Results 1 to 3 of 3
    Apr 2008
    McKinney Texas
    Default Attic access photos
    Full size HVAC is located in this attic. Purlin blocks 50% of the door.
    Default Re: Attic access photos
    That certainly does not look code compliant based on the IRC: (underlining and bold are mine)
    - R807.1 Attic access.
    - - Buildings with combustible ceiling or roof construction shall have an attic access opening to attic areas that have a vertical height of 30 inches (762 mm) or greater over an area of not less than 30 square feet (2.8 m2).
    - - The rough-framed opening shall be not less than 22 inches by 30 inches (559 mm by 762 mm) and shall be located in a hallway or other location with ready access. Where located in a wall, the opening shall be not less than 22 inches wide by 30 inches high (559 mm wide by 762 mm high). Where the access is located in a ceiling, minimum unobstructed headroom in the attic space shall be 30 inches (762 mm) at some point above the access measured vertically from the bottom of ceiling framing members. See Section M1305.1.2 for access requirements where mechanical equipment is located in attics.
    - M1305.1.2 Appliances in attics.
    - - Attics containing appliances shall be provided with an opening and a clear and unobstructed passageway large enough to allow removal of the largest appliance, but not less than 30 inches (762 mm) high and 22 inches (559 mm) wide and not more than 20 feet (6096 mm) long measured along the centerline of the passageway from the opening to the appliance. The passageway shall have continuous solid flooring in accordance with Chapter 5 not less than 24 inches (610 mm) wide. A level service space not less than 30 inches (762 mm) deep and 30 inches (762 mm) wide shall be present along all sides of the appliance where access is required. The clear access opening dimensions shall be not less than of 20 inches by 30 inches (508 mm by 762 mm), and large enough to allow removal of the largest appliance.
    - - - Exceptions:
    - - - - 1. The passageway and level service space are not required where the appliance can be serviced and removed through the required opening.
    - - - - - 2. Where the passageway is unobstructed and not less than 6 feet (1829 mm) high and 22 inches (559 mm) wide for its entire length, the passageway shall be not more than 50 feet (15 250 mm) long.
    - M1305.1.3.1 Electrical requirements.
    - - A luminaire controlled by a switch located at the required passageway opening and a receptacle outlet shall be installed at or near the appliance location in accordance with Chapter 39. Exposed lamps shall be protected from damage by location or lamp guards.
    Apr 2008
    McKinney Texas
    Thanks Jerry, for all your input. Appreciate it. Good info.
    Thanks,
    Gene
    - - - Exceptions: