Results 1 to 10 of 10
    TIM MASTICK's Avatar
    TIM MASTICK Guest
    Default Maximum step down for a french door
    We have an outswinging french door with a 6" step and was told this can be no more than 1 1/2" step down. I just wanted to clarify before I rip out the door and have it swing inward. This door goes out to a patio and the other door in the room goes to the garage. This door is also the only one on this floor that takes you outside of the home without going up a flight of stairs.
    Connecticut
    Default Re: Maximum step down for a french door
    This should help
    From the 2006 IRC.
    R311.4.3 Landings at doors.
    There shall be a floor or landing
    on each side of each exterior door. The floor or landing
    at the exterior door shall not be more than 1.5 inches (38
    mm) lower than the top of the threshold. The landing shall
    be permitted to have a slope not to exceed 0.25 unit vertical
    in 12 units horizontal (2-percent).
    Exceptions:
    1. Where a stairway of two or fewer risers is located
    on the exterior side of a door, other than the
    required exit door, a landing is not required for the
    exterior side of the door provided the door, other
    than an exterior storm or screen door does not
    swing over the stairway.
    2. The exterior landing at an exterior doorway shall
    not be more than 7
    3/4 inches (196 mm) below the
    top of the threshold, provided the door, other than
    an exterior storm or screen door does not swing
    over the landing.
    3. The height of floors at exterior doors other than the
    exit door required by Section R311.4.1 shall not be
    more than 7
    3/4 inches (186 mm) lower than the top
    of the threshold.
    The width of each landing shall not be less than the door
    served. Every landing shall have a minimum dimension of
    36 inches (914 mm) measured in the direction of travel.
    That is correct.
    The landing on an outswing door can be no greater than 1.5 inches below the threshold.
    I have included the code that addresses this.
    Exceptions:
    not be more than 7
    over the landing.
    more than 7
    of the threshold.
    Bob Spermo's Avatar
    Bob Spermo Guest
    Tim,
    Could you build a platform on top of the patio to reduce the drop? Of course the platform would have to be big enough to accomodate the outswing door.
    TIM MASTICK Guest
    Thanks so much for the info...
    TIM MASTICK Guest
    A platform was my 1st thought until I layed it out. It was so big it impeded the walkway so that is out. Just going to have to flip the door.....
    If you flip the door so that it opens inward, be sure that the door does not block a light switch.
    TIM MASTICK Guest
    thanks for the heads up
    Quote Originally Posted by TIM MASTICK View Post
    Make sure the door is suitable to be switched around like that - most exterior doors are not suitable to just turn around and use backward - the door, weather strip, and threshold are designed to be installed with the exterior side facing the exterior. Switching the door around will likely defeat all those weather resisting features, besides, doors are rated for given wind pressures and if the door is installed backward there is no rating.
    TIM MASTICK Guest
    Didnt even think of that thanks
