View Full Version : CPVC ?



Rick Hurst
07-03-2008, 04:57 PM
Do you call out CPVC on top of a gas water heater when it is close to the exhaust?

I always have called it out as being a risk for heat damage but all the plumbers around say its ok.

Any feedback.

rick

Nick Ostrowski
07-03-2008, 05:03 PM
I would still call it Rick. If the plumbers want to take ownership of that flood-to-be, I say let em' have at it. If I remember correctly, CPVC is only stable for temperatures up to 180 degrees and that's from water in the pipes. I could see the pipe melting if you get a water heater that has a backdrafting issue or even if it is firing for an extended period of time due to usage of a lot of hot water (bathing, washing machine running at same time).

Jerry Peck
07-03-2008, 07:32 PM
Do you call out CPVC on top of a gas water heater when it is close to the exhaust?

Rick,

It is required to be 6" from the drafthood, 6" from single wall vent, and 1" from Type B gas vent.

Let the plumbers say it is okay an do it, you just give them the code section/manufacturers' installation instructions which tells them *not* to do it.

Rick Hurst
07-03-2008, 07:39 PM
This is the one in question.

Jerry Peck
07-03-2008, 07:42 PM
Rick,

From the draft hood it requires 6" clearance to *all* combustible material: the CPVC, the foam insulation, etc.

That's not even addressing the effect of the heat on the CPVC, just that the CPVC is 'combustible'.