View Full Version : Turbine Clearance from Flue(s)?



Rick Hurst
04-01-2008, 08:46 AM
What is the recommended clearance for turbines and Flue(s)? (3) feet?

Got the wood decking clearance observation also.

rick

Jerry Peck
04-01-2008, 09:10 AM
Rick,

First, a question:

WTF ;) is that other termination?

I see the wind turbine, and the (what looks like) gas vent, but the other hooded four side top thingy (technical term) ...

Also having difficulty following your inside the attic photo.
- The exterior orientation of the wind turbine and the other 'thingy' is such that the 'thingy' is higher up the roof than the turbine, however, based on the photo ... is the photo showing the end of the OSB left hanging and unsupported, or is that a real nice and clean saw cut?
- Assuming that the further away 2x is the rafter, and the closer (lower) 2x is a purlin, then it makes sense and the 'thingy' is higher up the roof, but ...
- The 'thingy' is supplied with what looks like Type B Gas Vent - and the exterior photo does not show a Type B Gas Vent Cap on it.

Regarding your question, though, not sure if there is any minimum clearance between the two.

The 3 feet (above) only applies to "forced air inlets":

- G2427.6.7 (503.6.7) Forced air inlets. Gas vents shall terminate not less than 3 feet (914 mm) above any forced air inlet located within 10 feet (3048 mm).

Rick Hurst
04-01-2008, 09:27 AM
That 4 sided thingy :D is connected to the WH flue which was Transite pipe also. Hello asbestos.

Your correct in the observation of the roof decking. Someone went wild with the sawsall cutting out the opening for the turbine.

Rick Hurst
04-01-2008, 09:32 AM
I had heard that the venting from turbines could draw flue gases from combustion appliances such as water heaters.

Jerry Peck
04-01-2008, 09:32 AM
That 4 sided thingy :D is connected to the WH flue which was Transite pipe also. Hello asbestos.


Sooo ... you've got more to write up than 'just the unlisted gas cap'? :)