Are expansion tanks required at water heaters?

Garry Sorrells
02-28-2017, 06:07 AM
Think the answer you are looking for is between the last shutoff valve and water heater.

Jerry Peck
02-28-2017, 06:48 AM
Yes, no, and maybe

If there is no backflow device (check valve) or pressure regulator - no ... unless water utility requires it.

If there is a backflow device or pressure regulator - yes ... except that the code only requires a means to control thermal expansion, so most AHJ permit expansion tanks or pressure relief valves (not the T&P relief valve).