12-21-2007, 12:46 PM
...............

Michael Larson
12-21-2007, 12:53 PM
Is That the GEC from the panel?
It doesn't look big enought in th epic.

Michael Larson
12-21-2007, 01:01 PM
Hi Michael,

I am reasonably sure that is the GEC from the service equipment panel.If it's the GEC mechanical splices are not permitted.
Where are the water meters in Phoenix?

John Steinke
12-21-2007, 06:27 PM
IIRC, such connections are allowed if they are permanent crimps or welded connections.

As for the crimping method used, we are talking about a rather substantial metal fitting that requires a pretty hefty tool to make the crimp ... not one of those automotive-type 'butt splices' that are made with a glorified set of pliers.

Damage to the GEC is one of the headaches of the biz; this is one of the most common areas for local amendments to the NEC. Most often, town will want that wire enclosed in pipe.

John Arnold
12-21-2007, 06:37 PM
John - Since you mention the fact that local codes may vary ("town will want that wire enclosed in pipe."), it would be helpful if you would click on User Cp at the upper left and fill in your town and state.
Around these here parts, Philadelphia area, it would not be common for the local code to require the GEC in a pipe, in my experience.

Jerry Peck
12-21-2007, 06:42 PM
I am reasonably sure that is the GEC from the service equipment panel.

One would not run the GEC to the hose bibb, but rather (if the underground water pipe was to be used as a grounding electrode) to the underground water pipe itself.

Thus, and for other reasons, that looks like the "interior metal water piping bond", at least to me.

Billy Stephens
12-21-2007, 06:50 PM
Wendall,

It looks like the siding is closer than the IRCR404.1.6 Height above finished grade of 6 inches requirement. :)

Ken Meyer
12-22-2007, 04:11 PM
Splicing is permitted, but it must be a "non-removable" splice, crimped together with a special tool. Here's one that was done that way, the reason for it was that the old galvanized piping was removed, and the bonding wire had to be extended to reach the new copper pipe close to where it enters the basement. I think the rule is that the bonding clamp can be no more than 5' from where the pipe enters the basement.
The one in the photo looks too small, could it be for cable or phone? The installers often use hose bibs.

Jerry Peck
12-22-2007, 09:17 PM
Jerry, if you are correct and this is the "interior metal water piping bond", are you allowed to splice?

Yes.

You are allowed to splice those bonding conductors.

In fact, you are allowed to splice GEC - *just not from the service equipment to the first grounding electrode*. From that first grounding electrode, you can splice as needed to get to the other grounding electrodes.

As John S. indicated - use only irreversible compression connectors or exothermic welds for splicing the GEC (from the service equipment to the first grounding electrode).

John Steinke
12-24-2007, 04:20 PM
Looking at the better pic, that is a proper crimp splice. The one pictured has a pretty thick wall, and you need a special hydraulic crimper to make the connections.

This one looks OK.