Old 05-26-2008, 01:11 PM
Richard Stanley Richard Stanley is offline
Window height
2nd floor windows less than 18" above floor. 'thought I had read that they were not allowed any more. I can only find that they have to be safety glazing unless protective guard installed. I still recommend protective guard / barrier. The glass may not cut you, but, the fall wont improve your health. IRC 308.4.7 Applicable (2406.4.7 UBC) Comments welcome.
Home inspection
Old 05-26-2008, 01:56 PM
John Arnold John Arnold is online now
Re: Window height
They need to be 9 square feet or larger to "have" to have safety glass, if memory serves.
Old 05-26-2008, 02:56 PM
Jerry McCarthy's Avatar
Re: Window height
Actually it goes something like this:
2006 IRC - 613.2 - Window Sills: In dwelling units, where the opening of an operable window is located more than 72 inches (1829mm) above the finished grade or surface below, the lowest part of the clear opening of the window shall be a minimum of 24 inches (610mm) above the finished floor of the room in which the window is located. Glazing between the floor and 24 inches (610mm) shall be fixed or have openings through which a 4-inch-diameter (102 mm) sphere cannot pass.
Exceptions:
1. Windows whose openings will not allow a 4-inch-diameter (102mm) sphere to pass through the Opening when the opening is in its largest opened position.
2. Openings that are provided with window guards that comply with ASTM F 2006 or F 2090.
2007 CBC Ditto.
Construction Consultant
Old 05-26-2008, 05:35 PM
Re: Window height
Quote:
- R308.4 Hazardous locations.
The following shall be considered specific hazardous locations for the purposes of glazing:
- - 7. Glazing in an individual fixed or operable panel, other than those locations described in Items 5 and 6 above, that meets all of the following conditions:
- - - 7.1. Exposed area of an individual pane larger than 9 square feet (0.836 m2).
- - - 7.2. Bottom edge less than 18 inches (457 mm) above the floor.
- - - 7.3. Top edge more than 36 inches (914 mm) above the floor.
- - - 7.4. One or more walking surfaces within 36 inches (914 mm) horizontally of the glazing.
That leaves out a lot of windows.
I've always had a feeling that those windows should not only be tempered, but should also be laminated impact resistant glass.
Face it, there really is not a lot of difference in falling through a non-tempered window and a tempered window from 30 feet up, other than the size of the glass pieces you will be landing on.
Laminated impact resistant glass will at least stay in the frame when you fall against it hard enough to break it. Keeping you up there where you were.
Last edited by Jerry Peck : 05-27-2008 at 05:31 AM. Reason: ??"Face"??? er ... "Face it"
Old 05-26-2008, 06:26 PM
Re: Window height
I cannot find any reason to disagree with EC Jerry on this issue and what this clearly demonstrates, at least to me, is that the fingerprints of the NAHB are still all over the 2006 IRC.
  #6 (permalink)
Old 05-27-2008, 06:38 AM
Re: Window height
The 613.2 is what I was looking for. 24" instead of 18". Thanks wcj. I noticed that it was not referenced in 2003 IRC.
  #7 (permalink)
Old 05-27-2008, 07:22 AM
Re: Window height
Richard,
Correct, new wording to the 2006 IRC.
The old South Florida Building Code - Broward County Edition required guards at windows when the drop outside was greater than 4' and the sill was less than 30" if 24" wide or wider, and, where the drop is 4' or less outside, there were other options.
The above was changed in the 2001 Florida Building Code, HVHZ (High Velocity Hurricane Zone, which is Broward and Miami-Dade counties), but still required safeguards in many instances (to long to post here, and that went out with the 2004 Florida Residential Code anyway).
That's called 'consensus weakening of the codes', just another example of how codes become weaker the more people are involved in making of the code.
  #8 (permalink)
Old 05-27-2008, 07:30 AM
Re: Window height
Thanks JP
Similar Threads
electric eye height wayne soper Exterior Systems: Home Inspection and Commercial Inspection 10 06-10-2008 09:39 AM
Height of vanity tops Jim Thompson Building Interior: Home Inspection and Commercial Inspection 6 05-02-2008 08:27 AM
Flue height Jon Randolph Fireplaces, Chimneys and Solid Fuel Burning Appliances: Home Inspection and Commercial Inspection 3 04-07-2008 07:08 PM
Height requirement for exterior box David Macy Electrical Systems: Home Inspection and Commercial Inspection 8 07-16-2007 03:56 PM
Plumbing vent height John Stephenson Plumbing System: Home Inspection and Commercial Inspection 17 05-23-2007 12:44 PM
vB.Sponsors
Ad Management by RedTyger
