08-28-2011, 08:06 PM #1
Townhouse - self closing garage doors
Do doors that lead from a garage (all garages connected together) to a common area have to be self closing?
Similar Threads:Mazza Inspections and stuff...
https://mazzainspections.com
https://waterintrusionspecialist.com
08-28-2011, 09:57 PM #2
Re: Townhouse - self closing garage doors
If the corridor they join is habitable (has ducting going to it) then they all need to be self closing to prevent the fast spreading of fire, smoke, and poisonous gases. If the corridor has one hour fire resistance, than the door from the corridor to the other habitable portions of the building needs to be self closing.
08-29-2011, 06:55 AM #3
From the picture, this appears to be a common hallway. This is usually considered a one-hour "fire corridor" for safe exit. All doors usually are required to be self closing fire rated doors to prevent spread of fire. You often see them held open by magnetic catches tied to the fire alarm system if there is one.
You also often see fire doors to stairwells and such blocked open by residents. This is a huge fire code violation that I frequently call out.
877-466-8504
08-29-2011, 06:56 AM #4
08-29-2011, 07:53 AM #5
No.
What your describing would not be a "townhouse" under the IRC, or california's current version of same - but fall under the former CBC version of the UBC or IBC.
I suspect the inspected was and is actually a Condo and you have photographed limited common and shared limited common elements.
I further suspect and that none of the units themselves share the separation with that of the garage(s) spaces and are further separated by common or limited common hall/foyer/ space and that the doors to the actual habital units have self-closing doors with thresholds. There is likely a non-locking door separating this "garage"/storage "hall" from the entrance foyer/common egress/exit path from the units which opens to that foyer (escape path FROM the common garage hall) has a closer and may or may not be held open with electro magnet integrated with fire detection system. The deadbolts on those garage exit doors should not require a key to operate from inside the garage space(s) and the partition walls between the garage spaces themselves are likely NOT separation walls.
08-29-2011, 09:10 AM #6
They are fire doors and they need to self-close and latch. (IFC 703.2.3)
08-29-2011, 04:24 PM #7