    Default 3rd drain from HVAC Unit ?

    I found this odd, as most units I have seen have 2 drain lines for a HVAC unit, and I understand that upright systems do not even require a secondary drain to be connect as most of the time they are plugged.

    I have not seen 3 drains coming from a unit !, Am I just lucky enough not to have seen this before or is it truly uncommon ?

    I am writing it up and I figure anything draining needs to drain some where and not on the platform.

    Why 3 ???DSCN8596 (450x338).jpg

    Similar Threads:
    Crawl Space Creeper

  2. #2
    Join Date
    Mar 2007
    Location
    Orlando, FL
    Posts
    1,593

    Default Re: 3rd drain from HVAC Unit ?

    Quote Originally Posted by Joe Reilly View Post
    and I understand that upright systems do not even require a secondary drain to be connect as most of the time they are plugged.

    DSCN8596 (450x338).jpg
    Can't imagine why that would matter. Horizontal and vertical cabinet installations both require the exact same condensation drain systems, including secondary. Which leads to...

    Regarding your photo, the coil's drain pan simply has been designed to allow 2 drain ports no matter which orientation is chosen for the install.


  3. #3
    Join Date
    Mar 2007
    Location
    Santa Rosa, CA
    Posts
    3,154

    Default Re: 3rd drain from HVAC Unit ?

    Oh, I get it. The topmost plug can be removed for the secondary drain if the coil box is on its side.

    Lower/right, primary drain if vertical install
    Lower/left secondary drain if vertical install or primary drain if horizontal install.
    Top, secondary drain if horizontal install.

    Dom, you are smarter than you look (or smarter than me, whichever your prefer).

    Department of Redundancy Department
    Supreme Emperor of Hyperbole
    http://www.FullCircleInspect.com/

  4. #4
    Join Date
    Apr 2019
    Location
    California
    Posts
    80

    Default Re: 3rd drain from HVAC Unit ?

    That actually makes sense...


  5. #5
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,042

    Default Re: 3rd drain from HVAC Unit ?

    But ...

    Both condensate drains require traps, and if that shadow below the drain elbow is just a shadow - where does that drain to?

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  6. #6
    Join Date
    Apr 2019
    Location
    California
    Posts
    80

    Default Re: 3rd drain from HVAC Unit ?

    Quote Originally Posted by Jerry Peck View Post
    But ...

    Both condensate drains require traps, and if that shadow below the drain elbow is just a shadow - where does that drain to?
    It did not drain anywhere, yes.. I wrote it up


  7. #7
    Join Date
    Aug 2011
    Location
    Bennett (Denver metro), Colorado
    Posts
    1,461

    Default Re: 3rd drain from HVAC Unit ?

    Quote Originally Posted by Jerry Peck View Post
    But ...

    Both condensate drains require traps, and if that shadow below the drain elbow is just a shadow - where does that drain to?
    Where is a requirement for both to be trapped? I never see the "back-up" or over-flow drain trapped. Since it does not go directly to and into a DWV, I don't know of any requirement for a trap. For one thing, there would never be water in the trap, since the back-up drain never has condensate coming out, unless the primary is blocked. And the purpose of the back up drain is to make a mess that alerts the homeowner to a problem with the primary drain. What I see in the photo, is a typical installation.

    If you choose not to decide, you still have made a choice.

  8. #8
    Join Date
    Aug 2019
    Location
    TX
    Posts
    4

    Default Re: 3rd drain from HVAC Unit ?

    Quote Originally Posted by Lon Henderson View Post
    Where is a requirement for both to be trapped? I never see the "back-up" or over-flow drain trapped. Since it does not go directly to and into a DWV, I don't know of any requirement for a trap. For one thing, there would never be water in the trap, since the back-up drain never has condensate coming out, unless the primary is blocked. And the purpose of the back up drain is to make a mess that alerts the homeowner to a problem with the primary drain. What I see in the photo, is a typical installation.
    Without traps the cold air in the unit can escape (since there is a drain pipe size hole on the housing!) which lowers the system's efficiency. To make the traps work, you need to fill the secondary drain pipe trap with water (the main trap will be filled with condensate water anyway). Secondary drain pipe needs an emergency drain pan underneath the unit. And, another emergency drain line should be installed from the drain pan to outside of the building or visible location for notifying/alarm so the owner/tenant can clean the primary drain line. Please see another post in "HVAC condensate drain pipes".


  9. #9
    Join Date
    Aug 2011
    Location
    Bennett (Denver metro), Colorado
    Posts
    1,461

    Default Re: 3rd drain from HVAC Unit ?

    Quote Originally Posted by Jaeyoung Lee View Post
    Without traps the cold air in the unit can escape (since there is a drain pipe size hole on the housing!) which lowers the system's efficiency. To make the traps work, you need to fill the secondary drain pipe trap with water (the main trap will be filled with condensate water anyway). Secondary drain pipe needs an emergency drain pan underneath the unit. And, another emergency drain line should be installed from the drain pan to outside of the building or visible location for notifying/alarm so the owner/tenant can clean the primary drain line. Please see another post in "HVAC condensate drain pipes".
    In a nonexistent universe, an OCD homeowner might keep the traps full, but in our universe, that doesn't happen. The amount of air escaping these drains is not significant enough to be a consideration. I've never seen a drain pan under the back-up drain or a water leak alarm underneath one...but cheerfully agree that both ideas are good. The best solution is an inline shutoff like a Safe-T float valve switch on the back-up, but everything in the OP's photo is permitted every working day of the week around these here parts.

    If you choose not to decide, you still have made a choice.