07-28-2017, 08:00 AM
What is the distance a dryer vent that goes through the foundation need to be from a foundation vent from the crawlspace?

Brian Hannigan
07-28-2017, 08:27 AM
Hi David Noonkester and welcome to InspectionNews!

I'm Brian Hannigan and I created InspectionNews.

I hope you find everything you are looking for on this site.

If I can help you in any way just let me know.

As a "Thank You" for making your first post I have a gift for you. You can pick it up at:
http://www.SendYourFreeCard.com

Roy Lewis
07-28-2017, 08:44 AM
What is the distance a dryer vent that goes through the foundation need to be from a foundation vent from the crawlspace?

Its doesn't matter as long as it's exhausted to the exterior.

"M1502.6 Duct length.
The maximum length of a clothes dryer exhaust duct shall not exceed 25 feet (7,620 mm) from the dryer location to the wall or roof termination. The maximum length of the duct shall be reduced 2.5 feet (762 mm) for each 45-degree (0.8 rad) bend, and 5 feet (1,524 mm) for each 90-degree (1.6 rad) bend. The maximum length of the exhaust duct does not include the transition duct.

This means that vents should also be as straight as possible and cannot be longer than 25 feet. Any 90-degree turns in the vent reduce this 25-foot number by 5 feet, since these turns restrict airflow. "
https://www.nachi.org/dryer-vent-safety.htm

Jerry Peck
07-28-2017, 01:16 PM
Roy provided the old standby code length, which evolved over time into allowing longer lengths and options - go here: https://codes.iccsafe.org/public/document/code/553/9853026

Scroll down to M1502.4 Dryer exhaust ducts.

Way to much to type, also note M1502.4.5.2 Manufacturer's instructions.