View Full Version : Secondary A/C drain line



Jeff Eastman
11-27-2007, 07:27 PM
..........

Billy Stephens
11-27-2007, 07:46 PM
Jeff,

Electric or Gas Heat?

Billy Stephens
11-27-2007, 08:16 PM
[quote=Jeff Eastman;25611 all installed in a living space closet, [/quote]


Jeff, It's within the living space no need to insulate. Not in an open supply closet pulling unconditioned combustion air.

Jerry Peck
11-29-2007, 08:43 AM
You don't want to install an evaporator coil "above" electric heat strips.

Which is why all manufactured units have the heat strips above the coil - or to one side if a horizontal furnace.

Scott Patterson
11-29-2007, 10:12 AM
You don't want to install an evaporator coil "above" electric heat strips.

Which is why all manufactured units have the heat strips above the coil - or to one side if a horizontal furnace.

Jerry brings up a very good point and a problem that I see inspectors overlooking all of the time. When you find the heat strips below the coil this is a Red Flag that whoever put it in did not have a clue as to what they were doing.