12-19-2011, 06:23 AM #1
Cardboard as a foam backer in attic?
Recent inspection on new construction the builder used cardboard to seperate the attic space over the garage as a backer for foam insulation application. My concern is the exposed cardboard backer, as a part of the insulation assembly shouldn't it at least meet the flame spread charecteristic required for the foam? Fl code apps?
12-19-2011, 11:07 AM #2
Re: Cardboard as a foam backer in attic?
I've seen treated paper product insulation stop/venting channel at the soffit stapled to the trusses. It had a wax type of coating.
Was this used to separate the garage from habitable area? I/E gas fume barrier?
12-19-2011, 11:24 AM #3
The builder used the cardboard to seperate the area above the garage from the area above the conditioned area of the home. The foam insulation is applied to the underside of the roof deck and to the cardboard on one side only. I am concerned about the exposed face of the cardboard over the garage in the attic.
12-19-2011, 02:56 PM #4
2009 IRC
R316.4 Thermal barrier.
Unless otherwise allowed in Section R316.5 or Section R316.6, foam plastic shall be separated from the interior of a building by an approved thermal barrier of minimum 1/2 inch (12.7 mm) gypsum wallboard or a material that is tested in accordance with and meets the acceptance criteria of both the Temperature Transmission Fire Test and the Integrity Fire Test of NFPA 275.
12-20-2011, 05:11 AM #5
12-20-2011, 07:32 AM #6
12-20-2011, 03:52 PM #7
The foam insulation is required to be protected by a thermal barrier unless it is protected by an ignition barrier. This is an ongoing and evolving issue as to how to address what aspects in what why.
Currently, the most often accepted way is for an ignition barrier coating to be spray applied over the foam, although that may not be a technically correct code approved method.
The cardboard needs to be removed, install studs, drywall, then spray the foam on the drywall.
I should add ... BOTH the cardboard AND the exposed spray foam are hazards, but in different ways.