Gas dryer in Bathroom closet with louvered doors. Can not get combustion air from bathroom. Correct?
Tim Moreira
04-19-2007, 09:54 PM
David,
Yes you are correct.
03# IRC:
M1701.4 Prohibited sources.
Combustion air ducts and openings shall not connect appliance enclosures with space in which the operation of a fan may adversely affect the flow of combustion air. Combustion air shall not be obtained from an area in which flammable vapors present a hazard. Fuel-fired appliances shall not obtain combustion air from any of the following rooms or spaces:
1. Sleeping rooms.
2. Bathrooms.
3. Toilet rooms.
Powered by vBulletin® Version 4.2.0 Copyright © 2025 vBulletin Solutions, Inc. All rights reserved.