Victor DaGraca
01-14-2008, 02:50 PM
Ran into a service panel installed in a hall closet used as laundry room.
1. I'm going to call out the lack of clearance to the panel.
2. I found stating that panels are not allowed in Clothes closets or bathrooms
"E3305.4 Location of working spaces and equipment.
Required working space shall not be designated for storage.
Panelboards and overcurrent protection devices shall not be
located in clothes closets or bathrooms."
However... no mention is made of "laundry rooms" or proximity to water sources. As you can see in the picture, the clothes washer is directly under the panel.
Any references to sources of water or moisture you can give me?
3. Splices within the panel. As you can see, there is one breaker with 2 conductors which I will call out, however a single conductor comes off of a breaker and is then spliced into 2 conductors. is this allowed?
This is a Service entrance panel and the ground bar is bonded to the neutral bar. I have a problem with the double lugging and the lack of permanent color marking of white cable used as conductors.
Any other input will be greatly appreciated.
1. I'm going to call out the lack of clearance to the panel.
2. I found stating that panels are not allowed in Clothes closets or bathrooms
"E3305.4 Location of working spaces and equipment.
Required working space shall not be designated for storage.
Panelboards and overcurrent protection devices shall not be
located in clothes closets or bathrooms."
However... no mention is made of "laundry rooms" or proximity to water sources. As you can see in the picture, the clothes washer is directly under the panel.
Any references to sources of water or moisture you can give me?
3. Splices within the panel. As you can see, there is one breaker with 2 conductors which I will call out, however a single conductor comes off of a breaker and is then spliced into 2 conductors. is this allowed?
This is a Service entrance panel and the ground bar is bonded to the neutral bar. I have a problem with the double lugging and the lack of permanent color marking of white cable used as conductors.
Any other input will be greatly appreciated.