Results 1 to 13 of 13
Thread: service entry cable sizing
01-15-2009, 05:26 PM #1
House had a 225 amp SqD breaker with
[aluminum] 4/0 awg 600v rhh or rhw service
The breaker itself indicated the following: #4-300mcm cu/al.
I believe 4/0 can carry 200 amp max?
01-15-2009, 05:53 PM #2
Re: service entry cable sizing
Correct. #4/0 AWG aluminum is rated for 200 amps.
The rating on the breaker is for the approved conductor sizes allowed in the terminals.
I'm sure you got the multiple tapped neutrals. For all those empty terminals, why on earth did they put 2 and 3 in the same terminal? Then the grounds too.
Last edited by Jerry Peck; 01-16-2009 at 07:29 AM. Reason: correcting a typo Jeff pointed out - correcting #4 AWG to #4/0 AWG
01-15-2009, 06:59 PM #3
aren't they allowed 2 per terminal? three i know is wrong.
01-15-2009, 07:28 PM #4
01-15-2009, 07:51 PM #5
01-16-2009, 06:14 AM #6
We know why you fly: because the bus is too expensive and the railroad has a dress code...
www.atozinspector.com
01-16-2009, 06:58 AM #7
01-16-2009, 07:11 AM #8
Rhw can only handle 190A
Rhh can only handle 205A
If it is rated for both then the higher of the two applies.
01-16-2009, 07:30 AM #9
01-16-2009, 07:33 AM #10
Jeff,
See: (underlining is mine)
- Table 310.15(B)(6) Conductor Types and Sizes for 120/240-Volt, 3-Wire, Single-Phase Dwelling Services and Feeders. Conductor Types RHH, RHW, RHW-2, THHN, THHW, THW, THW-2, THWN, THWN-2, XHHW, XHHW-2, SE, USE, USE-2
- - 4/0 aluminum - 200 amp (reading through the table from right under Aluminum to the left under Rating)
01-16-2009, 07:38 AM #11
Yes, I understand that but the cable is already rated at 205 so the 200A allowable ampacity for 4/0 aluminum in single family residences is not relevant since they used a higher rated conductor.
01-16-2009, 07:51 AM #12
01-16-2009, 10:01 AM #13
According to the California code, based on the NEC, 4/0 copper can handle 250 amps, while 4/0 aluminum or copper-clad aluminum will conduct 200 amps safely.