05-16-2007, 04:17 PM #1
Electrical cable insulation cover
05-16-2007, 04:26 PM #2
Re: Electrical cable insulation cover
I was always told to remove it because it was a flammable material from inside the panel.
05-16-2007, 04:59 PM #3
With everything else which is wrong in that panel ... I would only mention it in passing, as in ...
Get a QUALIFIED and LICENSED electrical contractor out to correct all the sh*t in this panel, including, but not limited to: (make list, including that item - but that is the least of their problems).
Only I always said it nicer in my reports.
05-16-2007, 06:06 PM #4
For practical intents and purposes, no.
With sophisticated equipment, I'm sure one could measure a slight increase after a while with a load on it, however, it would not be a problem.
I'm not recalling anything which prohibits sloppy work like that, other than ones own pride in their work (which, obviously, was non-existent there).
That is, other than the vague:
- NEC
- - 110.12 Mechanical Execution of Work.
- - - Electrical equipment shall be installed in a neat and workmanlike manner.
05-16-2007, 08:25 PM #5
I keep seeing HIs saying 1-1/2" or thereabouts, any idea where you got it from?
"Workmanship" would put it such that the outer sheather was trimmed off 'just inside the strain relief clamp'.
I don't see were running an NM cable, sheath and all, up almost to the breaker, then slit the sheath far enough to allow the grounding conductor to reach the grounding terminals, the neutral conductor to reach the neutral terminals, and the hot conductor to reach the breaker. Sure, it would "look" *ugly as sin*, but I don't know what problems it would cause, other than contributing to physical excess fill - but if the sheath puts you into an 'overfill' condition, I suspect it was already overfilled with conductors.I don't see where it would cause overheating or any other issue.
Anyone have an authoritative source on that 1-1/2"? I mean a *real* authoritative source.