    I haven't seen EIFS before, at least around where I live until today, I think.
    Any of you guys recognize this as being EIFS? I see foam under the weep around the entire perimeter.
    not sure if the gap has anything to do with...I thought the sill was off but then noticed the sheer was flush with the stem.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Crawl Space Creeper

  2. #2
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,851

    Default Re: Eifs

    Quote Originally Posted by Marc M View Post
    I haven't seen EIFS before, at least around where I live until today, I think.
    Any of you guys recognize this as being EIFS? I see foam under the weep around the entire perimeter.
    not sure if the gap has anything to do with...I thought the sill was off but then noticed the sheer was flush with the stem.
    Looks like EIFS, most likely second generation EIFS. Should not see the EPS foam or the OSB substrate.

    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  3. #3
    Join Date
    Sep 2008
    Location
    so so, California
    Posts
    1,867

    Default Re: Eifs

    Quote Originally Posted by Scott Patterson View Post
    Looks like EIFS, most likely second generation EIFS. Should not see the EPS foam or the OSB substrate.
    Excellent. Much thanks Scott. BTW, can i ask why you can't or shouldn't see the foam? For example, is there something missing or ?


  4. #4
    Join Date
    Mar 2007
    Location
    Windsor Ontario
    Posts
    378

    Default Re: Eifs

    Detail data sheet -http://www.dryvit.ca/fileshare/doc/us/description/ds446.pdf


  5. #5
    Join Date
    Mar 2007
    Location
    Santa Rosa, CA
    Posts
    3,154

    Default Re: Eifs

    Quote Originally Posted by Marc M View Post
    Excellent. Much thanks Scott. BTW, can i ask why you can't or shouldn't see the foam? For example, is there something missing or ?
    Marc,

    If you had come to IW last week, you could have had Scott tell you all about EIFS!

    Department of Redundancy Department
    Supreme Emperor of Hyperbole
    http://www.FullCircleInspect.com/

  6. #6
    Join Date
    Sep 2008
    Location
    so so, California
    Posts
    1,867

    Default Re: Eifs

    Quote Originally Posted by Gunnar Alquist View Post
    Marc,

    If you had come to IW last week, you could have had Scott tell you all about EIFS!
    Haha...whats up Gunnar...?
    I know right? Nobody tells me these things and i haven't been lurking the IN halls lately.


  7. #7
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,851

    Default Re: Eifs

    Quote Originally Posted by Marc M View Post
    Excellent. Much thanks Scott. BTW, can i ask why you can't or shouldn't see the foam? For example, is there something missing or ?
    The largest reason for not wanting to see the EPS foam is that means it was not installed to the manufacturers requirements and you can bet that you will find other details that are missing as well! The EPS foam should be wrapped in a fiberglass mesh that is embedded in a base coat. This protects the EPS from sunlight which will degrade it and also protects it from impact by adding rigidity to the EPS board.

    Sometimes the installers will just set the unfinished EPS board in the starter strip just as it is showing in your photo. The reason for the holes "Keys" is so that the base coat will adhere to the starter strip and lock it in place; the hole are not to allow water to drain as many think.

    Gunnar, it was good seeing you at IW… Hope you enjoyed the class...

    Last edited by Scott Patterson; 02-03-2016 at 08:59 AM.
    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  8. #8
    Join Date
    Mar 2007
    Location
    Santa Rosa, CA
    Posts
    3,154

    Default Re: Eifs

    Quote Originally Posted by Scott Patterson View Post
    Gunnar, it was good seeing you at IW… Hope you enjoyed the class...
    Scott,

    It was good to meet you as well. I did enjoy the class. It was one of the better classes that I took.

    We don't see much EIFS up here, so it's nice to have some information as to how to look for installation problems if/when I do find something.

    Department of Redundancy Department
    Supreme Emperor of Hyperbole
    http://www.FullCircleInspect.com/

  9. #9
    Join Date
    Sep 2008
    Location
    so so, California
    Posts
    1,867

    Default Re: Eifs

    Quote Originally Posted by Scott Patterson View Post
    The largest reason for not wanting to see the EPS foam is that means it was not installed to the manufacturers requirements and you can bet that you will find other details that are missing as well! The EPS foam should be wrapped in a fiberglass mesh that is embedded in a base coat. This protects the EPS from sunlight which will degrade it and also protects it from impact by adding rigidity to the EPS board.

    Sometimes the installers will just set the unfinished EPS board in the starter strip just as it is showing in your photo. The reason for the holes "Keys" is so that the base coat will adhere to the starter strip and lock it in place; the hole are not to allow water to drain as many think.

    Gunnar, it was good seeing you at IW… Hope you enjoyed the class...
    Excellent Scott. I really appreciate the information.


  10. #10
    Join Date
    Oct 2010
    Location
    MONTREAL QUEBEC-CANADA
    Posts
    2,075

    Default Re: Eifs

    Quote Originally Posted by Marc M View Post
    I haven't seen EIFS before, at least around where I live until today, I think.
    Any of you guys recognize this as being EIFS? I see foam under the weep around the entire perimeter.
    not sure if the gap has anything to do with...I thought the sill was off but then noticed the sheer was flush with the stem.
    Marc, did you tap on the veneer surface of the EIFS envelope?
    If so, what tone or vibration was transmitted back?

    Sound. The EPS foam will sound hollow.
    Broadcast minerals or stone on concrete paneled surface will sound a higher tone vibration. Tap tap as opposed to lower vibration like a toc toc.
    Use the back of a screwdriver. I carry a 2-pound rubber mallet.

    Barrier or Drainage EIFS. also has a fixation.
    If you use your thumb and push into the veneer it will move sightly causing an impression and form its shape once the pressure is released. You have to give force.

    Barrier or Drainage EIFS.
    Best place to view the system is at the bottom.

    Drainage EIFS, Drip screed is easy to identify.
    Barrier eifs, the bottom should be coated.
    Buy a small extending mirror.

    Those images look like a form of broadcast stone or mineral overlay.
    I will try to provide some information tomorrow. I am not in my office.

    Robert Young's Montreal Home Inspection Services Inc.
    Call (514) 489-1887 or (514) 441-3732
    Our Motto; Putting information where you need it most, "In your hands.”

  11. #11
    Join Date
    Sep 2008
    Location
    so so, California
    Posts
    1,867

    Default Re: Eifs

    It was single coat. From the builder...


    Quote Originally Posted by ROBERT YOUNG View Post
    Marc, did you tap on the veneer surface of the EIFS envelope?
    If so, what tone or vibration was transmitted back?

    Sound. The EPS foam will sound hollow.
    Broadcast minerals or stone on concrete paneled surface will sound a higher tone vibration. Tap tap as opposed to lower vibration like a toc toc.
    Use the back of a screwdriver. I carry a 2-pound rubber mallet.

    Barrier or Drainage EIFS. also has a fixation.
    If you use your thumb and push into the veneer it will move sightly causing an impression and form its shape once the pressure is released. You have to give force.

    Barrier or Drainage EIFS.
    Best place to view the system is at the bottom.

    Drainage EIFS, Drip screed is easy to identify.
    Barrier eifs, the bottom should be coated.
    Buy a small extending mirror.

    Those images look like a form of broadcast stone or mineral overlay.
    I will try to provide some information tomorrow. I am not in my office.



  12. #12
    Join Date
    Oct 2010
    Location
    MONTREAL QUEBEC-CANADA
    Posts
    2,075

    Default Re: Eifs

    Quote Originally Posted by Marc M View Post
    It was single coat. From the builder...
    Marc.
    Please explain what type of EIFS you posted images of.
    Thanks!

    ICF wall?.Single coat with minerals?
    EIFS Single coat.
    What is EIFS?*EIMA : EIFS Industry Members Association

    I have taken a course through NACHI, Ron Huffman the educator/instructor.
    Here is a link. https://www.nachi.org/stucco-eifs.htm
    No poor remarks please.
    Good course. I am sure others here know Ron by name.

    Last edited by ROBERT YOUNG; 02-23-2016 at 05:43 AM.
    Robert Young's Montreal Home Inspection Services Inc.
    Call (514) 489-1887 or (514) 441-3732
    Our Motto; Putting information where you need it most, "In your hands.”