Is there a minimum clearance requirement for above a glass cooktop range?
Had an over the range microwave / vent combo unit with only 14" from cooking surface to the bottom of the unit.
Also while on the subject, does anyone know what clearance from a cooking surface to the bottom of the cabinets is required?
04-16-2010, 11:08 AM #2
Re: Clearance above range for microwave
SECTION M1504
INSTALLATION OF MICROWAVE OVENS
M1504.1 Installation of microwave oven over a cooking
appliance.
The installation of a listed and labeled cooking
appliance or microwave oven over a listed and labeled cooking
appliance shall conform to the terms of the upper appliance’slisting and label and the manufacturer’s installation instructions.
SPECIAL FUEL-BURNING EQUIPMENT
SECTION M1901
RANGES AND OVENS
M1901.1 Clearances.
Freestanding or built-in ranges shall
have a vertical clearance above the cooking top of not less thanand labeling of the range hoods or appliances.
30 inches (762 mm) to unprotected combustible material.
Reduced clearances are permitted in accordance with the listing
04-16-2010, 11:50 AM #3
This might help. www.inspectionnews.net/home_inspection/h-e-l-p/15401-cook-top-too-close-cabinet-vent.html
13 1/4 inches above the Range Top is as low I have seen for a Manufactures Microwave Installation Instruction.