Old 06-06-2007, 03:07 PM
John Stephenson
Posts: n/a
Stairway bottom landing
F.I.R.E. provides fireplace education, consulting services, fire investigation and litigation support across the United States.
Old 06-06-2007, 07:11 PM
Jerry McCarthy's Avatar
Re: Stairway bottom landing
That's not a landing, but rather a large tread.
2006 IRC R311.5.4 Landings for stairways: There shall be a floor or landing at the top and bottom of each stairway.
Exception: A floor or landing is not required at the top of an interior flight of stairs, including stairs in an enclosed garage, provided a door does not swing over the stairs.
A flight of stairs shall not have a vertical rise larger than 12 feet (3658 mm) between floor levels or landings.
The width of each landing shall not be less than the width of the stairway served. Every landing shall have a minimum dimension of 36 inches (914 mm) measured in the direction
of travel.
(Highlighted for emphasis)
Construction Consultant
Old 06-06-2007, 08:33 PM
Jerry Peck's Avatar
While it seems that West Coast Jerry feels the same way I do about 'that type of tread', the code is not so clear ...
R311.5.3.2 Tread depth.
The minimum tread depth shall be 10 inches (254 mm). The tread depth shall be measured horizontally between the vertical planes of the foremost projection of adjacent treads and at a right angle to the tread’s leading edge. The greatest tread depth within any flight of stairs shall not exceed the smallest by more than 3/8 inch (9.5 mm). Winder treads shall have a minimum tread depth of 10 inches (254 mm) measured as above at a point 12 inches (305 mm) from the side where the treads are narrower. Winder treads shall have a minimum tread depth of 6 inches (152 mm) at any point. Within any flight of stairs, the largest winder tread depth at the 12 inch (305 mm) walk line shall not exceed the smallest by more than 3/8 inch (9.5 mm).
I know, what about tread depth variation ...
My interpretation is that, while winders are allowed in a means of egress, they are not allowed 'within' a flight of straight stairs.
Also, going back to landings ...
R311.5.4 Landings for stairways.
- Exception: A floor or landing is not required at the top of an interior flight of stairs, including stairs in an enclosed garage, provided a door does not swing over the stairs.
- A flight of stairs shall not have a vertical rise larger than 12 feet (3658 mm) between floor levels or landings.
- The width of each landing shall not be less than the width of the stairway served. Every landing shall have a minimum dimension of 36 inches (914 mm) measured in the direction of travel.
My interpretation, which seems to also be that of West Coast Jerry, is that the landing must be in the direction of travel, straight down the stairs, i.e., the direction in which one would most likely fall.
HOWEVER, ...
Many, many, many, many (did I say "many"?) building officials and inspector say that winders ARE allowed 'within' a straight flight of stairs.
Those same building officials and inspectors (may I say "many") also treat "the direction of travel" as being a radius from the top corner of the first riser ascending or the last riser ascending. I.e., you can have a straight flight of stairs, a semi-circular landing, then another straight flight of stairs.
*I* say you need a straight landing, THEN you can make the semi-circular landing turning to the next flight of stairs.
*Some* building officials, inspectors, architects, etc., agree with that, many, many, many more do not.
When calling that out, check with your AHJ and see what they allow, and if they are one of the ones who allow those trip and fall hazards ... try to get them to change their mind (it is extremely difficult to get them to change their mind).
Besides, if you refer to the book which many HIs provide for a Visual Interpretation of the IRC, you will find ... winders shown in a otherwise straight flight of stairs, with winders taking the place of a proper (in my opinion) landing.
http://www.stairways.org/pdf/2003%20...C%20SCREEN.pdf
Look at pages 6 and 8.
HomeGauge Reports
Similar Threads
Interior stairway riser height dan orourke Building Interior: Home Inspection and Commercial Inspection 6 06-19-2007 07:47 AM
Light fixture location - stairway dan orourke Electrical Systems: Home Inspection and Commercial Inspection 1 05-08-2007 03:54 PM
Opening at bottom of guardrail dan orourke Building Interior: Home Inspection and Commercial Inspection 5 05-07-2007 07:29 PM
Stairway Illumination dan orourke Building Interior: Home Inspection and Commercial Inspection 4 04-15-2007 06:46 PM
From the old board, Stairway windows? Tim Moreira Building Interior: Home Inspection and Commercial Inspection 1 04-04-2007 12:03 PM
vB.Sponsors
Ad Management by RedTyger