If I had more time, I could probably figure this out, but I have a long report to finish, and I hope that this puzzle will prove interesting for you guys. The house I looked at today had 2 GFCIs back to back through an interior wall, one in the kitchen, and the other in the bathroom.
When I test the bath GFCI with my tester, nothing happens. When I test it with the button on the GFCI, it trips, but it still lights up the tester.
When I test the kitchen GFCI with the tester, the one in the bathroom trips audibly, but still lights up the tester. When I test the kitchen GFCI with the button on the GFCI, it shuts off.
Is this miswiring, or a defective GFCI? I am writing it up to have them both replaced, and the problem can be discovered at that time, but I won't know what caused it. :confused:
Any ideas?

Richard Moore
04-24-2008, 11:06 PM
The GFCI in the bathroom is hooked up with the line/load connections reversed. 99.99% certain

"When I test it with the button on the GFCI, it trips, but it still lights up the tester." That is the tell-tale. Everything you describe would be the result of that.

You probably don't actually need new GFCI's, as it sounds like they are both still functional. Just re-wiring the bathroom GFCI should fix it. And, of course, the kitchen GFCI is actually redundant in this case, but no harm at all leaving it there. Just tell the client that a fault in the kitchen might trip the kitchen GFCI, the bathroom GFCI, or both.

FYI...The newer GFCIs won't reset with the line/load reversed. Also, on a new house or remodel, the kitchen shouldn't be on the same circuit as, or fed from, the bathroom, but I'd normally let it go on an older home (depending on circumstances).

Aaron Miller
04-25-2008, 03:30 AM
Ken:

"A GFCI can be wired to protect itself (single-location) or to protect itself and all devices "down-stream" to the end of the circuit (multiple-location). It can't protect devices between itself and the main service panel. Single-location wiring is preferable, since multiple devices may make a GFCI overly sensitive to false trippings. Consult an electrician for help with multiple-location wiring."

Can't Reset a GFCI Outlet? (http://www.thecircuitdetective.com/gfis.htm)

Aaron

Michael Larson
04-25-2008, 05:39 AM
Richard nailed it.

I found this same condition in my daughter's place a few years ago.
Being it was family, I reversed the line and load connections and everything was fine.

Randy Clayton
04-26-2008, 05:30 PM
Those guys said it the gfci outlets are probably ok just the incoming and out going lines are reversed.