View Full Version : Wiring hanging from joists



Richard Roshak
04-08-2018, 04:39 PM
2006 build. I thought you needed a 1X6 to attach wiring to floor joists in this manner. Never seen this type wiring in 20 years of inspecting.

Bill Kriegh
04-08-2018, 06:11 PM
As is, the installation doesn't pass muster. If, however, a ceiling is installed, the cables fastened to the bottom of the joists might be OK. The exact code wording says that the joists have to be drilled or running boards used in an unfinished basement, and exactly what constitutes a finished basement is open to interpretation.

Jerry Peck
04-08-2018, 06:26 PM
The CSST bond connection is incorrect too.

Richard Roshak
04-09-2018, 04:29 AM
Jerry,
There is a grounding clamp and wire on the black gas piping where the piping exists the interior foundation wall. I don't know why an additional clamp was installed on the csst piping itself. The joint in the ground wire is soldered.

Jerry Peck
04-09-2018, 04:39 AM
I don't know why an additional clamp was installed on the csst piping itself.

Richard,

While it's good that it was "also" properly bonded, but still not good that there is a clamp on the CSST itself. That should be removed.