View Full Version : Condensor Clearance



Jim Robinson
07-03-2008, 12:56 PM
I cannot find the installation instructions for this Armstrong Concept 1000 compressor. Is there a general rule of thumb for clearance to the wall? It was about 3 inches away , and seemed too close to me.

Jerry Peck
07-03-2008, 01:03 PM
Is there a general rule of thumb for clearance to the wall?

Generally, 12" is the least clearance allowed, plus, not under roof water runoff.

Also, if the service access faces the wall, then 36" is required between the unit and the wall (to meet the minimum working space requirements).

Jim Robinson
07-03-2008, 01:06 PM
Dang, that was quick. Thank you, as always.

Michael Thomas
07-03-2008, 02:36 PM
You can ask them here http://www.armstrongair.com/contact.php, (http://www.armstrongair.com/contact.php) or call Lennox, 1-800-953-6669. That's the "customer care" number, but I've been able to get tech support numbers there in the past by explaining why I'm asking.

Brandon Whitmore
07-03-2008, 02:38 PM
The one I had yesterday required 8"-- that's the least I have seen.