Are windows supposed to be safety glass if the bottom edge of the window is lower than 18" to the walking surface?

Jerry Peck
04-13-2007, 08:36 PM
Sometimes. Read the underlined R308.4.7 requirements.

Depends on it it meets the following:


- R308.4 Hazardous locations. The following shall be considered specific hazardous locations for the purposes of glazing:
- - 1. Glazing in swinging doors except jalousies.
- - 2. Glazing in fixed and sliding panels of sliding door assemblies and panels in sliding and bifold closet door assemblies.
- - 3. Glazing in storm doors.
- - 4. Glazing in all unframed swinging doors.
- - 5. Glazing in doors and enclosures for hot tubs, whirlpools, saunas, steam rooms, bathtubs and showers. Glazing in any part of a building wall enclosing these compartments where the bottom exposed edge of the
glazing is less than 60 inches (1524 mm) measured vertically above any standing or walking surface.
- - 6. Glazing, in an individual fixed or operable panel adjacent to a door where the nearest vertical edge is within a 24-inch (610 mm) arc of the door in a closed position and whose bottom edge is less than 60 inches (1524 mm) above the floor or walking surface.
- - 7. Glazing in an individual fixed or operable panel, other than those locations described in Items 5 and 6 above, that meets all of the following conditions:
- - - 7.1. Exposed area of an individual pane larger than 9 square feet (0.836 m2).
- - - 7.2. Bottom edge less than 18 inches (457 mm) above the floor.
- - - 7.3. Top edge more than 36 inches (914 mm) above the floor.
- - - 7.4. One or more walking surfaces within 36 inches (914 mm) horizontally of the glazing.
- - 8. All glazing in railings regardless of an area or height above a walking surface. Included are structural baluster panels and nonstructural infill panels.
- - 9. Glazing in walls and fences enclosing indoor and outdoor swimming pools, hot tubs and spas where the bottom edge of the glazing is less than 60 inches (1524 mm) above a walking surface and within 60 inches
(1524 mm) horizontally of the water’s edge. This shall apply to single glazing and all panes in multiple glazing.
- - 10. Glazing adjacent to stairways, landings and ramps within 36 inches (914 mm) horizontally of a walking surface when the exposed surface of the glass is less than 60 inches (1524 mm) above the plane of the adjacent walking surface.
- - 11. Glazing adjacent to stairways within 60 inches (1524 mm) horizontally of the bottom tread of a stairway in any direction when the exposed surface of the glass is less than 60 inches (1524 mm) above the nose of the tread.