Results 1 to 19 of 19
Thread: Attic Access & Attic Ladder
03-21-2009, 07:57 AM #1
Does anyone know of a current requirement, either code or manufacturer requirement for:
1) Having "safety wires" on the attic access pull down ladder springs.
2) Attic access pull down ladder needing to have a handrail.
3) Attic access pull down ladder cover needing fire-guard protection when a gas furnace or water heater is located in the attic. The attic ladder system is located in the hall way of the home.
Regards,
Matt Brown
03-21-2009, 04:33 PM #2
Re: Attic Access & Attic Ladder
Nope. If that is required, I've never heard of it.
To my knowledge all manufactured pull down stairs have so-called 'handrails' built-in, and, yes, I would think it would be a requirement as, in some distance sense, it is a "stairway" (which is why most are referred to as pull-down stairs2) Attic access pull down ladder needing to have a handrail.
), and "stairways" require a handrail.
Nope, protecting the garage from a fire in the attic is not what the separation is about, however, most pull-down stairs are not wide enough to use for access, nor are they heavy duty enough (weight limit-wise) to be used as such.3) Attic access pull down ladder cover needing fire-guard protection when a gas furnace or water heater is located in the attic. The attic ladder system is located in the hall way of the home.
03-21-2009, 07:14 PM #3
I'm not familiar with such a safety strap. Plus, unless it's a new house, the building codes don't apply. Common sense does, though, and it would be worth a comment that the ladder is not the best access for maintenance for the water heater or any other items in that attic.
05-13-2009, 09:38 AM #4
I've installed pull-down attic stairs in the past, and I've never seen one with safety wires.
Interesting note: some of the standard attic stairs I've seen are not wide enough to allow access to replace the mechanical items in the attic i.e. HVAC units, water heaters, etc. Don't know how this was ever allowed, but I simply make note of it.
Linda - so if the ladder is the only means of access, would you recommend adding another access point?
Jerry - The fire separation question is interesting. If there is living space below the attic ladder, which seems to be the case with Matt, why would it not be required for the ladder panel (the part you see from below when the ladder is in the closed position) to be of the same fire-resistive material as the 5/8 sheetrock of the adjacent ceiling? I've installed these ladders which are manufactured with a simple 1/4" luan panel
hmmm...
05-13-2009, 02:44 PM #5
FINALLY! Some one picked up on that, I've been pointing that out for quite some time.
Now add this to your list for them: Check the weight rating and limitation of the pull down stairs, most are not rated enough for a worker AND the equipment either.
Yes, "fire separation" IS an interesting question, one that is not applicable to a single-family dwelling, but, go for it anyway, after all ... it is interesting.Jerry - The fire separation question is interesting.
There is no requirement for the ceiling to be anything. What makes you think there is 5/8 Type X in the ceiling?If there is living space below the attic ladder, which seems to be the case with Matt, why would it not be required for the ladder panel (the part you see from below when the ladder is in the closed position) to be of the same fire-resistive material as the 5/8 sheetrock of the adjacent ceiling? I've installed these ladders which are manufactured with a simple 1/4" luan panel
hmmm...
05-14-2009, 04:03 AM #6
Linda: That is not necessarily so, depending on the the adopted codes and AHJ's opinion in the area.Plus, unless it's a new house, the building codes don't apply.
05-14-2009, 07:11 AM #7
Aaron,
Some AHJ do not even use building codes (which is what you were saying anyway - or so I think).
Linda,
BOTH building codes and common sense apply.
That is not saying that all building codes make for good common sense or that common sense makes for good building codes.
05-14-2009, 08:12 PM #8
You keep calling it a stair, but they are ladders. At least the label on mine says it's a ladder.
They all look like ladders. They don't look like stairs.
Back to your normal broadcasting.
05-15-2009, 03:02 AM #9
807.1 Attic access.
In buildings with combustible ceiling or roof construction, an attic access opening shall be provided to attic areas that exceed 30 square feet (2.8 m2) and have a vertical height of 30 inches (762 mm) or greater. The rough-framed opening shall not be less than 22 inches by 30 inches (559 mm by 762 mm) and shall be located in a hallway or other readily accessible location. A 30-inch (762 mm) minimum unobstructed headroom in the attic space shall be provided at some point above the access opening. See Section M1305.1.3 for access requirements where mechanical equipment is located in attics.
M1305.1.3 Appliances in attics.
Attics containing appliances requiring access shall be provided with an opening and a clear and unobstructed passageway large enough to allow removal of the largest appliance, but not less than 30 inches (762 mm) high and 22 inches (559 mm) wide and not more than 20 feet (6096 mm) in length when measured along the centerline of the passageway from the opening to the appliance. The passageway shall have continuous solid flooring in accordance with Chapter 5 not less than 24 inches (610 mm) wide. A level service space at least 30 inches (762 mm) deep and 30 inches (762 mm) wide shall be present along all sides of the appliance where access is required. The clear access opening dimensions shall be a minimum of 20 inches by 30 inches (508 mm by 762 mm), where such dimensions are large enough to allow removal of the largest appliance.
Exception: The passageway and level service space are not required where the appliance is capable of being serviced and removed through the required opening.
05-15-2009, 06:30 AM #10
Jack,
You are correct, they are ladders ...
... that term started back when they were first called "disappearing stairs" and were NOT the folding type, but were actually "stairs", in one piece, which slid up into the attic. We had one in the house we lived in at Ft. Pierce, Fl when I as a teenager .. THOSE were STAIRS ... but the folding types are "ladders".
Note to self ... quite calling them sub-stairs
... they are "pull-down folding-ladders".
05-15-2009, 06:32 AM #11
05-15-2009, 06:39 AM #12
05-15-2009, 08:10 PM #13
A.D. - maybe in "your" part of Tennessee they do, but not in mine. They are called ladders here.
Memphis is like a different country compared to Knoxville.
05-22-2009, 09:59 PM #14
05-23-2009, 06:11 AM #15
05-24-2009, 04:45 AM #16
Ladders Or steps dose not matter you still have to take steps to get there . Its what ever you call it as long as its accessible .
05-24-2009, 09:24 AM #17
05-24-2009, 01:52 PM #18
05-24-2009, 02:11 PM #19
Aaron,
See that light off in the distance?
That's not a lighthouse, that's me waving my light back and forth showing you the way out of the grayness fog and into the light where white shines through the black darkness and makes the grayness go away.
Track straight toward that light and you will be safe, and if the currents cause drift and confusion, just keeping heading toward the light ... I'll leave the light on for ya, as Tom Bodet would say.
