    Default Tapping conductors in the service

    This is a 150amp service panel. They tapped the conductors to supply an auxiliary panel in the garge. The panel is rated for 125amp. Doesn't it have to be rated for 150amps?

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Member Benefits1

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Tapping conductors in the service

    Quote Originally Posted by mathew stouffer View Post
    This is a 150amp service panel.
    Presuming that means the main disconnect is rated for 150 amps.

    They tapped the conductors to supply an auxiliary panel in the garge. The panel is rated for 125amp. Doesn't it have to be rated for 150amps?
    Yes, with a few possible exceptions which most likely would not apply here (would need more information and then review 240.21(B)(1) through (5) ).

    Just as importantly, did you see what they did to the back of that service equipment enclosure? They really screwed that one up.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    mathew stouffer's Avatar
    mathew stouffer Guest

    Default Re: Tapping conductors in the service

    You mean the hole they punched in the panel with the make shift bushing.


  4. #4
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Tapping conductors in the service

    Quote Originally Posted by mathew stouffer View Post
    You mean the hole they punched in the panel with the make shift bushing.
    Yes sir, except that I would not call that a "hole they punched", looks more like 'Hey, Billy Bob, whatcha think ... 12 ga side-by-side? One or two?' 'Bubba, I'd go with both.' 'Sounds good to be Billy Bob - stand aside ... '

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  5. #5
    mathew stouffer's Avatar
    mathew stouffer Guest

    Default Re: Tapping conductors in the service

    Good one.