection methods. Rather than take word of mouth..__.:blah:

Test the DOWN (close) force

How do I adjust the travel and force limits? (http://chamberlain.custhelp.com/app/answers/detail/a_id/246/session/L3RpbWUvMTQ0ODM3MzkwNC9zaWQvNDk4QkxpQ20%3D#Step_2: _Adjust_the_Force)
Grasp the door bottom when the door is about halfway through DOWN (close) travel. The door should reverse. Reversal halfway through down travel does not guarantee reversal on a 1-1/2" (3.8 cm) obstruction. See Adjustment Step 3, page 30. If the door is hard to hold or doesn't reverse, DECREASE the DOWN (close) force by turning the control counterclockwise. Make small adjustments until the door reverses normally. After each adjustment, run the opener through a complete cycle.

Jerry Peck
11-24-2015, 08:51 AM
How do I adjust the travel and force limits? (http://chamberlain.custhelp.com/app/answers/detail/a_id/246/session/L3RpbWUvMTQ0ODM3MzkwNC9zaWQvNDk4QkxpQ20%3D#Step_2: _Adjust_the_Force)

The home inspector SHOULD NOT BE ADJUSTING the down force.

That is for homeowner maintenance.

Jerry Peck
11-24-2015, 09:47 AM
Not to uncommon to see the floor higher than drive in Maryland, typically to block rain water from entering. But your 2nd part of quote above had me thinking to find an example of installation. As it turned out not to difficult.

Take a look at Chamberlain help video. Notice the recess offset of the floor in relation to the door and sensors.

Showing a recess in the floor at the point of closure at floor and sensor location. About 30 sec into video. Ignore the question that the video is answering. Check the floor. Here is a link

(http://www.chamberlain.com/garage-door-openers/chain-drives/model-pd752kev)Why won't my door fully open? (http://www.youtube.com/embed/u1komdMy5pc?rel=0&autoplay=1&wmode=opaque)
(http://www.chamberlain.com/garage-door-openers/chain-drives/model-pd752kev)

That recess does not look to be at least 6 inches in from the center of the door, which would be required for that 12 inch wide by 6 inch high obstruction centered under the door - thus the 6 inch height of the obstruction would be on the floor, not on the recess.

Cut a piece of plastic sign which is 12 inches by 6 inches, mark the 6 inch center of the 12 inch length, center that under the center of the door - that should block the photo cell - if it does not, the photo cell is too high.

Yeah, like, right, all home inspectors are going to carry 12" x 6" piece of plastic sign with them ... :deadhorse: :dance:

Garry Sorrells
11-24-2015, 04:16 PM
Referring back to the OP.

Then as to____:boink:_to some.__ But not to restart an argument. Just to provide a little info/reference/support for anyone that may want a manufacture's wording/instructions to support their inspection methods. Rather than take word of mouth..__.:blah:

Test the DOWN (close) force

How do I adjust the travel and force limits? (http://chamberlain.custhelp.com/app/answers/detail/a_id/246/session/L3RpbWUvMTQ0ODM3MzkwNC9zaWQvNDk4QkxpQ20%3D#Step_2: _Adjust_the_Force)
Grasp the door bottom when the door is about halfway through DOWN (close) travel. The door should reverse. Reversal halfway through down travel does not guarantee reversal on a 1-1/2" (3.8 cm) obstruction. See Adjustment Step 3, page 30. If the door is hard to hold or doesn't reverse, DECREASE the DOWN (close) force by turning the control counterclockwise. Make small adjustments until the door reverses normally. After each adjustment, run the opener through a complete cycle.


The home inspector SHOULD NOT BE ADJUSTING the down force.

That is for homeowner maintenance.

It is not about the HI adjusting anything. It is about realizing that to much force can potentially cause damage when testing reversal at the floor using a solid block. It is also about providing an authoritative source, the manufacture, to support that position. As personal experience seems insufficient for some. Chambrerlain even say that in the link I posted. They state:
"

WARNING

Without a properly installed safety reversal system, persons (particularly small children) could be SERIOUSLY INJURED or KILLED by a closing garage door.


Too much force on garage door will interfere with proper operation of safety reversal system.
NEVER increase force beyond minimum amount required to close garage door.
NEVER use force adjustments to compensate for a binding or sticking garage door.
If one control (force or travel limits) is adjusted, the other control may also need adjustment.
After ANY adjustments are made, the safety reversal system MUST be tested. Door MUST reverse on contact with 1-1/2" high (3.8 cm) object (or 2 x 4 laid flat) on floor. "


Translation : " You could damage the door."

Jerry Peck
11-24-2015, 05:10 PM
It is not about the HI adjusting anything. It is about realizing that to much force can potentially cause damage when testing reversal at the floor using a solid block. It is also about providing an authoritative source, the manufacture, to support that position. As personal experience seems insufficient for some. Chambrerlain even say that in the link I posted.

Except that you keep harping on that as a TEST the home inspector should make.

It is a maintenance ADJUSTMENT test for the home owner, it is NOT a TEST that the home inspector should make.


They state:
"

WARNING

Without a properly installed safety reversal system, persons (particularly small children) could be SERIOUSLY INJURED or KILLED by a closing garage door.


Too much force on garage door will interfere with proper operation of safety reversal system.


Correct, and IF THE FORCE IS SET WRONG ... then the reversal system might not work, and there is a test for that, it is the 2x4 on the floor.

If you want to promote the Chamberlain site and information, did you notice that THEY HAD THE 2x4 THE WRONG WAY ... AND ... NOT CENTERED under the door opener in their test demonstration? Yep. And you are relying on them for good information?

Garry, this thread has :deadhorse: ... are you trying to beat the horse enough to make glue out of it? Or are you trying to continue side tracking it? :confused:

Roy Lewis
11-24-2015, 05:23 PM
it is NOT a TEST that the home inspector should make.

You really are delusional. Where do you come off making such an ambiguous statement?
A friggin knowledgeable inspector can make an assessment of the reversal.
Just because you don't have the knowledge doesn't mean crap to the rest of us.
Learn how then do it. It may save life and/or property..Huh?
WoW! Lay down Brother...
There is aways one in every group!

Jerry Peck
11-24-2015, 05:26 PM
There is aways one in every group!

And, from your posts, you are that one.

Roy Lewis
11-24-2015, 05:33 PM
And, from your posts, you are that one.
Now! You drawn first blood...
Be prepared. I for one am sure you don't have a clue . Baffling with BS..huh?
Are you friggin' telling me you don't test Garage door reversal?
If not! Then why in the hell would I want you as an inspector..?
What do you do with a garage door..Look at it go up and down..?

Jerry Peck
11-24-2015, 05:41 PM
There is aways one in every group!


And, from your posts, you are that one.


Now! You drawn first blood...
Be prepared. I for one am sure you don't have a clue . Baffling with BS..huh?
Are you friggin' telling me you don't test Garage door reversal?
If not! Then why in the hell would I want you as an inspector..?
What do you do with a garage door..Look at it go up and down..?

Yet another post verifying that you are one you referring to. :(

Roy Lewis
11-24-2015, 05:47 PM
Yet another post verifying that you are one you referring to. :(
Well! I guess the intellect isn't there to have a friendly conversation.
So! Since a lack of response on your part about a simple garage door inspection means you don't have a clue as to what you are doing when it comes to this subject.
Or would you rather babble on with you nothingness?
Yes or No?

Jerry Peck
11-24-2015, 05:53 PM
Well! I guess the intellect isn't there to have a friendly conversation.
So! Since a lack of response on your part about a simple garage door inspection means you don't have a clue as to what you are doing when it comes to this subject.
Or would you rather babble on with you nothingness?
Yes or No?

Geeze ... looks like we just got rid off one and then we get another one ... HG ... JA ... KW ... and now RL.

Put simply, your posts do not indicate that you can, or are even willing to, "have a friendly conversation".

No need for me to keep trying to communicate with one so clueless as you are.

Roy Lewis
11-24-2015, 06:04 PM
If you put me with KW you will be my enemy!
I have read multitudes of your post and I have came to the determination that you and Kevin Wood are brothers. You have pulled the wool over to many eyes and I for one will never believe your crap. You are truly a joke..admit it!
I'm sure you would never admit you didn't know everything..Huh?

Geeze ... looks like we just got rid off one and then we get another one ... HG ... JA ... KW ... and now RL.

Put simply, your posts do not indicate that you can, or are even willing to, "have a friendly conversation".

No need for me to keep trying to communicate with one so clueless as you are.

Garry Sorrells
11-24-2015, 06:13 PM
.....
Correct, and IF THE FORCE IS SET WRONG ... then the reversal system might not work, and there is a test for that, it is the 2x4 on the floor.
,,,,,,:confused:

I think I understand, rather than do something that might prevent damaging the door you would rather see the door get damaged and have a chuckle writing "failed under testing".

Jerry Peck
11-24-2015, 07:31 PM
I think I understand, rather than do something that might prevent damaging the door you would rather see the door get damaged and have a chuckle writing "failed under testing".

If one inspects the door FIRST - this discussion has been through MANY times before - inspect the door FIRST, and if anything looks amiss (there are many things which could lead to crumpling of the door), then the simple solution is to write those things up and state that the auto reverse function cannot, should not, be tested until those items are corrected, at which time the person making those corrections needs to verify that the auto reverse works after the other repairs have been completed.

If all the visual signs indicate that the door is suitable for auto reverse testing, and if the auto reverse testing is done PROPERLY, there is no reason for the door to fail.

Doing an unnecessary test for force will not assure you that the door will not crumple ... in fact ... doing that 'arm force test' is what crumpled the door and started this entire thread - so don't go beating your drums about doing that test to 'save the door'.

The most important part is a thorough visual inspection of the door - to make sure that all things are right (as best possible).

There have been reports here that the block of wood which was attached to the wall pulled off - even a thorough visual inspection might not pick that up, but it might.

There have been reports here of doors falling off the track when the tracks spread apart - a visual inspection might not pick that up either, but it might if the cause was missing track bracing.

There have been reports here of almost every type of failure - testing the force test would likely as not done nothing to stop those failures, a thorough visual inspection would have a better chance as some of those failures were from doors bending at the top due to not having a brace installed across the top of the door - a visual inspection would find that, a force test would only crumple the door.

If the home inspector feels a need to do the force test, then by all means do it, but they might as well also do every other test for the door too.

Or, do the standard, recommended, and required test - test the auto reverse.

Garry, when you test an oven for anti-tip, do you make sure that the range is fully in the hold-down brackets, that the hold-down brackets are properly and securely anchored to the floor? Both of those additional tests would require pulling the range out and doing additional testing of the brackets themselves. If the home inspector is so inclined, nothing prohibits it, but there is no practical reason to do those additional tests.

You keep promoting an additional, maintenance adjust test, as something which needs to be done by the inspector, with the proper and thorough visual test done first, that force test will not tell you anything that the standard, recommended and required auto reverse test will tell you, and, in fact, the force test will not tell you if the door auto reverses properly at the required height.

I don't mind dancing around the mulberry bush with you, but you really need to give it a break now and then.

Jerry Peck
11-24-2015, 07:53 PM
How do I adjust the travel and force limits? (http://chamberlain.custhelp.com/app/answers/detail/a_id/246/session/L3RpbWUvMTQ0ODM3MzkwNC9zaWQvNDk4QkxpQ20%3D#Step_2: _Adjust_the_Force)

Garry,

Here is an example of what I am referring to - taken from the link you provided:

You keep harping on, yes, "harping on" the force test, yet you skipped right over other maintenance adjustments and tests which should be considered (by your thinking) as just as important.

Why did you skip Step 1?


Step 1: Adjust the UP and DOWN Travel Limits


WARNING


Without a properly installed safety reversal system, persons (particularly small children) could be SERIOUSLY INJURED or KILLED by a closing garage door.


Incorrect adjustment of garage door travel limits will interfere with proper operation of safety reversal system.


After ANY adjustments are made, the safety reversal system MUST be tested. Door MUST reverse on contact with 1-1/2" (3.8 cm) high object (or 2 x 4 laid flat) on floor.

Isn't that just as important as your Step 2?

It says "SERIOUSLY INJURED or KILLED" (all caps are theirs, not mine).

It also says "Incorrect adjustment ... will interfere with proper operation of the safety reversal system."

It also says "After ANY" (all caps are theirs, not mine) "adjustments are made, ... Door MUST reverse on contact with" the 2x4.

Why did you pick out just Step 2 of the maintenance adjustments and tests?

I'm trying to follow your logic for picking just that one test and not all of the others, but your logic is illogical.

Garry Sorrells
11-26-2015, 04:12 AM
Jerry,
The short answer/reply.

The down force test is not the first first nor the last part of an inspection. Unless there is excessive down force and you might determine that further testing would be ill advised. The down force test is just part of the overall inspection with more than one purpose. Nothing illogical about it. It is part of a process.

The number of things that you look at and test is purely a mater of the degree of professionalism you want to attach to the inspection of the door.

:hand:......Stop here for the quick reply::::::::::::)

To clarify, I have not promoted or suggested the HI making any adjustments to any door. Rather I would strongly recommend that the HI not make any adjustment or alterations to the door's installation.

The OP of this thread may be an example of a poor determination of how the door and components were installed or had been modified. The door failure was due to a factor prior to the down force test, materials or installation. I am confident that I would be able to determine what caused the failure if I inspected the installation. The HIi may or may not have been able to see the defect. Recognizing that there is a defect is something else.


As for what you saw in the Chamberlain video using the block, unless I totally missed something, is placed in the center of the door. Manufactures can make errors in print and in videos. Don't think that is the case here, but possible. Possibly we are looking at different videos. Chamberlain is a major producer of operators world wide with a good product and a long track record. I don't like their how they have responded to technical questions I have posed to them in the past, but that is the way it is. I don't have to like the people to like the product.

Darn,,,,,:sorry:, ,,,,didn't want it to be this long a response... I know how many prefer the 10 word statements that are quick and easy to read.

Garry Sorrells
11-26-2015, 04:37 AM
Referencing the height of the sensors I sent a question to Chamberlain, made it simple and received a simple response. Here it is...

Question:
I understand that the height location for the sensor is not to exceed 6 inches.
Is there a minimum height from floor to mount the photo eye sensors?

Response:
We do not have a minimum height requirement. As long as the brackets do not exceed over 6 inches, you should be ok.

Jerry Peck
11-26-2015, 06:13 AM
To clarify, I have not promoted or suggested the HI making any adjustments to any door. Rather I would strongly recommend that the HI not make any adjustment or alterations to the door's installation.
.
.
Darn,,,,,:sorry:, ,,,,didn't want it to be this long a response... I know how many prefer the 10 word statements that are quick and easy to read.

Garry,

Short answer is: The down force test is part and parcel of the down force adjustment of the maintenance section for the home owner.

You are picking and choosing between home owner maintenance adjustment tests, trying to justify the one you picked.

IF the door does not reverse properly on the 2x4, the down force may be a cause ... as may be the travel limit ...

Long answer is: no need for long answer. :)

ROBERT YOUNG
11-26-2015, 07:48 AM
Roy, all things being equal in life, it's not the InterNACHI MB.
Full moon last night?

Garry Sorrells
11-26-2015, 08:11 AM
The down force test is a part of the total functionality of the door.

Jerry Peck
11-26-2015, 08:41 AM
The down force test is a part of the total functionality of the door.

Key words: ... "is a part of" ...

... as are ALL of the other tests ... yet you only single out that one test.

There are A LOT of other tests which are "part of the total functionality of the door". You have yet to explain why you are only pushing that one test over all the other tests which are required to be done.

The end result of all of the other tests is to properly automatically reverse the door, in addition to allowing the door to fully open and fully close. The auto-reversing on the 2x4 test, properly placed and properly done, is verification that all other tests are within their normal operational parameters with respect to the auto-reverse mechanism.

If the auto-reverse does not reverse, then one or more of the other adjustments are outside their normal operational parameters.

The most professional home inspector will do the professionally recognized and stated test: the auto-reverse on the 2x4.

Doing more testing does not make one 'more professional', it makes them look like they do not understand the requirements - the auto-reverse on the 2x4 test.

Doing more also increases their liability as they have now made more tests, and have not made the associated adjustments to verify that those test results are where the test results should be - i.e., testing the down force without making adjustments is not testing that the down force is at or near the lowest setting necessary to close the door.

From your link: (bold is mine)


WARNING


Without a properly installed safety reversal system, persons (particularly small children) could be SERIOUSLY INJURED or KILLED by a closing garage door.


- Too much force on garage door will interfere with proper operation of safety reversal system.
- NEVER increase force beyond minimum amount required to close garage door.
- NEVER use force adjustments to compensate for a binding or sticking garage door.
- If one control (force or travel limits) is adjusted, the other control may also need adjustment.
- After ANY adjustments are made, the safety reversal system MUST be tested. Door MUST reverse on contact with 1-1/2" high (3.8 cm) object (or 2 x 4 laid flat) on floor.


For clarification for all of us - you are saying:
- a) do the force test INSTEAD OF the 2x4 test
- b) do the force test IN ADDITION TO the 2x4 test

Garry Sorrells
11-26-2015, 10:06 AM
,,,,,....There are A LOT of other tests which are "part of the total functionality of the door". You have yet to explain why you are only pushing that one test over all the other tests which are required to be done.........................

For clarification for all of us - you are saying:
- a) do the force test INSTEAD OF the 2x4 test
- b) do the force test IN ADDITION TO the 2x4 test

What I keep saying is:

" b) do the force test IN ADDITION TO the 2x4 test "

Again, if the operator is out of adjustment in travel limits and downward force, especially with older operators, the door can be damaged when performing the reversal test using a 2x4 on the floor .

Again, I would promote the other tests that are part of the functionality of the operator and door.

Back to plucking the bird...:) ,,... hope you are having a good day, especially if you are able share it with family and friends..

Jerry Peck
11-26-2015, 10:20 AM
What I keep saying is:

" b) do the force test IN ADDITION TO the 2x4 test "

Thank you for that clarification, now, clarify why not the other tests which could ...


Again, if the operator is out of adjustment in travel limits and downward force, especially with older operators, the door can be damaged when performing the reversal test using a 2x4 on the floor .

There are many things which can contribute to crumpling of the door even when the force is properly set, and, again, that crumpling of the door can take place without even doing the 2x4 test - going back to the original post in this thread and the door crumpling while doing the force test. Your reasoning for doing the force test to prevent crumpling of the door just does not withstand the force being applied behind promoting it.


Again, I would promote the other tests that are part of the functionality of the operator and door.

You would, but you are not, you are singling out one test of the many tests which are "part of the functionality of the operator and door"

Hope everyone is having a good Thanksgiving day, and I also hope that Garry's and my bantering back and forth has not been, and is not, too much for the other members of the board. The purpose of which is to establish the proper test and the why behind it.

Ian Page
11-26-2015, 12:39 PM
There are many components within a home which are dangerous during operation, the garage door is just one of them for which there are recognized standard testing procedures. You certainly can't test for homeowner stupidity, which is often the cause for accidents and injury.

Aside from and including examination of the door, two basic tests are recognized both of which involved door reversal. One, if there is an obstruction across the threshold (beam sensor) and the other for downward pressure if the beam fails. The 2x4 method ensures that minimal or no damage to the door itself if the downward pressure is not adjusted properly. Holding the door at knee, waist or even higher can both injure the tester and cause damage to the runners or track, if too much resistance to applied. That's a huge variable, whereas the 2x4 is not.

I have never, never in 30 years experienced any damage to a garage door using a 2x4 or similar across the threshold. Though I used to use a tennis or rubber ball instead.

For those who discount the 2x4 method and rely solely on beams, consider this. A step ladder placed across the threshold during maintenance, light hanging, painting etc will not obstruct the beam. Should the door be activated in error, any person on the ladder stands a real good chance of crush injury or even death if the downward pressure fails. Food for thought.

Happy Thanksgiving to all.

Garry Sorrells
11-26-2015, 01:34 PM
What I keep saying is:

" b) do the force test IN ADDITION TO the 2x4 test "

..........

Again, I would promote the other tests that are part of the functionality of the operator and door.......


Thank you for that clarification, now, clarify why not the other tests which could ...
.......There are many things which can contribute to crumpling of the door even when the force is properly set, and, again, that crumpling of the door can take place without even doing the 2x4 test - going back to the original post in this thread and the door crumpling while doing the force test. Your reasoning for doing the force test to prevent crumpling of the door just does not withstand the force being applied behind promoting it.

......You would, but you are not, you are singling out one test of the many tests which are "part of the functionality of the operator and door"

.


My position is and has been that many things need to be inspected and tested regarding a garage door, both visual and physical not just the downward force. Downward force testing is at the end of the list of all of the visual inspections and physical testing that are performed. Not something that you skip over other things to get to or only do.

Your position is that the testing the downward force is not needed nor appropriate. Relying solely on the finial test of the downward force reversal with a 2x4 on the floor. Which I disagree with.

My position is that the downward force test is the test that should immediately precede the final reversal test at the floor. Since the reversal protocol is predicated on reversal after contact and with in 2 seconds the amount of force exerted can be great enough to possibly damage the door.
Evaluating the downward force is something many HI do not attempt. Many HI seem not to be comfortable testing the reversal at the floor with a solid object for fear of damaging the door. We have heard about some using a roll of paper towels. Others only test the photo sensors with their foot. Just to mention a few examples.

I am not arguing for less testing, but for more. I have repeatedly explained why this particular test should be done. You have argued that it is only done if you are going to also adjust the settings. Which is wrong.

You are correct when you stated "There are many things which can contribute to crumpling of the door...". Which is why the entire door installation and operator installation must be inspected, requiring that the person performing the inspection must be able to identify every aspect of the installations as being correct or incorrect and the potential consequences if incorrect.

Again, what happened with the OP and the failure of the door was related to some factor that either was not recognized by the HI that should have stopped any further testing; or there was an inherent problem with the door or its installation that could not be seen resulting in the failure.

Jerry Peck
11-26-2015, 03:30 PM
My position is that the downward force test is the test that should immediately precede the final reversal test at the floor. Since the reversal protocol is predicated on reversal after contact and with in 2 seconds the amount of force exerted can be great enough to possibly damage the door.

And I repeat again - that down force test could cause that very same damage, so testing the down force does not accomplish anything.

From the original post which started this thread:

I then proceeded to open and then close the door, while standing inside and extending my forearms with bent elbows at waist height to allow the door to come down on my forearms to meet resistance and hopefully return up again. EPIC FAILURE!

He was effectively doing the 'down force test' ... the door suffered - in his terms - "EPIC FAILURE!"

Garry Sorrells
11-26-2015, 04:35 PM
And I repeat again - that down force test could cause that very same damage, so testing the down force does not accomplish anything.

From the original post which started this thread:


He was effectively doing the 'down force test' ... the door suffered - in his terms - "EPIC FAILURE!"[/FONT][/COLOR]

But we have no way of telling to what degree the installation was inspected nor the level of knowledge/experience the HI had prior to the test and subsequent failure.

As I said"Again, what happened with the OP and the failure of the door was related to some factor that either was not recognized by the HI that should have stopped any further testing; or there was an inherent problem with the door or its installation that could not be seen resulting in the failure."


The down force test was not the root of the problem.

Jerry Peck
11-26-2015, 05:23 PM
But we have no way of telling to what degree the installation was inspected nor the level of knowledge/experience the HI had prior to the test and subsequent failure.
.
.
The down force test was not the root of the problem.

You are stuck in a groove, like an old worn out 78 rpm record, you cannot have it both ways "we have no way of telling" and "The down force test was not" ... either admit that you don't know, or admit that you are simply making it up as you go along trying to justify your position.

You keep repeating yourself like that old worn out record, the off switch appears to be broken too, so I guess the best thing I can do is to unplug it and put that old record player away in the closet.

Hopefully that old record player does not have a battery to keep it going - I don't recall seeing 'Everready' or a bunny on it.

Garry Sorrells
11-26-2015, 05:37 PM
The failure in the OP was not the result of the down force test. There was something wrong with the door or how it was installed.

If all is right with the door installation, meeting resistance (blockage) of movement that should trigger reversal should not cause the door to fail. Just reverse direction. It does not matter where the door is in the cycle of closing, first foot or last foot. Else no door could survive the test. Something was wrong with the installation or the door and operator..

Doors and operators are designed to operate through many different functions. Should you not expect that the door and operator be able to perform those functions on day one as yell as after ten years; provided that the installation is correct and the material has not deteriorated, been damaged/abused or not maintained?