Thread: fire rated door?
01-05-2008, 08:28 AM #1
fire rated door?
How can you tell the door is fire rated?
01-05-2008, 08:35 AM #2
Re: fire rated door?
Yes, it is not.
It has a window in it.
01-05-2008, 08:38 AM #3
Thanks Scott, I figured that, but is there a label or stamp on fireproof doors?
01-05-2008, 08:53 AM #4
01-05-2008, 09:01 AM #5
The door needs to have a 20 min rating or be 1 3/8" in thickness if it is a solid core. You can have a solid wood door that is 1 3/8" thick and it will satisfy the requirement. Solid wood doors seldom have a ID sticker, stamp or label on them.
01-05-2008, 10:21 AM #6
2006 IRC - 309.1 Opening protection: Openings from a private garage directly into a room used for sleeping purposes shall not be permitted. Other openings between the garage and residence shall be equipped with solid wood doors not less than1-3/8 inches in thickness, solid or honeycomb core steel doors not less than 1-3/8 inches thick, or 20-minute fire-rated doors.
(no label than can't confirm therefore report)
2006 IBC See 715.5 & 715,4,6,3,1 Fire protection Glazing. For those in California see 2007 CBC 715.5.
01-05-2008, 10:37 AM #7
Does not need to be a fire rated door.
It could be ... or it could be (as pointed out by Jerry Mc. below) ...
Jerry Mc.,or 20-minute fire-rated doors.
I'm not fully understanding the below:
You mean 'if not solid wood and not less than 1-3/8 inches and not a solid or honey comb steel door not less than 1-3/8 inches', right?(no label than can't confirm therefore report)
If not one of those, then it must be labeled (to be a fire rated door) or it is not a proper door (not fire rated, and not one of the approved options.
Scott,
A fire rated door CAN HAVE a window in it, albeit of limited size (I believe it is 100 sq inches, which is why you find 3" by 33" view glass in many fire rated doors).
A door with a window the size in the photo, I agree, with a window *like that* - not fire rated.
Also neither does it meet the other two options for doors.
01-05-2008, 02:21 PM #8