View Full Version : Refrigerant line protection at studs and top plates



Michael Thomas
01-12-2008, 05:22 PM
Does the IRC require refrigeration lines to be protected where they pass through studs and top plates (similar to the protection required for NM wiring)?

James Duffin
01-12-2008, 06:10 PM
IRC Section M1308.2 says yes.

Jerry Peck
01-12-2008, 06:50 PM
To add to James 'yes' ... the protection if closer to that required for plumbing pipes than for NM cable.

Michael Thomas
01-13-2008, 07:11 AM
Thanks as always to you both.