PDA

View Full Version : 1. Powdery Substance on CB Terminals 2. Solid aluminum conductor



Tom Cissell
08-01-2016, 12:05 PM
Inspected a house built in 1986 with a GE electrical panel. There was a white powdery substance on every circuit breaker terminal. Could it be some sort of electrical lubricant? I have never see this before. Also, there were solid aluminum conductors use for the AC and Range circuits. I think this is alright as long as the circuit breakers are rated for AL/CU but I have only seen solid AL conductors on homes built in the 70's that were all aluminum. All 15 and 20 amp circuits have copper conductors. Any input on the white stuff? Comments on the AL appreciated as well. Thanks!
32816 32817 32818

Alton Darty
08-02-2016, 02:36 AM
What size wires were the range and AC wired with? With a range I normally see around a 40-50 amp breaker and the wires in your photo look small for that application. Usually a #8 or #6 CU is needed for 40 or 50 amps. AL wiring would need to be a size larger to carry that load so I would expect to see a #6 or a #4 AL wire.The majority of the wiring I see at that size is stranded and not solid conductor. Longer runs from the breaker to the appliance need to be upsized to allow for voltage drop.
I seem to remember that there have been posts in the past concerning a white powder at breakers. I beleive that the concensus was that the manufacturer used some type of filler over screw heads and the material degraded over time & fell away. A search for "white powder" should turn up something in the older messages.
32823

ROBERT YOUNG
08-02-2016, 03:04 AM
Inachi MB.
Scroll down to Robert Meir's post #10.
Not always white.
https://www.nachi.org/forum/f19/white-powder-circuit-breakers-65964/

I was wondering, this powder desiccant? Anti moisture/humidity.
Like you find for double/triple pane glazing's.
Any thoughts?